Hi All,
I have a MultiPlus-II 48/5000/70-48 charging a bank of 4 * US5000 Pylontech batteries via 7KVA generator on its AC Input. With SOC around 60% the charge current into the battery bank is about 48A - well below the 70A rating on the Multi. This is in dense cloud with less than 200W from the solar panels. There are no loads taking significant current, and the output wattage reported by the generator matches that going into the Pylontechs. Room temp is mild (23deg).
The system has about 5KW of panels spread across two SmartSolar MPPT 150/70 controllers, and when the sun is good I have watched the Pylontech bank charge current go over 90A, so I know the Pylontech BMS will allow larger charge current, at least from the solar controllers. System is managed by a Cerbo GX.
Settings on the Multi:
AC1 Input Current Limit = 32A (7500W)
Grid Code is None (It’s an Off Grid System)
UPS mode is on
BatterySafe is on
Power Assist is on
Boost Factor is 2
Weak AC Input is on
Max Charge Current when viewed via VictronConnect over MK3-USB is 70A, but I believe this setting is irrelevant as the BMS will overrule.
Ideas?
Shalom
Bill