I’ve done 7 or 8 generator start integrations on recreational marine vessels now. All have required some variation of pulse timing to start and stop. On the first one I did the thing where you wire the Cerbo relay 1 outputs to the Multiplus aux inputs and add some elaborate assistant programming in the Multi to make the pulse timing work. It worked well enough (and still is) but I didnt like the complexity and the fact that the complexity was difficult for the owner and / or future technician servicing the system to understand. I have since switched to the time delay relay approach. Two are almost always required. Timing of the pulses vary. This has a very small materials cost to it but it can end up adding a decent bit of labor (and thus cost) to the job. It also adds some additional failure points. I was wondering if it would be possible to add the ability to use relays 1 AND 2 for the generator start / stop. When that option is selected you would be given the ability to select the timing settings for the relays; how long they are closed or open. Doing this or something like to would make projects cheaper (materials and labor) and the end product less complex for the same level of functionality.

Side question, is there anyway to do something like this using Node Red already?

just as a query, what type of generators need pulse inputs for start and stop (other than those where there is no engine control module)?
the Victron Gen start system expects there to be some logic between the 2 wire run/stop signal and the generator. Victron used to produce a box for this but no longer do. I have made an implementation with a nano pi, and a few relays, but this has integration problems on gas generators without automatic choke.

I did two Cummins Onan generators last week. Both required about a 20 second pulse to start and 5 seconds to stop. I get that the current system from Victron expects an external logic. Thats sort of the request. Could they change the software such that we can use the existing hardware (relay 1 and 2) to create the logic with in the Cerbo.

https://www.cummins.com/generators/marine-generators/onan-marine-generators

I have a Kohler generator which is set up with a 0.6s pulse for ON and 1.6s for OFF using external delay relays. If the ON pulse is longer than this, when the generator is hot and starts up very quickly it then turns straight off again… :frowning: