How to Limit DC-DC Charger Current on Orion-Tr Smart?

Hey Victron community!


First time posting here, so forgive me if I'm missing any formalities.


I recently bought a Victron Orion-Tr Smart DC-DC Charger Non-Isolated 12/12-30. We are planning to use the charger in a travel trailer with a custom 300ah battery bank. The problem is that we want to wait to upgrade the OEM positive wire from the tow vehicle's battery (it is currently a 10awg wire) to a much larger wire until after we start using the trailer. Per my research, we will need closer to a 2awg wire, which is much bigger and a pain to re-route from the tow vehicle, so hoping to kick the can down the road a little.


With that said, is there a way to limit either max current or max power output on these units? Or is the only way to limit it via limiting the voltage? Are there any tricks to artificially limit the current?


Thanks in advance!

dirtjackson asked
ronhanson01 answered ·

3 Answers

Multiplus 24/5000/120 settings: search mode, max charge current, input current limit

Hi,

I have the above Multiplus, BlueSolar MPPT 100/30, 2x200W/12V serial PVs, 2x200Ah/12V serial AGM batteries, Honda EU2200i generator and have the following questions about three settings:

1. If I have both the search mode and AES switched on, which is over-riding the other or can they work together?

1. For the 400Ah/24V battery set it doesn’t seem possible to set the maximum charge current as low as the generators continuous output 1800W/230V=7,8A. The lowest setting is 25% of something (percentage of what is still unclear? Maybe 100A x 25% = 25A?).

3. The input current limit can only be set to the following values:6,3A (1.4kVA at 230V),10A (2.3kVA at 230V),12A (2.8kVA at 230V),16A (3.7kVA at 230V),20A (4.6kVA at 230V), 25A (5.7kVA at 230V),30A (6.9kVA at 230V), 50A (11.5kVA at 230V). The question is how this setting affects the charging on different loads. It is clear that I should not have this setting to more than the generator’s continuous output power. But is it so, that 1) at no load the genset is charging with current of the setting (e.g. 6,3A), 2) when there is load up until the setting (6,3A), the load will be supplied 100% by the genset and the rest is used for charging and 3) when the limit setting (6,3A) is passed then the load will be covered by the genset AND the batteries and no charging will happen?


Thx.

Dosse asked

0 Answers

Multiplus 24/5000/120 settings: search mode, max charge current, input current limit

Hi,

I have the above Multiplus, BlueSolar MPPT 100/30, 2x200W/12V serial PVs, 2x200Ah/12V serial AGM batteries, Honda EU2200i generator and have the following questions about three settings:

1. If I have both the search mode and AES switched on, which is over-riding the other or can they work together?

1. For the 400Ah/24V battery set it doesn’t seem possible to set the maximum charge current as low as the generators continuous output 1800W/230V=7,8A. The lowest setting is 25% of something (percentage of what is still unclear? Maybe 100A x 25% = 25A?).

3. The input current limit can only be set to the following values:6,3A (1.4kVA at 230V),10A (2.3kVA at 230V),12A (2.8kVA at 230V),16A (3.7kVA at 230V),20A (4.6kVA at 230V), 25A (5.7kVA at 230V),30A (6.9kVA at 230V), 50A (11.5kVA at 230V). The question is how this setting affects the charging on different loads. It is clear that I should not have this setting to more than the generator’s continuous output power. But is it so, that 1) at no load the genset is charging with current of the setting (e.g. 6,3A), 2) when there is load up until the setting (6,3A), the load will be supplied 100% by the genset and the rest is used for charging and 3) when the limit setting (6,3A) is passed then the load will be covered by the genset AND the batteries and no charging will happen?


Thx.

Dosse asked

0 Answers

DVCC doesn't seems to work?

Hello again.

I'm a bit confused with DVCC function.

I've charged my batteries to 100% today, which triggered BMS to stop further charge, but Multi is not stopping, DVCC setting is enabled, BMS is sending all limits to VenusGX correctly, but it looks like Multi is just ignoring it. My DVCC settings are as below:

[image]

Battery is 100% charged, BMS set the charge current limit to 0.0A, but multi is still pushing nearly 1A into the batteries:

[image]

My system is VenuxGX (with ESS Assistant) + Multiplus II 48V/3000VA + AC coupled PV + Liion batteries with Batrium BMS (connected to VenusGX via CANBus)

I've also noticed that the same thing is happening when BMS is forcing limited charging mode (battery nearly full, CCL set to 0.5A), the Multi also is not limiting power to the set current:

[image]


Is that normal??? Am I missing something? Shouldn't Multi limit the power to the set value or I just misunderstood this function?!

Mysik asked
Daniël Boekel (Victron Energy Staff) answered ·

2 Answers

Blue solar 75/15 charge limit

I want to use a blue solar 75/15 to power a load at a max current of 10 amps, ie constant voltage. Ideally don’t want it to charge my battery with the unused power as that is dealt with by a different, bigger blue solar Array. The load will not always be as much as the power available, array is only 100 w, ie not enough for 10 amps..... although I could add a second 100w.......
basically it will be connected to an elec distribution board, that powers all the loads and has its own battery charge algorithim. It also has a display showing all battery voltages/solar currents etc, so I wanted to use it to control and display that stuff and charge the battery.
so, if I connect the load only to the 12v distribution board will that do the above, or does the battery connection also need to be used. I assume turning charge off stops all power, as limiting charge current limits charge and load?

Or any other ideas?


Wingphil asked
ejrossouw commented ·

2 Answers

Wieso lädt mein Victron Smartsolar MPPT Laderegler 100/50 nicht immer?

[image]

Nach der Installation meines Victron Smartsolar MPPT Laderegler 100/50 auf meinem Segelboot habe ich zwar Spannung auf der Batterieseite und auf der PV Seite gehabt, aber eine Ladung ist zunächst nicht erfolgt. Nach einiger Zeit und mehreren Versuchen, einen Fehler zu finden , hat die Ladung dann begonnen. Am nächsten Tag war es wieder dasselbe. Kann dieses Problem daran liegen, dass die laut Unterlagen verlangte Spannungsdifferenz von 5 Volt nicht vorlag (siehe Bild)? Muss an jedem neuen Tag zuerst wieder eine Spannungsdifferenz von 5 Volt vorliegen, bis der Ladevorgang beginnt? Kann man den Wert von 5 Volt verstellen und niedriger vorgeben?

Danke für jeden Rat

Reinhard

Reifla asked
Matthias Lange - DE edited ·

2 Answers

Is there a way to change the 5 Volt difference between the bat voltage and the pv voltage to start the charching sequenze?

Due to the parallel installation of my solar moduls I have only appr 16,5 Volts at the PV side. To start the charging sequence I need a 5 Volt difference to the bat voltage. That means, my bat voltage has to drop below 11,5 Volts to start the charging mode. Is there a solution other than a parallel wiring of my moduls?

Reifla asked
WKirby answered ·

1 Answer

SmartSolar MPPT 100/20 turning the load "On" then "Off" then back "On".

I purchased a Victron SmartSolar MPPT 100/20 Charge Controller. I am having a problem with the charge controller cycling the load "On" then "Off" then back "On".


Description of failure:

1. The charge controller will show that the load is set to "On".

2. A 12v fan is connected that draws a max of 9W of power or a car cell phone charger is plugged in (without the phone connected or charging)

3. The charger controller will show that the load is turned to "Off"

4. Have a pause for 1 to 2 seconds

5. The load will then be turned to "On"


Notes: The charge controller never shows a voltage below 12.6 volts from the battery so I know that it is not pulling a large load from the battery.


I don't see how a 12v phone charger without a phone connected could be tripping the 20A capacity of the controller.

SailboatTN asked
SailboatTN commented ·

1 Answer

How do I make software changes to my 48/3000/35 Easysolar to accept Ryobi RGN2500B?

I have read Multiplus Genrator FAQ and cannot access 'Disable UPS mode', 'Enable Dynamic Current limiting' or 'Weak AC' through Color Controller to make software changes to accept my 2000W 8.33A generator. It is not recognised at all despite setting Input 1 to generator. I assumed Easysolar came with easy BT or WIFI interface. Do I have to purchase additional hardware to make such changes?

I am running offgrid 240V in New Zealand. I have updated software to latest version by Ethernet through USB connection to my mobile data on Tablet. Since update I have been unable to access internet. My system has been registered on VRM. I don't have access to local Victron support so are configuring myself.

I got a 600Mbps: 5GHz 433Mbps, 2.4GHz 150Mbps that supports 802.11 ac standard wifi dongle but this has not been recognized by system. I have USB connected my phone and have been unable to access any internet or VE Configure settings.


southost asked
Daniël Boekel (Victron Energy Staff) commented ·

4 Answers

Is DMC GX still required for systems with Ve.Bus BMS for changing input current limiter?

Is the DMC GX still required for systems with a Ve.Bus BMS for changing the input current limiter?

The CCGX manual suggests that the DMC GX is still required if you have a Ve.Bus BMS:
From: https://www.victronenergy.com/live/ccgx:start#vebus_inverter_charger_monitoring

[image]


Are the current limit settings, which are now present in the CCGX, sufficient for for controlling input currents in systems with Ve.Bus BMS batteries without the need of a DMC GX?

[image]


Thank you,
Nate

Natebert asked

0 Answers

Limiting Orion TR Smart 12 12 30 current

I have fitted a 12 12 30 (Smart) to my caravan to charge the house battery and help with the fridge load using the tow vehicles alternator.

The Smart version is great with programmable voltage sensing capability but 30a is just too high for the wiring I have and the distance it travels. I believe the 18a equivalent would be ideal but they don't appear to be available at the moment (at least in Australia).

Is it possible to cap the output amperage?

Thanks in advance.

Luke W asked
koh commented ·

1 Answer

Current limiting using a Quattro

Hi All,

I have a Victron Quattro with a Venus GX. We have solar panels and mains input (from a hydro-electric system). The amount of electricity from the hydro fluctuates and at the moment is very low as it is so dry. I would really like to set the current limit so that once the current limit is reached the power is then drawn from the battery. I can't work out how to do this. Can you help?

Thank you.

Leander

Leander asked
JohnC commented ·

1 Answer

Load output inrush current HW fix availability for Bluesolar 75/15

Hello @mvader (Victron Energy),

I'm wondering whether your HW fix for the issue "smartsolar 100/20 load switches off in float mode" and other loads is already available today in the BlueSolar 75/15 series design?

Documented by "mvader" in

>> "smartsolar 100/20 load switches off in float mode" on

Mar 02 um 9:39 PM:

Here are the serial numbers per when the (hardware) change was implemented:

  • SCC075010060R SmartSolar MPPT 75/10 Retail HQ1935
  • SCC075015060R SmartSolar MPPT 75/15 Retail HQ1935
  • SCC110015060R SmartSolar MPPT 100/15 Retail HQ1947
  • SCC110020060R SmartSolar MPPT 100/20 Retail HQ1911

The 100/20 that we currently ship from our warehouses has the improvement. As do the 75/10 and the 75/15. The 100/15 is still shipping with hardware from prior to this improvement, due to stock levels of older production batches.

<<

Has my two week earlier bought (from Offgridtec) BlueSolar 75/15 (+ BT dongle) with serial nummer (pls. see below) also fixed this BD35 compressor inrush current issue yet (that I highly rely on) or do I need to replace this device with which SmartSolar charger instead or when will it be available?

Many thanks in advance for your help and BR!


[image]

edmond99 asked
edmond99 commented ·

0 Answers

AC input current limit setting is very different from where it actually limits.

Got a Quattro 12/5000/220-2x100 120V running firmware 2733430. (Same system as in this old post.) Since then, I've beefed up the shoreline to a true 20A circuit, and adjusted the input limit to 20A accordingly.

Sometimes the system will happily draw 19.8A from the shore, and sometimes it'll limit itself at 11.6A and go into PowerAssist for my roughly-2kW load.

Here's the weird thing: If I increment the input current limit just a little, the actual power drawn from the shore increases dramatically. Here's my observational data:

Current limit set in VEConfigure Actual current drawn Load and status
20A 11.6A 2kw, PowerAssist assisting
21A 12.6A 2kw, PowerAssist assisting
21.5A 20.2A 2kw, battery charging
22A 20.7A 2kw, battery charging
30A 27A 2kw, battery charging


AC input voltage is roughly 108-112V in all cases.

So why the huge jump in actual current, for a tiny bump in the set limit? It's not correlated with input voltage, and I can't identify anything this behavior is correlated with. I've tried setting WeakAC and it had no effect on the behavior either way. Shore power is 60Hz grid AC, so it's not like a generator is lagging its frequency or anything. What else should I be checking?

For the moment, I'm leaving it at 21.5A to keep the battery from draining while on shore power, even though it slightly overdraws the circuit's nominal rating, the breaker doesn't actually trip until a bit higher than that. ;)


nbezanson asked
Jack Peters commented ·

3 Answers

Sustain current too high?

Hello Victron fellows,


I have set some Li ion with Victron inverters, always for self consumption with PV inverters, but this one is cracking me up. This system consists in three 48V Multiplus II 3000/35 as a three phasic system, and an ESS assistant is set. The sustain voltage is 43V and cuttoff around 42V. The modules have a low SOH, but the system should work anyway. It charges and discharges correctly, up to the point where my BMS disables allow to discharge at around 48V, because there are low cells (it should discharge to less than 42V if it was good).

Then, Sustain mode is active and the current goes UP TO 90A. Of course when this happens the voltage raises quickly, the allow to discharge comes on again and it goes to Discharging mode. Repeating the process endlessly - Even without PV POWER, that means it consumes a lot of power.

My question is, why does it go up to 90A, since sustain mode should be 5A per unit and how can I solve this?

Thank you very much!

Jorge Folgado asked
Daniël Boekel (Victron Energy Staff) answered ·

1 Answer

AC INPUT 2 VICTRON QUATTRO

Hello everybody,

I have a Victron Quattro 5kVA/120V setup with a MPPT 250/100 and lithium batteries BYD B-BOX PRO 10.0. AC INPUT 1 has mains electricity of the grid.

I want to use the AC INPUT 2 not with a convencional generator but with the output of a eolic system that is installed in the same place, with another battery bank. The inverter output of this system is: 8kW / 127V single-phase (máx output current 63A).

I didn't find any question here about a hybrid system (solar+eolic) like that. The Victron setup will be the same as with a generator in the AC INPUT 2?

Is there anything else to pay attention besides the configuration?


Bruno Santos asked
Paul B edited ·

1 Answer

Is smart solar 100/20 able to limit by itself charge current at 20A or will it be damaged if too much power is provided by solar panels

In smartsolar datasheet it is written :

maximum battery current = 20 A


doest it mean that current to charge batteries will be properly limited to 20A or will it be a problem if, for instance, 400W are provided to victron and then : 400/12 => I = 33A. Will battery charge current be limited to 20A ? or will it break the victron ?


best regards

iostrym asked
Daniël Boekel (Victron Energy Staff) commented ·

2 Answers

Phoenix Multi Compact 12/800/35-16 Overload Warning and Low Battery Alarm

Dear all, we have recently bought a Multi compact 12/800VA together with a SB SUNLIGHT AccuForce 12V - 150Ah Solar VRLA Battery in order to replace an ONLINE UPS in a on-Grid Photovoltaic 500kWp installation. The system works in 12V mode. The inverter charger is connected to the AC grid and the only load is the Protection Relay (SEPAM) from Schneider Electric installed on the Medium Voltage Switchgears Board. The charging mode is 99% in "Storage" mode cause the load is very little. The problem we are facing is that after two or three days of operating the Inverter goes to fault mode and the alarms we got is overload and today together with a Low Battery Alarm and the PV station goes out of the Grid. The only thing we do when the fault comes is to go and turn off and on the inverter/charger and the problem is (temporary) solved. Today the fault happened, we got a "grid lost" e-mail message, when we reached the inverter the fault was gone (only the green light when on), as it seems the inverter was inverting. We turned off and on the inverter and the inverter "saw" again the AC grid.

Since we bought the inverter we did not do any optimizations or changed any settings for example for the current output (everything is as it came from the distributor). The system also has a Color Control GX and we can monitor the system from the VRM Portal. Please see attached pictures, videos. Any ideas for the fault or settings needed are much appreciated! No clue why thr fault takes place, on the other hand the overload maybe comes because the SEPAM maybe draws a lot of current in order to power the motorized central medium voltage circuit breaker.20200316 Status Monitoring2.jpgfaults.jpginput current limit.jpgMV SEPAM.jpgBattery.jpgGrid connection restore.mp4

trienergiamixaniki asked
trienergiamixaniki commented ·

0 Answers

CCGX Unable to set Multiplus Input Current Level below 1

Hi

I am attempting to control my Multiplus AC Input from the CCGX by setting the value to 0, whenever I set the number to less than 1 it always reverts to the value of 1. A value of 0 is also not accepted and reverts to 1. AES and PowerAssist has been disabled in the Multiplus Inverter settings.

Equipment details as below:

CCGX
Firmware Version: v2.51

Multiplus Compact 12/1600/70-16 with VE.Bus BMS
Product ID: 2606
Firmware Version: 469
VE.Bus Version: 2606469
VE.Bus BMS Version: 1145110

The same behaviour occurs if I use VictronConnect to connect to the Multiplus via a USB/Mk3 interface. I have also attempted to set a lower value using modbus and encounter the same behaviour.

How can I set this value to 0?

Thanks
Gary

Gary@105 asked
Gary@105 answered ·

4 Answers

atlas 24V/2000W low AC voltage output

hi, after the newly bought espresso-machine would not funtion, i measured the voltage and realized that it was only 190V (fully charged batteries, 6x150 ah, 12V). any hints how to fix that? thank you

docker38 asked
Daniël Boekel (Victron Energy Staff) commented ·

2 Answers

ESS Dynamic cut off paramters for OPzV Hoppeccke

Hi!

I need help about the parameters for cut off. The standard values makes that when the Multi draw up to 2500 - 3000w, they stop invert by low battery.

I have 24 cells Hoppecke 6 OPzS 600 that have a capacity:

C10 - 686Ah (1.80v)

C5 - 590Ah (1.77v)

C3 - 510Ah (1.75v)

C1 - 353Ah (1.67V)

I don't know if the voltages values from Hoppecke for each C value is the nominal o the limit when the battery is empty.


Many thanks!

Angel

Gurybush asked
mvader (Victron Energy) answered ·

1 Answer

Solarcharger and it's max PV current (oversizing PV-Array)

Hi Guys, I am new on this forum, but I would love to get some clarification regarding the maximum currents which may flow at the PV-array. I have looked around this forum, but I did not find a proper answer till know, with a clear explanation WHY/ HOW the MPPT is limiting currents...

another discussions around this topic is for instance: smartsolar-maximum-input-current

To be clear, we All know and accept that the Voltage limit (Voc) shall never be higher than the MPPT allows...


The questions comes from the manuals/ Data-sheets which list 2 different footnotes...

@ Manual:

Footnote 2): A higher short circuit current may damage the controller in case of reverse polarity connection of the PV array.

[image]

@ Datasheet:

Footnote 2): A PV array with a higher short circuit current may damage the controller"

[image]


And generally speaking people tell me that the PV-currents like Isc, may never be able to be higher than the rated current of the Solarcharger at it's PV-side. BUT, if I read the footnotes from both Manual and Data-sheet I get confused, and would like to better understand why Victron is writing this.

For me are these SolarChargers smart devices which can control Voltage and currents very well. It is for instance possible to lower the charge current by changing it's settings via the app. Why would then oversizing a PV-array (with e.g. a SmartSolar 75/15) with respect to Isc be dangerous for the device? If I would hook 2x 60cell PV-panels in parrallel for instance, theoreticlly a Isc of around 20A could occur.. But to my opinion this Isc Current will never occur within the solarcharger because it is searching for it's MPP. On the other hand Impp could theoretically still be higher than 15Amps, like around 17Amps which would be too high as well. BUT, Is this device not able to limit its input current (in this case max. 15Amps) by deviating from it's MPP working point (like lower it's Amps by increasing the Voltage to Ioc)??

[image]


I downloaded version 06 of following Manual https://www.victronenergy.nl/upload/documents/Manual-BlueSolar-charge-controller-MPPT-75-10-75-15--100-15-EN-NL-FR-DE-ES-SE.pdf:

and I download the Datasheet of the same MPPT, Datasheet-Blue-Solar-Charge-Controller-MPPT-75-10,-75-15-&-MPPT-100-15-EN.pdf).


Well looking forward for some comments/ Questions/ answers and/or clarifications :)

Ruben




Ruben asked
Ruben commented ·

1 Answer

Minimum input current limit and PowerAssist

Especially if I have a small AC input fuse the PowerAssist is needed to feed the loads.

Today we had a customer with a RV he wants to drive to Finland and at some campsites they only have 3A sore power. But he have a Quattro 12/3000 230V, so with activated
PowerAssist the minimum input current is 4.5A.

What is the reason for the limit in combination with the PowerAssist? Is this a hardware limitation or can this be change with a future FW?

Matthias Lange - DE asked
Daniël Boekel (Victron Energy Staff) answered ·

1 Answer

MPPT 100/20 load output reading current wrong?

Greetings,

I am using an MPPT 100/20 charge controller with a DC/DC Converter and a pump at the load ouput. Although this load is asking for a maximum of around 17A from the controller, the reading at the controller is 20A and it disconnects.

Could this be a defect from the product? Is it perhaps reading the current wrong or it has too high sensitivity?

Thank you for your help,
Ana

Ana Carvalho asked
JohnC commented ·

1 Answer

Can I control the discharge current from the batteries to load output on my MPPT 100/20 Charge Controller?

I have a MPPT 100/20 Solar Charge Controller connected to Lithium batteries. The load output is connected to my load (a pump).

In the settings I already limited the charging current to 5A. Can I also limit the discharge current from the batteries?


Thank you!

Ana Carvalho asked
WKirby answered ·

1 Answer

Pylontech Charge Current Limit

I have 3 Pylontech US2000 Plus connected in parallel with a MultiPlus 48/3000/35 and a MPPT 150/45.

The CCL is set at 30A by the battery, is this because the MultiPlus can only charge with 35A and the battery knows this? I haven't connected the PV panels yet but when I do should I see this value raise to 75A as the MPPT can provide an extra 45A?

The DCL is set to 75A so I'm assuming that all 3 batteries are being detected and everything in the setup is fine. Any comments welcome please and thank you.

[image]

Spudgun asked
Murray van Graan commented ·

3 Answers

No Load output current sensing

[image]


Hi all,

We are employing the SmartSolar MPPT 75/15 in a number of remotely located instrument cabinets that will eventually be inaccessible to people. To remotely monitor the SmartSolar device, we are utilizing a Serial to Ethernet bridge. This device also allows us to also perform any mandatory firmware updates remotely, but with a caveat.

In order for us to be able to take advantage of the SmartSolar’s load current sensing, our load (‘Ethernet Devices’) needs to be connected to the LOAD output. However, during a firmware update, the LOAD output switches off at the 4% mark, thereby causing the firmware update to stop indefinitely. D1 solves this issue by sourcing power directly from the battery (Batt) when the LOAD output switches off (during a firmware update). The side effect of connecting the Batt terminal to the LOAD via D1 is that the LOAD output never comes back on, despite VictronConnect stating that the LOAD is ON. Instead current continues to flow through D1, therefore current sensing on the LOAD terminal never takes place. Only by utilizing D2 does the load current flow through the LOAD terminal and reported in VictronConnect.

Our question: Before we invest time in building a low-power-loss device (FET in place of D2) to circumvent this issue, is Victron able to provide a firmware update that ensures that either the SmartSolar LOAD output always stays on during a firmware update, or at least a firmware update that would allows us to omit D2? And failing a response here, how can we contact Victron directly with this request?

Thanks in advance,


Michael

Michael Vesovic asked
klim8skeptic commented ·

2 Answers

Multiplus charge current isn't reaching its potential maximum?

i'm charging my batteries from a generator on Ac input- 1, it won't charge at more than 21 A DC even though i have set the DC charge limit to 35A, i have also played with the AC current limit but it still won't charge at a higher current, any ideas?

(Multiplus 48/3000/35-16 230V, pylontech us2000b x2)

Thanks

Lief.

@Guy Stewart (Victron Community Manager)

lief ryan asked
lief ryan commented ·

3 Answers

AC Current Limit when using ESS as a grid parallel system

I have a Multiplus II GX system which is installed with the ESS application. It's connected to the UK grid via a single phase 100A supply, connected to AC IN of the Multiplus.

All loads and an AC coupled solar inverter are also connected to AC IN of the Multiplus.

The Multiplus is able to balance the grid supply close to zero, charging the batteries off of solar and discharging them as required. I also have time of use tariff which enables the Multiplus to charge the batteries over night.

The issue I have is that I run a lot of loads over night in the cheap period of my tariff including a 32A electric car charger. This regularly take my load over 50A.

The Multiplus needlessly regulates its own charger down in this period and on occasion supplements my grid supply from batteries. This is needless and results in me not having a full battery bank at the end of the cheap time-of-use period.

I can't increase the current limit beyond 50A on the Multiplus or seem to disable it. It is not needed in a parallel grid connection as I have it, as far as I can see.

Can somebody advise me as to whether I have missed a setting or if this is something Victron need to consider in a future firmware update. I want to be able to heat my water, charge my car, batter bank, run my dish and clothes washers during my off peak period!


Marcus Fosker asked
garethcurtis commented ·

3 Answers

Peak Current Time - BatteryProtect 48V-100A

Does anyone know what the max peak current (250A) time is on the BatteryProtect 48V-100A? It's listed as 30s on the data sheet for the 12/24V version but its silent on the 48V data sheet..

jonaslobitz asked

0 Answers