What size battery storage is recommended for a 3kwp pv system?

Hi, I'm currently in the process of building a 3kwp pv system. Im not sure how many batteries I will need. The batteries need to be either 12v or 24v if possible. Thankyou.

ggi2020 asked
nobodyspecial edited ·

1 Answer

Multiplus inverter low battery Alarm as the power demand increases

Hello [Victron Staff] and @Alexandra ,

I recently installed a backup system consisting of a Multiplus 48-5000/70-100 with 12 Gel batteries of 200Ah each, for a total capacity of 600Ah-48V, the multiplus automatically starts a 13KVA generator when the load exceeds 3500W, and the customer wants to reduce its fuel consumption by increasing the power of the inverter.

The problem is that I noticed that the customer's load very often goes from 2600 to 7000W when he turns on the microwave, as well as all his air conditioners, even if it lasts only a few minutes, and this produces a strong drop voltage in the batteries (High DC ripple)leading to the starting of the genset.

The section of the cables between the inverter and the batteries had been well respected during the installation, this means that the voltage drop cannot be caused by an insufficient cable cross-section and leads me to believe that the batteries are small compared to the load.

What formula can I use to calculate the current drawn from the batteries when the load is high(7500W), and thus determine the optimal capacity of the batteries?

I thank you in advance for your quick reply.

Deutch asked
Alexandra commented ·

3 Answers

LifePo4 200Ah x 2 30% reduced capacity with super long bulk charging times

My 2019 (from former boat owner) purchased 2 x 200 Ah LifePo4 Victron batteries have a significant reduced capacity. Bulk-Charging from landline via Philippi charger and solar bulk charging take forever. The maximum capacity is terminated at 280 Ah in sum of both batteries. The B2B system to an AGM is working fine. The alternator charger (Sterling) from the vessel's diesel to the starter is fine as well.

How can I locate the problem within the batteries? If there is a problem, who can be contacted at Victron, since the batteries worked perfectly the last 2 seasons...

ambutiva asked

0 Answers

Parallel 65AH and 100AH battery in 48v ESS system

I have 4 strings of 4x65AH battery's can i ad a string of 4x100AH battery's to increase the total capacity for my ESS system MultiPlus II 48v 3000VA

The battery's a SUN Battery SB12-65 (12V65AH) and SB12-100 (12V100AH)

https://www.battery-kutter.de/main/additional_files/Daten%20Webshop/SUN%20Datenbl%C3%A4tter%20Nov%202019/12V/SB12-65.pdf

https://www.battery-kutter.de/main/additional_files/Daten%20Webshop/SUN%20Datenbl%C3%A4tter%20Nov%202019/12V/SB12-100.pdf


jens-due asked
marekp commented ·

2 Answers

BMV712 battery capacity percentage

Just installed a BMV 712 on a ”house bank” of 2 deep cycle AGM Firefly’s in parallel. Just learning how to use the system but it appears that the “battery percentage” indication doesn’t go down as power is used. The Bluetooth app shows the number of amps being used...it also shows a negative value when I turn on the battery charger. But after disconnecting from shore power and leaving my fridge and water heater running the battery percentage is still at 100%. Could anyone help out with an idea as to why this might be. Much appreciated. Thanx.....

seahawk asked
seahawk commented ·

3 Answers

MPPT 100/20 Battery Bank Size/Capacity?!

Am I correct in thinking:

I can keep adding to my battery bank capacity (Ah) as long as its 12 or 48 V and I don`t need it recharged fast with the current MPPT 100/20 Victron charge controller and the limit is how many panels I can add (up to 300W for MPPT100/20)?

I`m planning to increased my Battery Bank Capacity (add a second bank) from 160 to 580 Ah as I was given 2 X 210 Ah Lead Acid Batteries for free, but at the same time don`t want to damage my Victron 100/20...

Thanks,

Sam

zandi asked
wkirby commented ·

2 Answers

Probleme mit Victron GEL Batterien 220 Ah

Hallo allerseits,

ich habe Probleme mit 2 Victron GEL Batterien 220 Ah. Die wurden im Juli 2018 in einen Wohnwagen eingebaut. Seit März 2020 haben beide Batterien nur noch eine Kapazität von ca. 10 %. Getestet wurde mit einem professionellen Batterietestgerät, das über mehrere Tage definiert die Batterien auflädt und entlädt und dann die Kapazität berechnet.

Beide Batterien haben jeweils einen Victron Solar-Laderegler 100/50 und ein jeweils eigenes Victron Ladegerät 12-25. Sie sind auch nicht hart parallel geschaltet, sondern über einen Victron Combiner zusammengeführt, so dass ich Querströme ausschließen kann.

Die Solaranlage liefert 850 Wp, so dass immer genug Nachladung zur Verfügung stand. Der Wohnwagen wird ganzjährig bewohnt. Solange der fest steht (98% des Jahres), hängt der am Landstrom, so dass auch die Victron Ladegeräte die Batterien stets voll gehalten haben. Es hat bei einigen wenigen Fahrten im Winter mal eine Entladetiefe auf ca 70% gegeben, also weit entfernt von den 50% entnehmbarer Kapazität. Gemessen wurde dies über zwei Victron BMV.

Jetzt hat mir der Händler mitgeteilt, dass jeder Kalendertag einen Zyklus darstellt, und die Victron GEL Batterien nur eine Zyklen-Lebensdauer von 600 - 700 Zyklen haben. Das würde ja bedeuten, dass Victron GEL Batterien ganz generell nicht in Solaranlagen tauglich sind, wo sie jeden Tag mit Sonnenaufgang einen neuen Zyklus beginnen.

Wer kann mir was dazu sagen? Alle 2 Jahre zwei neue GEL-Batterien von Victron zu kaufen ist mir zu teuer. Wenn die auch nicht länger halten, als billige Batterien vom Discounter, warum dann Victron?

Nette Grüße

Gode

gode-re asked
Matthias Lange - DE commented ·

1 Answer

Need a battery backup for the night alone; thought of a single PYLONTECH 48V 2.4KWh

Hello friends

I currently have 37 panels feeding two 5.0 kW inverters with 4 MPPT total. Different position and size panels force me to have all strings covered. During the day I have between 60 to 80% of my power needs covered (on grid installation).

My problem comes once the sun goes, where I have nevertheless some consumption that I want to sort it out. The usage ranges from 250 to 500W on a constant basis, so I thought of getting a simple inverter/charger and one Pylontech 48V 2.4kWh, with no panel attachment; the battery would be charged during the day and if the Pylontech runs out of juice I would then allow the grid to take over.

What do you suggest I use as an inverter and how well do you think a single Pylontech will cope with that small consumption?

Best Regards,

SpanishFlyer

spanishflyer asked
gherlt answered ·

2 Answers

Remaining Battery Capacity display

I have a 200Ah lead acid battery so 200 is entered into my BVM-712. Is the battery percentage display showing 100% (fully charged state) to 0% completely dead and probably ruined? or is it smart enough to show 0% as 100 amps have been used (50% of total amps and probably down to 12.2v)? If the display shows 0% as completely dead and ruined, should I set the battery capacity to 100 instead if I want 0% to be displayed when 50% of the total amps have been used?

wog42 asked
wog42 answered ·

1 Answer

Add more battery or more panels?

My system is ~3 months old and has been working well through our NZ summer, but, on cloudy days the battery voltage drops into the <50% SoC range. With winter coming up, I am trying to prioritise between adding battery capacity or adding panels. My sense is that it's 'now or never' for battery because I hear that new batteries adopt the 'age' of existing batteries.

My question is, what information produced by the system should lead me to decide on more batteries or more panels? Hoping someone can help...

My off grid system comprises:

  • 6x 320 W Trina brand panels (roof mounted so point more east than optimal)
  • 3 kW Victron EasySolar II GX (seems to consist of:
    • SmartSolar MPPT 250/70 -Tr charge controller
    • Multiplus-ll] 48/3000/35-32 inverter/charger
    • connected to VRM about 1 month after install )
  • BMV 700 battery monitor (no VE.Direct connection- should there be?)
  • 4x 12V 260 Ah AGM batteries in series

Our power draw averages around 250 W 24x7 plus 30 W for the EasySolar II GX itself. VRM says over last 30 days, consumption has been 171 kWh and production 192 kWh. I haven't found anywhere that VRM (or the remote console) tells me "but production would be higher by X if you had more storage".

Hope someone with more experience can help.

Thanks, Graham


spicedreams asked
Eduard answered ·

5 Answers

Skylla-TG 24/50 capacity of batteries

GD, sir/madam,


What can cause using batteries with this charger with smaller capacity than minimum adviced by manual (minimum 150Ah, we use one set - 24v 560A 70Ah and second set with second charger - 24v 815A 50Ah)? Last time the working time of this kind of batteries is about 1year, after charge starts fall down, should I adjust any of float/equalize/boost charging time? Thank You

neutral asked

0 Answers

Calculate DYI Lithium battery pack Ah capacity

Hi All,


I build 3 DYI jehugarcia (youtube) 18650 battery packs, each pack consist of 9 times 7x18650 cells with a 24v output. So, in total 63 cells. Each 18650 has an average 2400mAh.

So, in a grand total I have 3 packs of 63c = 189 cells.

Each pack has it’s own BMS and they are charged by a Victron 100/30 MPPT Solar charge controller. A BMV 702 keeps an eye on things and a Raspberry PI with VictronOS on it to log statistics to a VRM dashboard.

All well so far and after weeks of charging and discharging the cells are still very much balanced. A Victron Battery Protect as a measure to prevent to low a discharge and opens at float voltage to keep the MPPT as maximum power. Basically, this pack functions as an equalizer as the total capacity isn’t enough for off-grid purposes. (In The Netherlands we have clouds now and then with the sun disappearing).

The issue I have is to calculate the correct total Ah settings in the BMV shunt. I think each pack of 9 has a 21Ah capacity, so a total 63Ah. But the key question is, did I calculate it correctly?

Hope one of you can assist.

Kind regards,

Robert





robert-welling asked
robert-welling commented ·

3 Answers

Evaluate battery capacity

Hi everyone,

My lead battery (12 OPzS) is getting old (9 years). I am figuring out how to evaluate its actual capacity. The steps would be:

  1. Diminish the reporting frequence to VRM to limit error on times
  2. Equalize, measure the electrolite density
  3. In the evening, take note of time (h1) and SOC (S1) of the end of solar charging or at the very beginning of decreasing SOC;
  4. Cut off the feed from panels
  5. Next day follow SOC until 50% (s2)
  6. Note time (t2) and put back on the feed from panels
  7. From VRM note total load L between t1 and t2
  8. Cx=100*L/(s2-s1)
  9. x=(t2-t1)/(s2-s1)

I will not try to evaluate the voltage: not accurate. The electrolyte density should be enough

Any other method?

Thanks

Lionel SEYDOUX asked
mvader (Victron Energy) answered ·

1 Answer

Can my van electrical setup power an induction stove?

Hi there,

I have a van that I am building out and trying to straighten some things out in my system as I design for kitchen.

The basics:

  • I have 400W of solar on roof.
  • I have 200ah Lithium Ion in battery bank. (I ran some calcs early on and was looking at ~180ah of use per day, so 200ah seemed doable. I left a space open to drop in another if needed.)
  • I have the 3000W 12 V MultiPlus Inverter Charger. (Some of my calculated items pulled a good bit of wattage (hot water kettle=1k W, induction stove ~1-1.8k W) so I figured Ok lets do the 3k W.)


I am hitting a lot of points where the inverter just won't budge though. Sometimes I'll be at a good charge say 75 - 80% of capacity and the inverter light will switch to "low battery" when I turn on the 1k watt hot water kettle. Really, at 1kW? No go. If I start the car, the kettle works. I haven't even bought the induction stove yet since I'm running into these issues.

I saw somewhere that potentially I would need at least 3 x 100ah batteries just to give enough current to the 3K W Inverter to do its thing. Is that right??

I'm hesitant to drop another $1k on a battery, although I would do it if it let me run my whole setup with the induction stove smoothly. It starts to worry me though that maybe I couldn't fill the 300ah battery bank fully with only 400W of solar. I've heard good rule of thumb is 200W solar per 100ah battery charge. I have enough room on the roof for another 50V panel..maaaybe 100W. So I'd be at 450W-500W, not the ideal 2:1 ratio. I do have an Orion that charges while I drive... so there is that. I would hardly ever be parked anywhere for days on end without moving. This is mostly a family extended trip mobile. Going for several days up to 2 months at a time remote work/travel trips. I also have a shore power hookup but don't plan on relying on that for steady refill, more of an emergency backup thing if in a pinch.

The other option would be to just swap out the 3k W inverter charger for the smaller 2k W inverter charger - if that is in fact a more appropriate current draw on 200ah batteries- not buy another battery, and just go propane setup for the kitchen stove instead of the induction stove. Thoughts? What say ye?

Recap:

  1. Could my 3kW inverter charger (and solar setup) function smoothly with an additional 100ah battery and be able to supply for induction stove? Or
  2. Cutting it too close and best to go to 2k W inverter charger + propane setup?


vannie asked
vannie commented ·

2 Answers

Can I connect two Isolated Orion converters powered from different battery banks?

I want to have a common DC bus for powering a system. We already have a battery bank that has been working for a couple years and we are adding a new battery bank for expansion. Can I include an Isolated Orion DC-DC at each battery bank prior to the Bus to couple all the loads in one bus?

macevedo asked

0 Answers

Battery choice - guidance requested

So I have a small travel trailer with limited space for a battery. Have a Victron Solar controller and SmartShunt but looking for a better capacity battery than the cheap one that it came with. Draw is a handful of LED lights, USB ports etc - no need for large current draw but capacity and lifespan are king

The current battery box is 280x175x244mm so want to look for something that sits inside the same footprint

I am looking at the BAT412110081 AGM Super Cycle or the BAT412600104 Deep Cycle Gel as the two that will fit.

Which would people recommend as the better choice and which has the larger capacity?

Thanks in advance for the help!

ttttfrosen asked
Rob Fijn commented ·

1 Answer

Dumb question? Series and Parallel batteries.

Hi, this may be obvious, but I've got to ask...

I have a 12v battery bank consisting of 4x 6V, 200AH, AGM batteries.

I have 2x2 connected in series to form 12v, then these blocks of two are connected in parallel - giving a 12v system.

My question is: What is the total AH size of my battery bank. Is it simply the combined total of all batteries? ie 4x200AH=800AH

Or is it the size of only those in parallel? ie 2x200AH-400AH?

Thanks

mlsp asked
mlsp commented ·

2 Answers

what settings do I use for these results on my IP65 24|8 ?

what settings do i need to use to get these results? I am lucky if i get 10Ah charged in a day

[image]

hibrn8 asked
seb71 commented ·

2 Answers

Question About batteries

I'm struggling to understand batteries, I have a small solar installation SmartSolar 100/30, SmartShunt and Smart battery protector in exhibition trailer which is currently being used as test rig, I was using two Flooded leisure batteries in parallel 220AH effective. I Run a 3.9A (Lights and network switch) I calculate that at 3.9A (4A.) 220AH/4 which I estimate should run for 55hrs, runs for about 2hrs before the BatteryProtect kicks in.

I have purchased AGM battery for testing cos I'm looking at replacing my 2 x 110AH flooded leisure batteries with VE 110AH AGM batteries in a slightly more complex installation in the camper and wanted to do some comparisons.

I am thinking the flooded batteries are no longer serviceable although the indicator display is green on both.

The 110AH AGM battery I would estimate 110AH/4 = 27hrs running time and not even coming close to that. What sort of running time would you normally expect with such load?

What is the maximum discharge point for AGM batteries? 80% AGM and 50% for flooded, but other websites saying 50% for AGM and 80% for flooded, which is correct?

What setting for battery protect would you recommend?


Thanyou in advance




southsideph asked
marc-de-montreal answered ·

1 Answer

Charging a 12V Lifepo4 battery. Who has the key to this mystical knowledge?

I have bought a lifepo4 12.8V 40Ah battery from an unknown but experienced manufacturer for a small project, that was not too expensive to wake the kraken and dragon of my spouse.

It came at 13,33V and looked very tame.

I charged it with a blue smart ip65 12/15 charger on lithium configuration and low current (4A) instead of 15A to wake it up softly.

The manufacturer prescribes a CCCV load profile with cut off voltages of 14,6v high to 10V low. But Victron thinks that 10V is too low. They told me to cut off at 12,5V. And load with 14,2V.

I think Victron uses a more conservative load profile. Maybe to protect the battery from unballanced cells in these high limits? Is that right? Or does that have another reason? Lifepo4 is lifepo4 right?

The first charging got to 14,2V for a little while, but then very quickly started ballancing at 13.5V. Is that normal?

So now the battery is 13,5V... Which is good I guess for storing the battery? When I look at a voltage chart of 12V Lifepo4, that is about 90%SOC? I have enough capacity to do what I want, so that's ok.

But I need to calibrate an Aili battery monitor (I know it might be rubbish but I want a little experiment). So when the battery is 100%, I have to tell the monitor by pushing a button that it's 100%SOC. But how do I know whether the battery is completely charged at 100%? On the voltage charts of lifepo4 I see that 13,5V is not 100%, but the smart charger brings the voltage automatically to 13.5V, and I don't want to start messing with the configurated values...

I also have a smart battery sense, a smart battery protect on load side, a battery protect on charge side, and an mppt 75/15 for a solar module when I install everything. Some are new, some were of a previous AGM project (that's why the chargers are 15A, instead of 10A which would be preferable for a 40Ah battery). But without a shunt, these victron appliances can't determine the SOC, so they can't help me either, although they all blink very willingly.

Any suggestions to educate me on this and protect my precious investment from my erratic ignorance, and help me to set this battery monitor please?

Would it calibrate itself when the battery reaches full capacity again? Even when the voltage drops again to 13,5 V?

maartenvt asked
alan answered ·

2 Answers

Voltage to SoC chart for lead carbon batteries

Usually battery manufactures can provide a chart showing a battery's resting voltage to state of charge. I'm looking for that information for a Victron Lead Carbon 160Ah battery. I've looked at the Datasheet but it doesn't have that information.

A



JohLil asked

0 Answers

Wie kann die Kapazität auf dem Can VU GX angezeigt werden?

Hallo zusammen

ich habe 4 Smart Batterien in Reihe über eine BMS angeschlossen. Diese sind mit dem Quattro und dem Can VU GX verbunden. Auf dem Display kann ich alle Daten sehen aus die Ladung der Batterien, was muss ich einstellen um dies zu sehen?


Vielen Dank

slbike asked

0 Answers

can i set my charger to charge the Ah of a battery quicker?

I have a BSC IP65 24/8 charger for my 24V 75Ah mobility scooter (my original scooter charger is a 24v 5A charger). Problem I see is once it reaches the high end of it's charge cycle the Ah of the batteries are about a 3rd of what I need to get full milage from the batteries.
Does anyone have any ideas on how to fix this or what I should realistically expect?

hibrn8 asked
hibrn8 commented ·

1 Answer

BMV712 shows current but no history

Hi,

I have installed a BMV712 and believe everything is wired correctly, we have a voltage reading and the current also registers values but when we tap the history tab there is next to nothing showing.

The shunt is wired with a single 95mm2 link cable to the negative of a 3x110ah battery bank. That is the only wire that side. The right of the shunt then links into the boat (its on a narrowboat) and has about 3 or 4 load wires coming off it. The battery bank has nothing but link cables going between the negative poles and the positive only has link cables except the most positive battery with the loads again.

Overnight our battery went too low, we inherited the system a few weeks ago when we purchased the boat so I'm not sure if we have a duff battery bank. I'm confused how current it flowing via the shunt yet there appears to be little to no history.

When installing the shunt we ensured all loads got switched off and clicked the calibrate button. Running some loads last night showed a negative current and running the generator this morning activating the built in charger showed a positive current.

The 12v wiring consists of a split charge relay from the starter, solar input and a Freedom 20 inverter and 12v circuits.

When we purchased the boat the previous owner had the first battery feeding the positive and negative loads and some other loads on the middle and end battery. We rewired the bank so all negatives were fed from most negative battery and positives from most positive. I'm not sure if they've damaged the batteries in the way they had it wired up.

stevebates asked
dazey77 answered ·

3 Answers

My Agm Camper life duration

Good evening, this is the story of my Agm battery for cyclic use.

We have been living in a camper for almost 3 years.

The battery is almost exhausted.

I mean, with loads of 2/4 amps it is still good.

But with a load of 15 amperes (C 0.15), it only returns 25/30 ah.

I took a test with the recently purchased victronenergy smartshunt.


Is this normal after just 2 years and 8 months of continuous daily use?

The battery has about 1000 light cycles.

It discharges daily at approximately 12.5 / 12.6v.

He only suffered 3 or 4 deep discharges.

It is always charged at 100% every day, from a 300watt panel with a 30 amper mppt regulator.

The charge is set as follows:

- maximum current phase

- absorption phase of 90 or 120 minutes at 14.5v

- floating phase at 13.7 / 13.8v.

- temperature compensation at -3mV / C / 2V (about -18mV / C)

The working temperature has always been between 15 and 30 degrees. So very good.

The charging parameters are correct right?

On the battery it is written to charge at 14.7 / 14.9v in cyclic use and 13.8v in buffer use.

But my cyclic use is very light, almost a buffer use.

So I decided that 14.9v is too much.

Also I have seen that charging at 14.5v, the tail current is reached at the same time as at 14.9v.

In few words, monitoring the absorbed amps, I noticed that 14.5v equals 14.9v.

So I preferred 14.5v because it generates less gas.

The battery is designed for 1000/1200 discharge cycles (70%).

It actually has less than 1000 cycles at 80% now.

francesco asked
francesco commented ·

6 Answers

Battery / inverter recommendation

I am going to be installing an Onan QD5000 into my race truck motorhome but also want to run off batteries whenever possible ie. overnight and whilst on the road travelling (the generator will be great for big loads i.e tools etc when needed but obviously cant be running all the time and while travelling) we will be running 230v appliances (Fridge, TV, led lighting, microwave, combi boiler, charging phones / laptop).

I am looking for recommendations for batteries to look at and how long would i should expect these to last? agm vs lithium - id rather use agm due to costs. (im not sure what my average consumption will be as i haven't finished building the truck yet) and also what sort of recharge time would i get out of the generator to the batteries.

Adding to the above, what inverter would be best suited? and also are there any other related products i will need / will be of value to have.


thanks in advance.

barclay-89 asked
DeVo Tyler answered ·

3 Answers

Multiplus Compact recommended battery capacity

What is the basis for the recommended battery bank capacity for Multiplus Compact?

The manual for the Multiplus Compact 12/2000/80-50 recommends a battery capacity of 350-1000 amp-hours. I have two 100 amp-hour lithium ion batteries, with a maximum continuous discharge of 100 amps each. That does not meet the 350 AH minimum recommendation, but my total storage capacity should be enough for my limited A/C power demands. (Running a microwave oven for a few minutes each day, and making a slice of toast).

I do not want to buy an inverter/charger and go to all of the effort to install it and find that it really does not do what I need.

jhinman asked
Paul B answered ·

1 Answer

BMV-712 capacity discrepancies

Hello, Group. I'm using a BMV-712 with a Relion 100AHr LiFePO4 battery that I purchased a couple of months ago. Both are in an emergency power battery box I built as a pandemic project. I mostly power computers, phones, and other electronics from it. I also recently acquired a Blue Smart IP67 12/25 charger to charge at 25A, and previously used a West Mountain Radio Epic PWRgate to charge at 10A.

The BMV-712 is configured per recommended LiFePO4 settings: 100Ah, Peukert exponent 1.05, charge efficiency 99%, charged voltage 14.2. What I'm confused by is the following:

Last discharge I hit 11% SOC, and voltage was 11.24 with 4.75A draw. Consumed Ah was reported as 94.5A, however. 5.5A remaining is certainly not 11% of 100Ah. From the low voltage, I'm inclined to believe that 5.5Ah was left, so why is the SOC saying 11%, and how can I align that with actual capacity?

Also, on recharge, SOC reached 100% some time (maybe 20 mins) before the charger output dropped down below tail current. The Blue Smart charger was still charging like gangbusters at 24.37A when SOC hit 100%, with voltage only at 13.92. I think there was around a 3A draw at the time. How can I set this up so SOC is more accurate?

Thanks,

Abe

abeness asked
abeness commented ·

1 Answer

Battery voltage reading at 50% capacity at C20

Hello battery experts;

I have two Victron AGM 130ah (@C20) batteries. The question is simple: What "voltage number" do I read after spending 50% capacity, assuming under normal conditions and C20 rate. I haven't been able to find a chart for Victron AGM batteries.

leventtopcu asked

0 Answers

103 Posts
101 Users
0 Followers

Topic Experts

Stuart
0 Points