Hi There,
Got an interesting one for you all regarding the Earthing between 2 x Standalone Power Systems.
I am a licensed electrician in Australia and live on a very remote Off Grid homestead.
We have our original Standalone Power System (SPS) on our house that uses a Multiplus 24/5000 and this feeds our standard Switchboard, complete with circuit breakers, safety switches and a standard Earth rod.
This system fed our shed which is located 200m away. The shed supply is an underground feed of 4mm2 twin and Earth that was installed by a prior owner.
I know this size cable is not ideal for that run and intend to upgrade it, but for the short term I am able to use 10A @ 230V at the shed without the Voltage dropping and would like to utilize this underground cable if possible in the short term until the upgraded underground is completed.
Over time, our power needs grew so I’ve completed a second SPS at the Shed with its own switchboard, circuit breakers, safety switches and crucially, its own Earth rod.
The Shed has far better solar orientation/exposure plus much more room to increase PV capacity.
The Shed SPS uses a Multiplus 2 48/5000 GX.
My intention is to use the 4mm2 underground feed in reverse to send power back up to the House SPS from the Shed SPS.
The idea is to eliminate the need for a generator at the House SPS and have an auto start generator at the Shed.
The problem I see happening is that the 2 x earth rods (original at House and new one at Shed) might/will create earth loops and therefore nuisance tripping at both the House and Shed, plus possible dangerous currents between the 2 Earth rods .
This is because if I were to connect the Shed SPS up to the House Multiplus AC IN the single earth terminal on the Multiplus creates a permanent point of connection between the 2 earth rods.
Theoretically, I could potentially disconnect the Earth rod at the house (and deactivate the Multiplus Earth relay), but the Earth Fault Loop impedance over that distance in the underground feed would be far to high to properly activate the safety switches at the House by using the Shed Earth Rod.
Similarly, if I disconnect the Earth rod at the Shed (and the Multiplus 2 Earth relay), the Shed safety switches will not operate properly due to the high Earth Fault Loop impedance using the House Earth Rod.
So my question is this…
Using the existing underground feed, how can I have the Shed SPS feed the House SPS to act as Shore Power/Generator for the House SPS?
How can I do this and still maintain low Earth Fault Loop impedance at both the Shed SPS and the House SPS?
Or, is the only proper fix, to run a heavy duty underground Earth cable between the House SPS and the Shed SPS thereby eliminating the need for 2 Earth Rods
Thanks in advance for any advice or ideas.