The system consists of the following components:
- 3x Quattros 15000VA 48V 230V on 3phase configuration
- 2x SmartSolar mppt 250/100 connected via ve.direct
- 1x Fronius Verto 33.3kW
- 1x CCGX
- 6x 16.6kWh poweroad Tervol L16
- 1x 3 Phase 20kVA generator
The Quattros will form a 400/230 V, 50 Hz island network. The PV Inverter Support Assistant will regulate the Fronius through frequency shifting during inverter operation, with the Fronius configured for compatible MicroGrid operation (MG50 grid code). As expected, the Fronius inverter will connect to the AC output of the Quattros because no grid is present. The MPPTs are there for maximum reliability and also for breaking the deadlock with the AC-coupled PVs in the event the BMS locks out due to low SoC.
During normal off-grid operation, the Quattros regulate the Fronius through frequency shifting, and the system works as expected.
The concern arises when the generator is connected to the Quattros’ AC inputs. Once the Quattros synchronise with the generator, they can no longer independently adjust the AC frequency to regulate the Fronius.
If the batteries cannot accept further charging, the loads are low, and PV production is high, surplus power could flow back into the generator, potentially damaging it. I therefore need a reliable way to stop or disconnect the Fronius before the Quattros connect to the generator.
I have considered three options, but each raises some questions:
-
Connect the Fronius to AC-out-2 and reverse the default relay logic.
The outputs would remain enabled during inverter operation and disconnect when the generator is connected. However, the Fronius produces approximately 48–49 A per phase at nominal voltage, while AC-out-2 is rated for 50 A. Is this arrangement approved for continuous, bidirectional operation at that current? I am concerned about the limited current margin and long-term contact reliability. -
Connect the Fronius to AC-out-1 through an external three-phase contactor rated for the application, for example 100 A.
The contactor would be controlled by a programmable relay on the master Quattro. Does VEConfigure support the necessary logic to disconnect the Fronius before the generator is accepted and reconnect it after the generator has been disconnected? Can this be coordinated reliably across the three-phase system? -
Control the Fronius over the local network through the CCGX.
The Fronius will already be connected to the same LAN as the CCGX for monitoring. Victron documents Fronius zero-feed-in control for ESS installations, but does this functionality also work in a fully off-grid system using the PV Inverter Support Assistant? If so, can it reliably prevent reverse power into the generator, including during sudden load rejection or loss of communication?
Which approach would you recommend? Is there an official Victron-supported solution or application diagram for this arrangement, including the required settings and switching sequence?