So I want to pose a question and get some feedback.
I had 2 x 48/5000 (MP2) in parallel, something happened to the masters voltage regulator circuit (2 years in), it would no longer maintain voltage and I was getting swings of 8v under small to medium loads and out to 20 volts on larger loads. The repair is being taken care of by Victron, (Fantastic customer service by the Vendor), however this has taken both MP2 out of service. I reconfigured both to be single units and tested them, The master was cooked, the slave would get to the set voltage ok, but it was still hunting 5 to 8 volts with just a couple of lights turned on. So effectively both out of service.
I had a third which at this point had never been in service it was my backup unit, so this is running the house on its own now, and we are back to the good old days of knowing what the load is /appliances are on before turning on another (large items like kettles, air fryers etc).
So I am considering the following.
- Run 1 MP2 with the assistant set to start the second unit when the load gets over 3500w for 10 seconds, and stop it when it drops below 2500 for 5 minutes. So this would ultimately operate in a pass through / assist mode, (Generator / MP2 style) as the load climbs during the evening periodically to 7kw the second unit would be called. Typically my daily load is around 1kw to 1.3kw, its only when the EV gets plugged in or the AC is running that we sit around the 5kw to 6kw, maxing out around 7kw at night. During the day the fronius Adds to the system capacity…but that would need to change in this setup.
Questions.
a. My thought process is should I have another malfunction of an inverter it doesn’t take out two inverters, just one, and a simple 5 minute bypass cable connection would see one unit out of service and back to a sole source again.
b. The same load is still managed by both inverters, can setup an assistant to stop the primary from charging the battery when AC input1 has power.
Can you see any issues with this ?
Other Options
- Option 2 is configure exactly as before (both in parallel) and hope nothing goes wrong now that the warranty period is 1/2 way through?
- Option 3 buy a new 48/10000 and sell two of the 48/5000, probably end up recovering 1/3rd to 1/2 the cost of the new unit…..not ideal.
I currently have 7.8kw of Fronius inverters on the AC out1 side of the MP2(both isolated awaiting fix of MP2) 2x MPPT’s 450/100 keeping the house alive. In option 1 above I would have to do away with one of the AC coupled fronius units and make it a DC coupled solar. Not really a big issue, I have space on the shed (battery / inverter room is in shed) for those panels. Alternatively, I could up the cable size from the panels to the MPPT, and run the 40m to the shed(leaving them on the house)
Appreciate your comments and feedback / suggestions on this. A youtuber (OffgridGarage) does this cascade inverters using a 48/5000 and a pheonix 48/3000, so I know it will work, but is it a good solution.