I recommend a bypass switch to connect the loads directly to the grid in case of MP2 maintenance.
I recommend putting critical loads on ACout1 and normal loads either after energy meter on ACin or ACout2. In both cases the MP2 tries to achieve the grid set point defined either by DESS or manually (usually 0W).
ACout2 can be configured to open circuit based on battery SOC using relay assistant in VEconfigure.
ACin, out1 and ou2 are connected via the 50A-AC-bus bar having 50A relays on ACin and ACout2.
my AC PV inverter to a ET112 and then to the AC2 out. The system can see the power input (through AC2 out) and charge the batteries?
=> That’s a perfect in between solution (although less efficient)!
Does Victron Multiplus / ESS needs an understanding if I add an MPPT (from another company) without communication to the Lynx for charging the batteries?
As far as I see, there no DC variant of the ET112 so it can see the load.
You can connect it to ac out 1, then you will also have pv power when grid fails, but your ac pv inverter need to support frequency shift for that (most do) but on ac out 2 it will also work fine
You could add another brand mppt with a victron shunt for measuring, but it can not be controlled by the GX
keep using your current AC PV inverter on AC in and use 2 meters, one for grid and one for AC PV. The PV output can’t be scaled back when prices are negative.
replace your AC PV inverter with a fronius or SMA and connect over network to the cerbo. PV output is controlled by the cerbo.
rewire your panels so you can use a victron MPPT
Option 2 seems best, you can connect all loads and the PV inverter to the AC out so everything works when offgrid. This way you don’t need any grid or PV meter.
Make sure to check if your grid has a neutral!
If you connect a AC PV inverter to the AC out make sure to comply with the 1:1 rule
A bypass switch for maintenance is a good idea.
You will need AREI certification for both the battery and the PV installation, maybe even for the existing installation depending on what you change.
Extra options to take into account are nice. And yes, I will need the AREI certification.
If this calculator was correct, a parallel 6 panels x 2 string may be possible without changing the 4 mm² cable.
This way, I can maybe get an electrician on my roof to create the 6x2 parallel string without changing internal cabling and go with the MPPT and the other suggestions like bypass, etc.
1 panel:
VoC: 36.47 V
Imp: 7.34 A
6 panelx2 strings.
Max power voltage (Vmp): 218.82V
Max power current (Imp): 14.68A
And if this is not possible for whatever reason, I have other options.