Multiplus-II 2x120V tripping GFCI

Here are some other leakage values measured when in different electrical panel states

No B-Stop, 0.42 mA, Shore power off, innverting mode


B-Stop, 1.26 mA, Shore power on, inverters breakers off, in inverting mode


No B-Stop, 5.51 mA, Shore power on, inverter power breakers on, in the inverting mode


No B-Stop, 18.9 mA, Shore power on, inverters in pass-through mode, 251 V, 60 Hz


B-Stop active, 4.28 mA, Shore power on, inverter breakers on, no pass through, inverting on


B-Stop active, 5.71 mA, Shore power on, inverting, no inverting pass through


B-Stop active, first on the leakage starts at 9.68 mA, shore power on, inverter breakers on, inverter pass through on 251 V, 60 Hz


B-Stop active, settles at 12.3 mA in a few minutes, inverter pass through, MW on, IP43 Charger on