Fuses questions for Multiplus-II 24/3000W

Hello,

We are building our electrical system in 24V and will be using Multiplus-II 24V/3000W.

Based on the manual it state a single 1/0 with a 300A Fuse which with marine grade wires (abyc chart) seems pretty fine, if not in engine room and less than 5 meters. But if the temperature rise let say over 40-50 celcius (I guess we wouldn ot be using the inverter if its that high).

But let say we do use it at 40-50 celcius, i beleive 1/0 and a 300A fuse is not gonna protect the wire?

We were thinking to do 2/0 cables… using T-Fuse, then Lynx distributor with 300A Fuse but with engine room temperature that seems risky too.

We are then thinking to use a 175A fuse ( which would be 100% safe ) and we do not plan to use more than 2800 - 3500W on the inverter anyway. I know we would be limiting ourself but is our mat right? Ambient temperature in a campervan can be quite high and i want to be on the “safer” side of things.

Anything i’m missing?

Yes, but doesnt it surge ?

In reality we will only use a cooktop (1800W) and maybe a few device.. so way below (2400W).

I read somewhere that i guess the surge can be 5500W for maybe 30sec .. so yeah your right htat the maximum is mostly 2400W.

Which is good for us.

Yes, it will do 5500w. But it doesn’t tell you for how long.

See this thread in the archive area:

1 Like

Question on the AC Output. Let say we want to simply do

AC-OUT => 20A Braker => GFCI Outlet => (1-2 outlet)

Does that make sense ?

Last question i guess for now.. :smiley:

I know the victron 24/3000A requires 18mm ferrules on AC Input with like 6/3

Can we use 10/3 cables ? If we know we will limit the Input at 15A ?

:(, i found some 6/3 cables (round triplex) i guess that would be better. I wish i could of used my 10/3 oh well… more expense haha :smiley:

Thanks