Hi all,
I’d like to start a discussion for controlling AC-in connection/disconnection based primarily on grid frequency stability, not just voltage.
Background / why
We recently installed our first grid-tied Multi RS system (we previously did grid-tied installs mostly with MultiPlus / Quattro; Multi RS has been used by us mainly off-grid until now).
This site is on Easter Island (Rapa Nui) where the grid is notoriously unstable. For the first ~10 days the Multi RS tracked the grid fine, but then we experienced ~2 days where the AC-in relay was clicking constantly (rapid connect/disconnect). After inspection we correlated it with grid frequency going “roller-coaster” in VRM.
What I’m trying to achieve
I’m looking for a Node-RED algorithm on the GX device that evaluates grid stability and decides whether the inverter/charger should:
-
stay grid-connected (normal operation), or
-
temporarily switch to Inverter-only / AC-in disconnected when the grid frequency becomes unstable,
-
then reconnect once frequency is stable again (with proper hysteresis / delays to avoid relay chatter).
This is for a guest house: sometimes loads are tiny (no guests), sometimes loads spike (kettle / AC / etc.). So it cannot be permanently off-grid — it must reconnect to grid in “emergency” scenarios or when battery/solar cannot support the loads.
Existing logic (voltage-based, simple)
On other sites with chronic low voltage I already use a simple Node-RED rule:
-
If PV + battery can cover loads → run inverter only (don’t “copy” bad grid voltage)
-
If battery is low → connect to grid just long enough to recover, then isolate again
Now I want the same idea, but triggered by frequency instability (pattern/noise/rapid deviation), not merely undervoltage.
Questions for the community
-
Has anyone already implemented a frequency-stability detector in Node-RED (GX) that drives AC-in connect/disconnect?
-
What’s the best signal / DBus path you use for AC-in frequency (and/or “grid is OK” flags)?
-
Recommended approach for debounce / hysteresis / minimum time connected/disconnected to protect the relay and avoid oscillations?
What I’m thinking (rough requirements)
-
Use AC-in frequency as input
-
Detect instability via one of:
-
frequency outside thresholds for X seconds
-
high rate-of-change (Δf/Δt) above threshold
-
standard deviation over a rolling window above threshold
-
-
Actions:
-
If unstable → force inverter-only (disconnect AC-in)
-
If stable for Y minutes → reconnect
-
Override: if SOC low / battery power limit reached / load too high → reconnect even if grid is marginal (best-effort)
-
If anyone has an existing flow or even just a proven strategy, I’d really appreciate it.