Hi all. I have an off grid set up with a victron 48/15000. Up till now I had a single stack of pylontech batteries and everything functioned fine.

When adding a second stack and wiring up the LV hub to both stacks, the hub keeps getting a red flashing light error. The dip switches are correct and all wiring is perfectly done.

Each stack connected independently works fine but when put both through the hub they don't work. The error is also present if the hub is not connected to the colour controller. Does anyone have any ideas?

The sellers puntoenergija have no idea. Not much documentation online either. Pity cause pylontech batteries are very good quality.

Neil Pavia asked
flotsch commented ·

3 Answers

Pylontech High Voltage Alarm

Hi I'm getting hIgh Voltage warnings on the CCGX. I understand the cells need to internally balance as it's a new system. They are, slowly, day by day.


My issue is that I have set the DVCC to 53.2V to mitigate the alarms and to allow the cells to balance but it's not stoping the alarm!.


Any ideas?


The alarms currently trigger just above 52V.



[image]


[image]


[image]

jimbo asked
jimbo commented ·

2 Answers

Configuring Multiplus with Pylontech Batteries (Possible with just CerboGX and Touch 50)?

I have a solar kit I bought recently with a Multiplus 48/5000/70 and a SmartSolar 250/100. The system has a CerboGX and Touch 50. The battery bank is 4 Pylontech US3000.

I was reading the Victron-Pylontech compatibility article, and just watched a webinar on the topic, but I'm still unclear.

To make sure all my Victron components are configured properly according to what the batteries need, can I just use the VictronConnect app via my smartphone? Does this operate via some sort of bluetooth connection internal to the CerboGX?

Or do I need to buy the Smart Dongle or MK3 USB separately?

Doesn't the CerboGX and Touch50 replace the need for the VictronConnect app or at least replace the need for the SmartDongle/MK3-USB?

agroventuresperu asked
Alexandra edited ·

2 Answers

pylontech mit multiplus ladung erhalten,

guten morgen, bitte um hilfe,

habe 4 pylontech 3,5kw, cerbo gx, multiplus2 5000, mppt 150/60,

habe gelesen, dass die pylontech nicht länger als 24 stunden leer sein dürfen, wie kann ich das einstellen damit der multiplus die batterien mit netzstrom also ohne pv, mit strom versorgt, zb. bis 15 %, so dass sie nie ganz leer werden können ? vielen dank.

gromheisei asked

0 Answers

HUB Pylontech problem, red light, CCL limit changing and battery error

Hello, after adding 4 US2000 Pylontech and HUB batteries for a total of 12 US2000 batteries, I have the following problem (see video)

Thank you.

https://www.youtube.com/watch?v=p5TrYf3VQJc


nonop4 asked
nonop4 answered ·

14 Answers

wie arbeitet dvcc genau ? funktioniert das so, wie ich es brauche ?

hallo,

ich plane eine erweiterung meines systems mit einem weiteren akku und 3 multiplus II, sowie einem gerbo gx mit aktiviertem dvcc.

allerdings weiss ich noch nicht, ob das alles so funktioniert, wie ich es moechte. deshalb habe ich dazu noch ein paar fragen:

- wird wirklich der strom der mppt-ladereger direkt gesteuert oder nur die ladespannung so eingestellt, dass der gewuenschte ladestrom erreicht wird. in meiner ersten anlage mache ich das naemlich genau so. das hat naemlich den vorteil, dass es nicht noetig ist, immer gleich nachzuregeln, sobald die last sich aendert.

- ich will auch mehrere spannungswandler und andere verbraucher direkt auf den akku anschliessen. damit der strom erfasst werden kann, werde ich diese verbraucher an den lastausgang eines mppt 100/20 haengen. funktioniert das dann auch mit der ladestromeinstellung noch, wenn die (an diesen laderegler angeschlossenen panels) weniger leistung bringen als die last benoetigt ? wenn die last direkt am akku haengt, fuehrt das ja zu einer verringerung des ladestroms um den strom der last.

- ausser den multiplus will ich auch noch einen wechselrichter mit ve.direkt-anschluss einbinden. kann ueber dvcc dann auch der strom dieses wechselrichters kompensiert werden ? ich konnte leider keinen entsprechenden hinweis finden. mit einem weiteren ve-bus-system und einem mk3-usb soll es ja funktionieren.


da ich auch noch nicht weiss, welche informationen ich ueber das gerbo gx vom akku bekomme, werde ich wohl noch ein bmv 700 anschliessen, das dann die daten fuer meine datenerfassung liefert. zumindest so lange, bis ich die daten aus dem gerbo gx automatisch auslesen kann.

tschuess

d-ferdi asked

0 Answers

Pylontech UP3000 & BMV settings

Just setting up the BMV 702 for use with the Pylontech UP3000

Are these settings ok?

1 Capacity: 518AH (7 units @ 74AH)

2 Charged Voltage: - 52.2V (0.2V under charged levels of VDCC capped voltage of 52.4V)

3 Tail: 0.4

4 Time: 3min

5 Peukets: 1.1

6 Efficiency: 95%

jimbo asked
mvader (Victron Energy) commented ·

1 Answer

Pylontech VEconfig Inverter Tab Settings conflict.

The Victron Pylontech install documentation recommends:


5.3 Inverter Settings

In the Inverter tab of VEConfigure

VEConfigure Inverter Parameter Setting

DC input low shut-down 44V

DC input low restart 48V

DC input low pre-alarm* 48V


However:


PylonTech recommended

DC input low shut-down 42V

DC input low restart 45V

DC input low pre-alarm 45V


which is correct/best to use?


thanks


J



jimbo asked
seb71 edited ·

2 Answers

Est-il possible d'utiliser des batteries Pylontech US2000 avec un Phoenix Smart 48|3000 ?

Bonjour.

J'aimerais concevoir une installation photovoltaïque avec un convertisseur Victron Phoenix Smart 48|3000 et trois batteries Pylontech US2000 (ou deux US3000).

  1. Est-ce compatible ?
  2. Faut-il un appareil annexe pour la connexion ?
  3. Comment obtenir des infos sur les batteries (pourcentage de charge par exemple)
  4. Est-ce mieux d'utiliser 3 x US2000 ou 2 x US3000 ?
  5. Est-ce mieux d'utiliser d'autres batteries lithium ? (je suis parti sur celles-ci pour le côté pratique : empilement, câblage simple)

Je vais disposer d'environ 2000 W de panneaux solaires. Est-ce que ce dimensionnement semble suffisant ?

Merci d'avance.

eliska asked
eliska commented ·

4 Answers

Pylontech UP3000 DVCC not activated automatically

Hi i just installed 7 US3000 and followed this

https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom

for install


SYSTEM:

CCGX

BMV702

MPPT250|100

MPII 48/5000

all running latest alpha Firmware


According to the above install manual:

When the battery is correctly connected this will also set the following values automatically:

Venus Settings → System Setup Parameter Value

DVCC ON

Shared Voltage Sense OFF

Shared Temperature Sense OFF


I did not get DVCC set to ON in the CCGX and no auto config took place on any devices... any ideas why?

the batteries are visible in the CCGX devices tab and no apparent errors.


I ended up configuring everything manually but curious why DVCC did not work and potentially if there is an issue i need to address.

[image]

[image]

thanks in advance.


Jim

jimbo asked
Guy Stewart (Victron Community Manager) commented ·

2 Answers

Multiplus II entlädt die Batterien nur bis 97%. Ohne Solareinspeisung MPPT 150/35 wird überhaupt nicht entladen

Hallo an alle.
Ich habe seit Oktober einen Multiplus-II, Cerbo GX, MPPT150/35 und 3 Pylontech US2000. Auf dem Dach sind je 6 Solarmodule an der Ost- und Westseite montiert.

Alles zusammen funktioniert soweit problemlos. Gedacht ist es als UPS für kritische Lasten (Server, Telefoanlage, Heizung, Beleuchtung, Gefriertruhe). 50% der Kapazität der Batterien reicht für den unabhängigen Netzbetrieb über die Nacht aus, bis wieder Solarenergie zur Verfügung steht.

Der SOC Mindestwert ist ist im ESS auf 50% gesetzt. Das hat aber keinen Effekt! Steht Solarenergie zur Verfügung und ist die Ladung bei 100%, wird kurzfristig die Last aus der Batterie und Solarenergie versorgt, bis der Ladezustand bei ca. 97% ankommt. (49,7V an der Batterie). Danach wird die Batterie wieder geladen. Kommt mehr Solarenergie an , als benötigt, wird in das Hausnetz eingespeist. (Gridmeter soll auf 0W gehalten werden.)Bleibt die Solarenergie aus, wird die Batterie nicht mehr entladen und bleibt bei anfangs 100%.

Ich würde gerne die Batterie über Nacht bis zu der eingestellten Grenze von 50% entladen und erst dann Energie aus dem Netz nutzen.

Das gelingt mir nur, wenn biem Multiplus-II "Netz ignorieren" aktiv ist.(Trennung vom Netz bis eingestellte Grenze erreicht ist) In dieser Einstellung funktioniert das Einspeisen ins Hausnetz aber nicht mehr. Bei guter Sonneneinstrahlung wird der MPTT gedrosselt und ein Teil der Energie geht "verloren", den ich im Hausnetz hätte nutzen können.

Die Firmware habe ich bei allen Komponenten im Oktober aktualisiert.

Ich habe schon zahlreiche Konfigurationen durchprobiert, kann aber den gewünschten Ablauf nicht erreichen. Stehe ich hier selber auf "meiner Leitung"?
Irgenwie finde ich den Einstellknopf nicht!

Für Hilfestellung bin ich dankbar.


christoph asked
christoph commented ·

2 Answers

Warum wird Strom aus dem Netzt entnommen?

Hallo Leute ,


mein ESS System funktioniert soweit sehr gut und zuverlässig:

Multiplus II 3kw

Color Control

2x Pylontech us2000B

Zähler netzt und Zähler pv


Nun kommt es immer wieder vor das Nachts oder am Morgen Strom aus dem Netzt entkommen wird obwohl der Akku noch mehr als 10% hat(10% ist mein Soc) . Wie auf dem Bild zu sehen ist wird Strom aus dem netzt entnommen obwohl der Akku 30% hat und zudem wird sogar noch aufgeladen.

Teilweise habe ich beim Laden den Eindruck das Victron nicht richtig misst oder Werte fürs laden als Verbrauch annimmt ???


[image]


[image]

rb994 asked

0 Answers

Updated Pylontech wiring

Victron has updated its Pylontech Wiring. See the picture below.

[image]

In the version before, the GND cable was connected to the negative pole of the DC Distributor.


Now they have excluded the GND cable at the negative pole of the DC distributor. So the system is not grounded at the negative pole anymore.

Why did they change it?

Is it true, that the negative pole of the Battery is connected to Ground over the case Ground, as this fellow says:

https://community.victronenergy.com/questions/48804/pylontech-battery-earthing.html

I have read in the MPPT manual:

WARNING: WHEN A GROUND FAULT IS INDICATED, BATTERY TERMINALS AND CONNECTED CIRCUITS MAY BE UNGROUNDED AND HAZARDOUS.

So the MPPT should be grounded on the negative pole am I right?

Cansin Sari asked

0 Answers

Easysolar 24/300/70 + pylontech UP2500 24v

Bonjour,

Je viens de terminé mon installation hors réseaux avec 2000wc de PVs un easysolar 24/3000/70 et une batterie 24v pylontech up2500.

Les petites puissance (1200w) sur la sortie AC fonctionne sans problème, mais lorsque j'essaie de mettre en route une machine de 1500W j'ai une erreur sur le GX (batterie faible avec alarme) et la batterie se met en protection.

Comment remédier au problème?

Est ce qu'un fils can-bus entre la batterie et le CCGX résoudrait le problème?
A mon avis le problème pourrai venir de la batterie qui doit se protégé d'une grosse charge (ici un pic de 3000w lorsque j'allume la machine)


Ou est ce qu'il faut modifier quelque chose dans le multiplus, qui dois être en mode ESS d'origine?


Merci pour votre aide.

Nim


nimrod asked
Thierry Cortassa (Victron Energy Staff) answered ·

3 Answers

Venus OS v2.60 & Pylontech batteries generating high voltage errors

Hi.

After updating my ColorGX to 2.60, the Pylontech batteries (installed and configured since more than 1 month according to Victron document), the charging voltage is getting now up to 52.5V and generating high voltage errors. Before this, the maximum voltage was 52 - 52.1V. No other changes were done on the system after batteries were installed, and yes it took 3-4 days for them to balance each other.

So, anyone else experiencing this? Is this a known error?

Thanks

cristimv asked
Daniël Boekel (Victron Energy Staff) commented ·

3 Answers

pylontech schaltet bei 97% ab

servus bitte um hilfe, meine pylontech werden bei ca. 97% abgeregelt, ist das normal? vielen dank.

gromheisei asked
gromheisei answered ·

2 Answers

State Of Health Degradation Rate - Pylontech US3000

Hello

These Pylontech batteries have been around for a while. The design life on the US3000 is advertised at 10+ years at 25℃.

I understand that SOH is directly affected by usage, charge state and operating temperature. No two installations will be the same.

I am interested in your experience with these batteries specifically around State Of Health (SOH) rate of degradation. What is the average SOH degradation rate (% per year) across your installations? Is this more or less linear?

Thank you

Jean










jeanmc asked

0 Answers

Pylontech Force-L2 and Victron compability

Dear All,

I am looking for information which confirms that Victron is compatible with Pylontech Force-L2 series battery.

Can someone confirm that for me?

Can someone explain to me that I am wrong?

:)

Best Regards,

Paul

enersol asked
mvader (Victron Energy) answered ·

4 Answers

¿How much would you discharge your Pylontech's to keep warranty?

New US3000C claim up to 95% discharge, but, is this compatible with the 10 year warranty that they claim? I heard it's better not to discharge them more than 50% to keep them "healthy".


What is your limit to trigger the grid or generator?

What is the limit to have 10 year warranty?


Thanks

tpwchr asked
Alexandra edited ·

1 Answer

Battery Monitor [512]: Alarm: Internal error alarm - Quattro and Pylontech US2000 Battery

Hello,


This alarm appears very often: once in two or one day. System components: Venus GX firmware 2.33 (downgraded because with new firmware there occurs fimware insufficient alarm), Quattro 48/5000/70 firmware 430, BlueSolar MPPT 150/60 firmware v1.47 and Pylontech US2000x3 battery.


When this alarm appears, battery shows red ALM and starts to make continuous beep noises.

Share link: https://vrm.victronenergy.com/installation/43728/share/ebb50a16


What can be done to solve the problem? Picture of battery with alarm is attached to this post.

What is the reason of this alarm? How could the setup/settings be changed to avoid or reduce the alarm event? System setting I took from pylontech manual (https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom)


Best regards,

Timofey

[image]

timofei-pasechnikov asked
John Hobill answered ·

6 Answers

Advice for my off-grid setup!

Hello everyone. I have made a final setup that im going to install shortly. I would love to hear some advices about the setup, i am no expert so anything will help :)

-12x450Wp Trina solar

-Multiplus II 48/5000

-Smartsolar MPPT 250/100-Tr Ve.Can

-4x US2000B Pylontech

-Cerbo GX

-GX Touch 50

-And maybe the Lynx Power In to be able to install MEGA Fuses.


What do you think of this system? Thank you in advance!



tpwchr asked
tpwchr commented ·

4 Answers

Suitable Circuit breaker between multiplus-ii and battery

Hello everyone,

I want to put a double pole MCB between a MultiPlus-II 48/3000/35-32 and 3 48V Pylontech batteries.

Pylontech recommends 25A for each Package and it supports up to 100A of discharge for each Package.


Victron states in manual:


-You must have the minimum number of battery modules to supply the inverters startup inrush surge currents that charge the capacitors when the inverter is first connected, this occurs prior to any loads being connected. For this Inverter, 2 Batteries are minimum.

-Victron recommends a 125A MCB between battery and Inverter, since its Peak power is 5500Watt (3000 AC Load + 1500 feeding in shore power)

We dont want to feed in the shore power, so only ac loads left. 3000 W / 48 V = 62,5 A. So an 80A MCB should be fine, but maybe the Inverter wants to pull more current? Maybe the stated 125A due to the startup inrush current?


I found 3 MCBs (80A, 100A, 125A) from the same series from ABB

https://new.abb.com/products/2CCF019606R0001/s802pv-sp80-high-performance-mcb


I really would like to use an 80Amp MCB, so that the Inverter does not pull much more than the calculated 62,5 Amps.


My Questions:

Do you think the 80Amp MCB will "handle" the startup inrush current?

Does the MCB could have a minimum operating Voltage(Datasheet not found)? Is 48V fine?

Is the rated Ultimate Short-Circuit Breaking Capacity (Icu):(800 V DC) 5 kA enough for a 7,2kWh battery system?

If you have remommendations for other MCBs, please share.

Cansin Sari asked
geko22 commented ·

2 Answers

Battery Monitor[512], Alarm - High Voltage Alarms - Victron Multiplus and Pylontech Battery

Hi There,


This might be quite elementary to solve, however I keep getting high voltage alarms from the Pylontech battery at times of high solar yield.


What can be done to solve the problem. The alarms tend to show up at voltages below the recommended charge voltage settings, ie max voltage for absorption charging 53.2V and Float 53V in accordance with the manual.


I have downloaded logs for some of the alarm events, these can be found at the following link.

https://drive.google.com/open?id=19c45KZUPvGrVP4q_MgFSeSdjDPtzZu3r


Where could the alarm be triggered and why, and how could the setup/settings be changed to avoid or reduce the alarm event. At present it is a once a week occurrence.


Best Regards

Riaan

Riaan Barkhuizen asked
Daniël Boekel (Victron Energy Staff) commented ·

2 Answers

Off-Grid - Multiplus II GX and Pylontech/Liontron

I want to build an offgrid system that mainly will be used during the summer.

Briefly outlined:

Energy generation, storage:

  • Phoenix Combi 12V / 1600W (we already have)
  • 4x PV panel 300W
  • MPPT 250/100
  • Car battery 12V 45Ah

Consumers:

  • Waterpump 1 phase 800W - 230V, 1h/d during summer
  • Intrusion detection (SMS module ca 5W, 24h/7d)


The system will be placed in a gardenshed.


The following questions come to mind:

  1. On a sunny day, will the power flow directly from the MPPT to the inverter?
  2. Plans to a future upgrade to a 48V system. I made calculations for the battery pack and the result was a 4x 12V-110Ah Gel battery combination. This was based on the rule which limits the maximum charge and discharge currents in regards to their expected lifetime. For this 48V system i need 3 battery balancers, which have their costs. My friend google found the Pylontech or Liontron LiFePo rack system. These systems have an integrated BMS. Can I use the Multiplus II GX or EasySolar II GX for the communication with the BMS of the rack battery? Or do I need an seperate GX device. And what power consumption is to be expected from this GX device.
  3. Do I need in regard with the future, buy the MPPT with ve.can functionality for communication with battery rack?
  4. Shouldn't Victron upgrade their MPPT's to higher voltages? I understand that more PV-panels on a string is a better choice. 250V seams limited to me for future design, if compared to AC-grid inverters.

janvd asked
joanes-banko commented ·

1 Answer

Camper Van Schematic - please critique

Hello everyone :D,

please check my schematich below. Feel free to criticize the schematich.

Here are some side notes:

This PV schematich is intended to be installed in Germany on a camper van. 80% of the time it is off grid and 20% on grid. Since I have not a GND connection on the DC side, I want to protect the postive side as well as the negative side, as it also proclaims the German Law. 3 x Pylontech US2000 batteries are used. The PE is connected in our case to a grounding strap for cars, which touches the surface of the asphalt.


Here are some short things, where I am unsure:

Should I connect the PEoff the Grid to the PE from the van. The MCCB at the Multiplus is really obsolete in my opinion, beacause all supply lines (which go to the multiplus) are protected. Unsure about the ESS, because it is actually only for on grid applications, maybe a HUB2v2 is a better option, but no one is using it.


https://www.victronenergy.com/live/assistants:hub1_and_hub2_notes#disqus





[image]

Cansin Sari asked
Rob Duthie answered ·

1 Answer

US2000B vs US2000C Pylontech batteries

Hello everyone. I've read some people have problems with mixing both. Has anyone tried a system with only US2000C and how is it going with Victron devices?


I also read that they have got rid of the RJ11 connector to use the RJ45 insteaed.

Thanks!

tpwchr asked
tpwchr edited ·

0 Answers

Quatrro inverter shutdown on Pylontech low battery

Hello,


Recently got a system consisting of:

1x Quattro 48/3000/35

2x Pylontech US3000c

2x BlueSolar Charger MPPT 150/35

1x CerboGX


As part of my testing I ran a load until shutdown. What happened is that the whole system turned off at the low voltage point. The Pylontech shows the RED alarm LED. The Victron setup does not seem to see any DC power at all at that time (touch display off etc).

It would be nicer if there is a shutdown mode where the inverter is disabled (but still powered, just not generating AC). That way the display still shows what is happening. At some point the batteries are going to turn off completely and then whole system will be down.

I've had bad experience (with another vendor) where it becomes a real struggle to get the inverter/charger to wake up when there is (generator) AC, but not DC yet.

Is that not an issue with the Victron, as soon as I apply AC the system comes back to live?

Also, when the system was in shutdown, non of the console commands on the Pylontech seemed to indicate a powered down state :) I must be looking at the wrong command since the inverter saw low voltage over CANbus. What is the correct command to see historic shutdown reasons?

Bas

bas-rijniersce asked
Alexandra commented ·

2 Answers

How to charge up to 80% max? Pylontech

Hello everyone. Finally I'm going to install the equipment for an off-grid and I have studied the values recommended from victron:

Absorption voltage 52.0 V
Float voltage 51.0 V


But I have read that it's much healthier for the battery to not charge it at 100%. Would it be better to charge it at less than those values?

What values is people using? I'm a bit worried for this because i trust in Victron but maybe it's better to tweak a bit those values to extend the life of the batteries. Thanks a lot.

tpwchr asked
Rob Duthie commented ·

1 Answer

Correct DVCC setting for Quatto + Pylontech US3000c + Bluesolar MPPT

Hi all,


Recently got a system consisting of:

1x Quattro 48/3000/35

2x Pylontech US3000c

2x BlueSolar Charger MPPT 150/35

1x CerboGX


All firmware updates available via the VRM portal have been applied. I don't have a USB adapter, so I guess the inverter is on the firmware it came with.

The Pylontech - Victron setup manual says that the DVCC settings will be automatically populated. This was not the case for me.


What settings should I use for my setup?

DVCC -> On

SVS Shared Voltage Sense -> ?

STS Shared Temperature Sense -> ?

SCS Shared Current Sense ->

SCS Status shows "Disabled, external control"


When I enable limit Charge Current, it defaults to 50A. But I can change it.


It does look like the system sees the batteries correctly. Looking at the max charge current on the battery view, it matches the two batteries I have in my system.


Thank you!

Bas




bas-rijniersce asked
davidrkennedy edited ·

2 Answers

Pylontech High Voltage Alarm US3000

Hi,

We have just replaced batteries with Pylontech US3000 x 2 on an existing off grid solar system. We are getting a high voltage warning with the SOC at 81%. We have updated all the firmware to the lastest release as directed on the victron and pylontech page.


Here are the details of the system


Victron easy solar with 48V, 3KVA Multiplus, 150/70 blue solar MPPT, 2 x US3000 Pylontech Batteries.


Firmware Versions

CCGX - V2.63

MultiPlus 3KVA - V2620459

MPPT 150/70 - V1.54

VRM Portal ID - 508cb1e4251b


Please Help

Chethan Bandi asked
seb71 edited ·

3 Answers