Can I use a Victron MPP to regulate charge a DC water heating element without batteries?
I’m not charging batteries, solely using a resistive load (DC water heating element), freestanding- not connected to the grid.
Presumably I need an MPPT designed for a direct DC load control?
As I understand it an MPPT will be more efficient as opposed to charging the element direct from the panels.
I have;
2 x JA Solar JAM66S30
Values for these 505W panels:
• Vmp (voltage at max power): ~38.5V
• Voc (open-circuit voltage): ~45.8V
• Imp (current at max power): ~13.1A
I’ll probably buy a 3rd panel.
I directly wired the two 505W panels to a 48V 1000W heating element.
I tried series and parallel, read some advice somewhere and went for parallel, which may well have been another mistake.
The element has an integrated thermostat.
It turned out to be a mismatch. In parallel the element only ran at
36.78V
14.26A
524W
Naïvely I was expecting 1000W which would have been happy days, off we go. After about a weeks use the element went pop and gave up. Now that did surprise me as I thought it was under stressed. It was rated at 2.5 ohm’s but by my calcs it was running at about 2.9 ohms. Anyway it’s toast , which is a good thing because it wouldn’t have enough grunt to heat 200ltrs. So up with the volts, down with the amps, I’ve ordered a 96v 1000W and a 96v 1500W with thermostats. ( with delivery and special offer it was better to get 2 in case I burn out another).
The plan is;
3 Panels in Series
• Vmp total: 38.5V × 3 = 115.5V
• Voc total: 45.8V × 3 = 137.4V
• Power: ~1515W
What could possibly go wrong?
Would I be better off with an MPPT ( a 150/35 or 45 or even 60)?
Would I need a DC load relay?
Thanks for any help.
Once this is sorted the plan is to get a separate system with batteries because they’ve suddenly taken to cutting the power for the whole country here in Spain. One thing at a time though.