Hi. I have an ESS system set up as zero-feed, initialised a year and a half ago and has been running with no issues, except from the fact that there is not enough solar during winter. The system comprised of a Multiplus-II 5kVA, a SmartSolar 150/45, a Cerbo GX and a 10kWh battery with can-connected BMS. The battery is not on any “supported” Victron list, but its BMS seems to be working as a Pylontec clone (battery updates CCL as expected when near full, but there are no forced options under DVCC).
In order to deal with the winter situation mentioned above, recently two additional MPPTs were added on the installation. Since then, I find it that when the battery is full and there is a constant load on the Multiplus, the MPPTs seem to cycle on and off, unable to match the AC load, hence the battery is constantly charging/discharging at 20-30Α currents. I find this non-optimal, since it’s stressing the whole system, and especially the battery. Please have a look at the screenshot, which depicts all 3 MPPTs at the same time period, when AC current draw was CONSTANT at around 3kW.
I was suspecting that the BMS was turning off charging due to a cell climbing too high, which would stop charging, and then the MPPTs would ramp up and so on, so I lowered the maximum charge voltage all the way down to 54.5V, but this behaviour still stands.
Wouldn’t it be a good idea to add a function so as when the battery is full (or near full) the system would try to mach the output demand and the MPPTs would ramp up slower than their normal speed?