Greetings:
I potentially found my answer to this question on the old community site, but I don’t think I understand it, and am looking for some additional clarification.
Original Question: Split Phase dual Multiplus with generator - VictronEnergy
In his answer, @kwindrem said:
> If you need more inverter power, then using a pair of Multis (or Quatros) in a split-phase configuration would be needed. This works great except when presented with 120 volt single phase shore power. You need a transformer ahead of the Multis to create 120/240 volt split-phase power from the single 120 volt shore power leg.
This makes sense to me, if my input was always 120v from shore power, but depending on what type of input I have, I could have :
1 phase : 15 Amps @ 115V,
1 phase : 30A@120V
2 phase: 50A@120V
I have an ATS in the RV that selects between shore and generator, and the generator produces two phases of 120V, one at 30 A, one at 20 A, with unknown phase relationship.
Following Kevin’s suggestion, I can put an AT between the ATS and the inverter(s), but it’s not clear to me if it can handle / auto switch between 1 phase at 120 or 2 phases @ 120, or true 240 to make a true 240 V output…
I think I could solve the problem by:
- Remove the existing ATS and inserting a couple of Q2 -120V in parallel or
- keep the ATS, and insert a couple of split phase MP2-120V
The problem with either of these solutions is that I need more inverter power than the 120V./24VDC products provide. Temperature de-rated at 65 Celsius I need 4kW@120 on phase 1, and 3 kW@120 on Phase 2 of the inverter solution. So, that means moving to parallel 5 kW units on phase 1. Hence why I was trying to go 240V. This is an RV solution, and space and weight are important.
A third solution is 48V system to get more inverter capacity, but I’ve been advised not to use 48V for RVs (safety), and I’m not having a lot of luck finding 48V batteries built for the vibe/shock of RVs. I know I could do series connections of 24V, but when combined with the safety concerns, I didn’t look too hard at a series solution.
So, the questions:
Q1: Is there a mode with the AT can autoswitch between 1 phi @ 120, 2 phi @ 120, true 240 inputs and create / pass through 240V out?
Q2: In the original posting shaneyake asked about using a 3 position, 3 pole switch… My google fu has failed me, and I’ve not found something like this that can handle 50A of current without going to some big grid-grade massive device for many $k. Does anyone know of something RV appropriate?
Q3: Is there another way to approach this problem / solution?
Thank you all.