ve can shunt

Does Lynx Shunt substitute for Battery Terminal Fuse?

Pretty sure the answer is no but any input appreciated.

200amph of 24v Lipo batteries with integrated BMS wired in parallel. Max potential load something like 120 amps. Plan to connect directly to busbars of Shunt VE.Can connected to Lynx Distributor.

The Shunt VE.can manual states

"If the Lynx module is the first in line, the last in line or is used by itself, it is possible to connect batteries, loads or chargers directly to these connections. However, we do not generally recommend this because additional insulation and fusing is needed. "

Sounds like a battery terminal fuse is a great idea. Not sure what they mean by additional insulation.

Thanks




dberdinka asked
pwfarnell edited ·

1 Answer

Cant get VE Can shunt to work.

Help Needed. working on a new system at the moment, multi 2 GX, ve bus BMS, Lynx VE Can shunt. everything is working except the shunt data is not showing up on the gx device, i have aDC loads but when i turn them on No Load current shows. Also cant see the shunt settings in the gx device, the rj45 cable has been checked and replaced and checked again.

christyler asked

0 Answers

Lynx Shunt VE.Can mV values

What are the Amps -> mV values for the Lynx Shunt VE.Can 1000?

rspott asked

0 Answers

Lynx Shunt VE.Can Installation and Wiring

I am aware that a new Lynx Shunt VE.Can is initially set up to have the battery distribution to its left and the load distribution to its right. Is it possible to modify the Lynx Shunt to allow for the battery distribution to be on the right instead?

I am wondering if changing the position of all or some of the five sensing wires inside the unit would allow for changing the location of the battery distribution. If it is possible, which wires need to be moved and to which positions? If this is not possible by physically moving sensor connections, is there a software setting that could be changed?

My system is currently set up with the battery distribution on the right side of the Lynx Shunt. Based on my VRM portal reports the shunt is measuring the current flow in the opposite direction for how the system is connected. As an example, if my battery bank (9.6kW capacity) SOC drops from approximately 100% to 21% and my inputs are 1kWh from the grid and 21 kWh from the PV array, the VRM is reporting my consumption as 15kWh. Based on those input numbers (which I assume are collected directly from the Multiplus and MPPT), I think that the consumption number should be around 29kWh.

My system is:

8 x Battleborn 12V LiPO batteries (configured as a 24V 400Ah bank)

2 x Multiplus 24/3000/70

1 x SmartSolar MPPT 150/85

1 x Orion 24/12-70

2 x Lynx Distributor (used on battery and load sides)

1 x Lynx Shunt VE.Can

1 x Cerbo GX

1 x GX Touch 50

@Matthias Lange - DE @mvader (Victron Energy) @Daniël Boekel (Victron Energy Staff) - user overview - Victron Community

warren-b asked
sarahb commented ·

1 Answer

One cerbo gx, Two shunts to measure another DC supply

Hi.

I have a cerbo gx in the cabin. There I have a shunt from before and want to add an extra shunt. The plan is for it to measure the 24v dc current coming from the wind turbine (Primus Windpower Air 40, 24V) into the battery bank. will this work?

kimelim asked
Stefanie commented ·

1 Answer

Synchronising Ve-can shunt!

Can't synchronise battery Soc for VE-can shunt,pressing the synchronise button on the CCGX menu, seems to have no response or effect!.....is this a bug?

Mark asked
Mark answered ·

4 Answers

Current from Battery Monitor on the CAN Bus from Venus GX

We connected the Victron Battery Monitor to the Venus GX. At which CAN Bus address the current can be read.