I see your comment about running your AC dive compressor from a 3000w inverter. I am struggling with mine (also 3000w but 240V). The dive compressor is 2.2kw.
Hi there,
I have a victron system with a 3kw Phoenix inverter and am trying to run a 2.2kw Bauer Junior 2 dive compressor.
The compressor motor starts turning slowly, then stalls and the inverter trips out. Obviously the start up current is too high.
If I disconnect the compressor (remove drive belt) the motor starts up no problem. The compressor is unloaded and can easily be turned by hand.
I’m looking for an electrical solution, I could use a mechanical solution like some form of clutch en…
Thats a link to my question on victron community.
Thanks for any information,
Rob