Is this initial moment when the Boost Factor is triggered only when the load current reaches the input current limit? Isn’t it too late to wait until the limit is reached to apply the Boost Factor?
JB its starting at the setpoint , before here the charge current is already throttles down of course. when the load remains below the setpoint, the power assist will not start.
Doesn’t it trigger the use of the Boost Factor a little before the limit is reached? How much sooner?
Jb No, not sooner.
Basicly every source can be overloaded a little without a big problem, thats happening at most start up currents or switching in a switch mode device. Every fuse ( even the fast version) will not trip that fast.
Is the use of Boost Factor triggered based only on the current level, or does it also depend on the current growth rate?
Jb On the level only. The slope is not taken into the account.
This would be nice of course , but as it is done now it work under the most critical circumstances. Only criteria which messed the power assist up is a high fluctuation in the incoming voltage as the inverter might find it hard to follow/keep synced
If it is used for such a short time, it is unlikely that the effect of using the Boost Factor will be visible on the measurement panel, right?
JB With a digital scop it can be seen, otherwise I doubt you will find it.
If the load continues to oscillate around the input current limit after using the Boost Factor, can it be used continuously?
Jb there is a minimal time that the power assist remains active , (2 sec) , so if the load drops and comes back the power assist will do the same again.
For stopping charge/doing nothing/powerassist no moving parts are involved, only the voltage setpoint which is adjusted contatsnt anyway. So there is no maximal usage for powerassist
So, the fuse on the Ac input will not trip as this 20A will be used 10,1 for the load, and therefore a 9,9 A Burts travels to the input.
Does this mean that 9.9A will be injected into the grid? But what if the system is configured off-grid, so that no current is injected into the grid? Does it still inject it?
JB Off grid , so a generator powered it you mean?, yes, then the initial pulse will travel there. This is the main reason that IF there is a generator and then specially ne with an inverter output on it, the ACinput voltage window should be ideally be Brough to limits that the pulse cannot raise the voltage to much. Standard thats 190-270Vac on a 230V model, so theoraticly the powerassist can raise the voltage to 270Vac to get the current to the desired level
This would not make a generator happy, therefore in these cases the ACin window should be lowered to lets say 245-250 to be sure the power assist will limit itself is boosting with a high voltage
Based on AC Input or AC Output measurement?
JB Based on the AC input ( you might be aware the output is not actively measured, what you see on a minitor is a calculation ACin power/DC power)
Does this mean that if the load remains above the input current limit, the Multiplus will continue to use the entire input current limit and only supplement what is above it?
Jb Yes ! If there would be a DC source feeding the battery, the Multi can be in power assist 24/7
Or does it use a little less than the input limit? How much less? If it uses less, does this amount of less depend on the Boost Factor?
Jb There is a small hysterisis built in to compensate for voltage fluctuation,
Normally a power assist will aim at 85-90% of the setting to stay well below the ACin setting and there is little/no change the fuse will trip
Is it possible for Power Assist to remain on even if the load is slightly below the input current limit? I have seen situations where Power Assist was in use even if the load was below the input current limit, and I have seen reports that the amount of less input current that was being used depended on the Boost Factor (with a lower Boost Factor, the Multiplus would continuously use more input current than with a higher Boost Factor). What is the explanation for this, if the Boost Factor is only used for 50ms?
Jb The boost factor is only the initial burst, after this is not looked at.
Yes the power assist can remain active if the load goes just below the setpoint. There are two major reasons, one is that there is a margin as far as setpoint, so at a 10A setting the power assist aims for 9A , so if the load remains between 9-10 it stays in power assist mode. but hardly uses battery power, Secondly there is the accuracy on the AC measurement. The power factor/losses on the dc and deviation in the measuring makes that the powerasist is not always exact at the level it needs to be (but close).
The larger the system , the wider the current range is on measuring ACinout, the less accurate the unit will be..