I would like to optimize my battery charging with two IP22 chargers.
I have two 12V 300AH LiFePo4 batteries connected in parallel.
I have a 100/50 MPPT with 1Kw of panels but they are insufficient for my winter consumption.
So I bought two IP22s to charge my batteries with a generator.
Everything is synchronized via a BMV 712.
Without sun, the chargers remain in bulk mode, but each charger delivers only 20A on average, instead of 30A.
With sunshine, everyone switches to absorption mode, while my batteries are still almost empty at 13V. (and the chargers stay at around 20A).
This is how my chargers are set up:
Absorption voltage 14.6V
Float voltage deactivated
Standby voltage 13.5V
As they go into absorption mode too early, I’ve set the absorption time to 3 hours, so I have to unplug/replug my chargers every 2 hours to continue charging.
If anyone could tell me if it’s possible to charge at 60A with my IP22s that would be great, thanks.
Disconnecting the EV network doesn’t work either. I bought a BMV because I had exactly the same problem without it, and I thought it would correct this problem.
Today there’s no sun, and my MPPT shows me 3A at most. Even so, the system is in absorption mode, while the BMV currently shows me 13.48V.
Hello,
I have deactivated the “battery safe” function on both IP22 chargers.
I set the absorption time to “adaptive”.
I’ve also removed the MPPT from the EV network (all that’s left is the BMV and the two IP22s on it).
As soon as I plugged them in, they started absorbing immediately this morning.
My batteries are literally 90% empty at 12.7v.
It didn’t work
Currently, the chargers deliver 22A each.
The BMV indicates a voltage of 13.23V and the chargers 13.44.
8.37 should really be enough, maybe you have a contact problem somewhere ?
If possible measure the voltage drop from charger to battery, should be less then 0.1V otherwise you have a problem. And pls check on DC and on AC, the plus and minus wiring.
ok, it could be the diameter actually.
The chargers’ datasheets indicate a max 16 mm² terminal (AWG6) and for a cable length < 2m Victron recommends 10mm².
I don’t know how I managed to ignore this information when I set up my system.
In terms of measurements:
The Victron application tells me:
BMV = 13.37v
Chargers = 13.55v
Manual measurements:
Batteries: 13.15
Chargers: 13.4
BUS: 13.26
After disconnecting a charger, the remaining charger instantly sends 28A and switches to “Bulk” mode.
Measurements:
I’ve connected the BMV’s plus to the other battery, and the gap remains the same:
BMV: 13.43v
Batteries: 13.62v
So I took manual measurements again:
Batteries: 13.22v
BUS: 13.32v
Main fuse (closest to the batteries):
Fuse - Batteries: 13.27v
Fuse - BUS: 13.31v
These measurements are taken on the bottom terminal of the fuse. If they are taken on the top terminal, there is a difference of +0.05v, which gives:
Fuse - Batteries: 13.32v
Fuse - BUS: 13.36v
The measurements taken from the fuses of the two chargers are identical:
Fuse - battery: 13.32v
Fuse - BUS: 13.35v
Idem, measurements taken on the high terminal indicate an additional 0.05v:
I left this morning’s settings on adaptive absorption.
The chargers have just switched to “storage” mode.
They continue to deliver 20A each.
They’re rapidly dropping to 18-16A each, so I’m switching them back to “fixe” mode, I need them to charge, I can’t run my generator every day, nor for too long
All right, thanks.
I will soon change the diameter of my cables and pay more attention to my installation.
I’ll come back here to give some news, in case it could be useful to someone later.