Maybe a dumb question. I have a lot to learn. I bought a BVM-712 to install in a new to me truck camper this weekend (2013 Lance 825). I will use the VictronConnect Android App to monitor. I note that the setup wizard will ask me to input the battery capacity. Unfortunately, I don't have a clue what my battery's AH rating is, and would appreciate advice on how best to proceed. The battery is a single 12 volt flooded lead acid. The label on top reads "MARINE-RV" ;"EXTREME CYCLE DUTY"; "Distributed by ABSS, Everett, WA." That, along with a yellow "8/18", is the only information provided. (I have reached out to the named distributer, but haven’t received a reply yet.)
My question is, how important is it for me to ascertain the battery’s capacity rating and input that into the app? Is it required for State of Charge and Time to Go? If I just guess, will the monitor self calibrate over time? If I should instead manually determine the capacity, any suggestions for how best to do that either using the BVM itself, or a DVM?
[image]
2 Answers
Hi all,
i'm struggling to get my solar set up to charge the batterie of my battery bank.
The solar panels give the right output voltage of about 37-something volts but 0 Amps and Watts.
I've tried resetting and re-detecting the system on the EasySolar unit to no avail.
Also it gives no errors in the notifications section of the menu.
I reckon it's something relatively simple I've been omitting but I just can't get my head around it...
Any ideas and help would be appreciated.
Also let me know if you would require some more information if needed.
Here are the specifications of my set up build in on a MAN 4X4 overland camper truck.
5 x Canadian Solar CS6K-295MS panels (1475W in total).
One set of 2 panels and one set of 3 panels.
[image]
On the picture the panels are not wired up yet but you'll get the idea.
[image]
4x12v Victron Deep Cycle 220 Ah Gel Batteries in set up 24V / 440Ah configuration.
[image]
Here are the readings from the Connect app
[image]
[image]
2 Answers
I have a 12V 2 batteries in parallel system with two revolution power lithium 60Ah batteries with 1m of 2B&S cable running from the positive to a circuit breaker then load. The Victron shunt probe (Supply cable) is connected to the line side of the circuit breaker (I.e. always on and before any load). All load, charger and earth are connected to the correct side of the shunt with only both batteries connected to the other side.
All load components are working normally and voltage is as expected around 13V however my Victron BMV712 is only reading 7V and says that there is an idle draw of over 700A, This is definitely false.
I've tried factory reset and linking to my phone to update firmware, the errors persist.
Any Ideas what's going on or if I've done anything wrong? is the unit just faulty?
2 Answers
It’s currently producing 17 volts but only 0.8amps ? Is this correct ? It does not charge my leisure battery very well
1 Answer
I have just installed a Victron bmv 712 unit in my boat. Setup for house and started battery banks. The display shows voltage of main and auxillary batteries, but is giving a fixed amp and watt reading, both positive and both excessive, I have worked the setup program and consulted the manual, making sure all functions are turned on. I tried the synchronize and zero calibrate functions on both the head unit and phone and they do nothing. I did this with all input power shut off, batteries fully charged. Then applied fridge & other components to see the draw...no change. ie. it is not reading current or power. I tried reversing the negative battery terminals on the shunt...no change.
I see others have had similar problems but do not clearly see the answer. Is this a defective unit? Surely not the cable. I have not taken a photo of the shunt installation but will attach soon.
Thanks.
1 Answer
712 connections at shunt are ok, the unit keep showing 0ah .
What is wrong , no reverse shunt connection
2 Answers
Watt from Solar-
How to know the total of watt generated before the reduction?
i understand that the SmartSolar will send only Watt-Volts-Amp when the batteries need it but i am curious to know what is the value before.. directly coming out of the panel
Any tips?
1 Answer
Bonjour,
J’ai un problème avec le battery monitor BMV-702.
Même en l’absence de production d’energie, l’afficheur indique une consommation d’ampères alors que les appareils’ électrique en consomment.
J’ai pourtant respecté le plan de montage.
Merci d’avance pour vos réponses !
0 Answers
Dear All,
I have a Smart Blue Power IP22 Charger 24v/16amp for my boat engine. I need to charge a 24v system consisting of two AMG 12 batteries (vestus marine batteries). The batteries were delivered with a voltage of each 14.2 volt and the system showed me (using a multi-meter) 28.x volt. It is my second pair of batteries having just lost the first once (chronically discharged).
Now, as I have used the new battery a bit, it shows me 24.6 volt, meassured with the multi-meter. When I connect the Smart Blue Power IP22 charger and look into the App, it says 28.x volt, but 0.0 amp., So, I'm afraid I have connected the chrarger wrongly or that it is broken (?).
Unfortunatly, the guideance in the manual is not sufficient for me as it only shows the side of the charger, not the batteries. As I was unsure whether I have connected the system in the right way, I changed the connectons, but the system still showed the same values. I would have expected that it would show me an error if I connect them in the wrong way (?).
Through this questions may not be difficult for most of you, I'd be glad to understand whether we should already see amps flowing, or should this only happen when the batteries has reached a discharge below 24v? Can I find better information on how to connect the system and is the above written (connection in different order does not change anything) an indication that the system is defect?
Thank you very much!
Olli
0 Answers
Hi everyone. I have 2x Sunpower E-20 327w solar panels that i'm going to install. The output of these panels is shown in the image below:
[image]
Now, my question is about wire sizing. I will use 6AWG from the panels to the Victron 100/50 smart solar controller which will be within 3' of the batteries. 6AWG is good for 37amps effective use current, so that should be more than enough for the approx 20' fun from the panels to the controller (i'm open to other suggestions on wire size if you have advice).
My biggest concern is wiring size from the controller to the batteries. The 100/50 MPPT can only accept up to 6AWG (37amp wire). From my research, that can be a problem given the panels statistics. When the MPPT uses the extra voltage to create more charging amps, the amps can spike considerably on the MPPT output side to the batteries. The panels are approx 650w together, divided by 12v = 54.17amps potentially coming out of the 100/50 MPPT to the batteries. I know there are losses here and there, but it will still be way above the max current rating of 37amps for the MPPT's max wire receptacle size of 6AWG.
Feel free to blow my limited knowledge of all this out of the water. Im new to it all but the brain cells are firing on all cylinders, but I could be completely off the rails with it all.
I apologize if this sounds a little long winded or confusing....probably because I am confused! haha.
Looking forward to any and all advice, help. Thanks in advance.
Scrimma
11 Answers
I had 2x200 watt 12v nominal panels connected in series attached to my Victron 100/20 charge controller. The most watts they ever pulled was ~270 according to VictronConnect. I figured it was due to a very long cable (70 feet). So recently I added two more panels to get the panels up to 48 volts, and should be 800 watts. But in VictronConnect it's still showing only around 270 watts on a perfectly sunny day. In Connect, the voltage is showing that it has doubled since there were just two panels, so that looks good, but the amps is showing that it's been halved. Any ideas?
1 Answer
Hallo !
I have a 1200 watt oven that has drawed that (almost 1200 watts and approx. 45 amps) every time I have switched it on. (I bought the oven new last summer)
However, the last three times I have used the oven has used almost 3600 watts at about 125 Amps (!!).
-I get an "Overload L1" message followed by "Recovery" every time (VE.Bus).
[image]
What could be the cause of this?
I dont understand how or why this could happen (the only other appliance i a fridge that pulls about 70 watts for a few minutes every hour).
(I have an offgrid Easysolar 3kVA (24/3000 - 150/70) with 10 kW lithium ion and 1,8 kW panels.).
Alittle disturbing that my system draws almot three times more amps than I expect, so would greatly appreciate views/solutions to this.
Eric
2 Answers
I have 3 domestic batteries and one engine battery. I assume all negatives go to the shut? The voltage goes down to 12.1 v yet the bmv says 100% and infinity time remaining. Any clues? Thanks
2 Answers
I'd like to be able to see amp hours in the Color Control instead of just watts, including input and output on all connected devices. Does anyone know of a program that can do this?
1 Answer
5Likes
2 Answers
I have installed a new BMV-712 on my camper that has 2 x 12v 115AHr AGM's in parallel. I also have a separate Volt/Amp meter installed. The BMV reads current lower than what it actually is. 3-5 Amps on Charge and Discharge. 10mm cable used to connect the shunt?
I have no idea if the BMV is just not a very accurate device or how to investigate the problem
1 Answer
Just one more question; IT was sunny, solar panel deliver 17-18 volts, says my victron 75/15. The battery is full (over 13 v). Is that why victron only deliver 1,5 amps? If the battery was low, lets say 12,2, my victron would deliver up to max amps? My solar panel says Max 3,98 amps ....
1 Answer
Just help me - on my Victron connect. What is solar current and Battery current? And why is battery current higher than solar current? Is that the Mppt magic?
1 Answer
i have a 3000 watt inverter running off a 660 amphour 12 volt battery bank. i occasionally will pull close to 300 amps for several minutes from the battery bank. this seam like it would exceed the amp rating on the 220a smart battery protect unit. could i run 2 of these units in parallel to provide the amperage capacity? or is there another similar product. my primary desire is adjustable/programmable low voltage cut off protection.
3 Answers
Hello, anyone else having an issue with the app showing very low amps on the solar side. Have hooked up to old controller and VTVM, both show 10.9 amps, App shows 2.5 or less. Thx for the help.
Mike
1 Answer
Good Afternoon, I am currently designing a hybrid battery system across three phase, the phases are unbalanced and can't be fixed due to the sites businesses. I know that the max AC amperage output is 2 x 100 amps, on a 15kVa Quattro. but if I install 2 per phase does that give me a total of 400 amp output per phase or I am miss reading the spec sheet. My Ampage max output is at its highest around 12 midday and i am also installing 100kWh of BYD batteries that will move up 200kWh by mid-year.
Please can someone just confirm what the max AC amperage output is in this situation
6 Answers
Hi! My newly installed Solar Charger draws about 45 mamps out of my 24AH Battery in my boat.
That discharges the battery in a week or so.
Is that high current normal in sleep mode? The load output is 'always off', no solar cell connected.
2 Answers
Hi All
I have a 6ooAh AGM batt bank on a sailing boat (3 x 200Ah)
What is the max safe current drain for said bank, especially with longevity in mind?
Reason:
I have a 1,6kW 230V AC watermaker and would like to run it off the batt bank through an inverter for about 30min at a time. (and some other power tools on the odd occasion)
I do have a generator so that watermaker can be run for longer periods but for 30min (making 50L of water), it would be very convenient to not use the generator, not to mention saving petrol, fumes, and noise.
I have 640W solar and 300W wind gen which should be more than enough to deal with the discharge, I believe, on a sunny day.
So, is there a rule of thumb for a max safe discharge current for (AGM in my case) Lead Acid Batteries?
My gut feeling is that 300A for an hour on a 600Ah bank should be safe. But then my 2nd gut will freak out when it sees 200A of discharge on the BMV.. Even 100A is a hell of a lot in my mind.
Regards
6 Answers
My controller shows I made 2.15 KW yesterday. I am trying to determine the approx Amps it would have put back into the battery.
I used a Calc program and if I calc it at 80v I get 27 amps and if I use 12v its 179 amps. We had reasonable sun yesterday in the desert of Arizona. Since the voltage from the panels varies all day long depending on clouds and angle of the sun I am wondering what voltage to use to calculate the approx amperage put back from the KW reported by the 100/50 controller.
Thanks, Bill .
[image]
2 Answers
[image]
Please see picture. I'm trying to figure out why no watts are being tracked as well as the crruent/amps always seems to show zero in both solar and battery section. This happens even when I plug in a space heater and put it on high. That should definitely draw some amps. Please help.
Editing to add some more photos that may help:
[image]
[image]
[image]
Thanks!
4 Answers