Multiplus II shuts down for a few seconds VE.Bus error #1 and #3

I have a problem in one of my installations. It is a 3-phase system with 3 Multiplus II and Cerbo GX. There is ESS running. The batteries are 3 Pylontech US3000, connected via a Lynx Distributor.

After running 1 1/2 years without problems, it now happened several times that the 220V output shut down for only a few seconds. The customer can not tell, if it was just one phase or all 3, because it was so short. In have different errors in the VRM alarm-protocol and on the GX. The GX device shows most times VE.Bus error#1 and just one time VE.Bus error#3. On the VRM alarm-protocol only the error#3 appears, but always 3 times with just 1 or 2 seconds time difference. The error#1 on the GX device is about one hour later.

I have no idea how I can localise the problem. It is very rare, the first time in August 24 and now 3 times in December. And the shut down is extremly short. I checked the DC fuses, but they are OK and I also checked the communcation connections. Thats all short original Victron cables.

What modifications and updates were made at the time the problems started?

There has been no modification or updates at all since the first installation.

What are the text descriptions of these errors ?

This is the VRM listing:

276 VE.Bus System [276] VE.Bus Error: VE.Bus Error 3: Not all, or more than, the expected devices were found in the system 2024-12-12 13:26:16 6m, 56s
276 VE.Bus System [276] VE.Bus Error: VE.Bus Error 3: Not all, or more than, the expected devices were found in the system 2024-12-12 13:26:16 1m
276 VE.Bus System [276] VE.Bus Error: VE.Bus Error 3: Not all, or more than, the expected devices were found in the system 2024-12-12 13:26:27 38s
276 VE.Bus System [276] VE.Bus Error: VE.Bus Error 3: Not all, or more than, the expected devices were found in the system 2024-12-03 12:33:40 14m, 6s
276 VE.Bus System [276] VE.Bus Error: VE.Bus Error 3: Not all, or more than, the expected devices were found in the system 2024-12-03 12:33:40 1m, 7s
276 VE.Bus System [276] VE.Bus Error: VE.Bus Error 3: Not all, or more than, the expected devices were found in the system 2024-12-03 12:33:56 35s
276 VE.Bus System [276] VE.Bus Error: VE.Bus Error 3: Not all, or more than, the expected devices were found in the system 2024-08-28 13:21:31 1m, 1s
276 VE.Bus System [276] VE.Bus Error: VE.Bus Error 3: Not all, or more than, the expected devices were found in the system 2024-08-28 13:21:31 29s
276 VE.Bus System [276] VE.Bus Error: VE.Bus Error 3: Not all, or more than, the expected devices were found in the system 2024-08-28 13:08:59 3m, 58s
276 VE.Bus System [276] VE.Bus Error: VE.Bus Error 3: Not all, or more than, the expected devices were found in the system 2024-08-28 13:08:58 1m, 1s

The GX device says: #1 Gerät ausgeschaltet (device switched off)

Clean and check all contacts of the ve.bus.

You’d have to ask victron if its possible to make a trace with wireshark and a mk3, but I’m afraid not

I made some more investigations and found out, that all 3 phases shut down at the same time. At that time also the VE.Bus went to off and the DC current was quite high. I am not sure what causes what and why. Today it happened 3 times and yesterday one time. Does anybody has an idea?

This is what it looks like: