Hydro and Wind Power Image

Hydro and Wind Power

What type of Wind Turbine works best with EasySolar

Greetings, I would like to add a wind turbine to my off grid easy solar 3 kva 48v system to keep batteries charged on overcast days. Looking online, Kestrel wind turbines have various voltage output options on their e160i product, amongst others, they have 48v or 200 VAC turbines.

Question is ...What is the better solution .. to go for the 200v and plug directly into the shore power input or alternatively feed the 48v output from the Turbine into the DC input.

Also, will the easy solar unit dump off the excess power input from the turbine when it is not required? Thanks Maarten

Maarten De Graaf asked
ttbb commented ·

3 Answers

600V from micro hydro generator, to battery bank?

I plan to add a battery bank to an existing micro hydro system. I would like to parallel 3 of the Victron Quattro 10kVA 120V to take power from the 24kW capacity hydro generator (or a diesel backup generator) to charge the battery bank and feed through / invert to 120V AC for household power. The problem is that the hydro generator produces power at 600V AC whereas the Victron Quattro inverter-chargers will accept only between 90V and 140V AC input. I could put a 600V to 120V step-down transformer between the hydro generator and the Quattros but this would reduce efficiencies.

Is there a way to set up a Victron product to handle the 600V AC output of my hydro generator? Or else is there an inverter-charger on the market that can handle that input voltage directly?

wahlet asked
mt-geek commented ·

0 Answers

Wind Turbines and victron charge controllers

hi, i would like to know if victron mppt charge controllers support wind turbines? if yes could i run 2 controllers in parallel, one with solar and one with a wind turbine?

Thanks

Lief.

lief ryan asked
houser edited ·

11 Answers

Mppt as wind controller problem with power transfer??

I recently made a knowledge group in facebook for enthusiasts like me, everybody is welcome to join

I am a solar installer from Gsol Energy Global, we make offgrid and on grid Solar systems for the UN.

In my private project, I am allso building a hybrid system containing wind and solar.

Technical information -

Wind turbine 1kw 3phase Greef generator mounted on 9m mast, with home made blades( vertical )

Victron quattro 10000Va,

Ccgx, lynx shunt can bus,

smartsolar 250/70 as wind input with rectifier, and 10000uF capacitor infront.

Smartsolar150/100 for pv.

Wind break will be added through a changeoverswitch later. I can raise and lower wind tower at will, and the vertical design is not prone to overspin due to the design.

My problem is that windmill it is not transferring power, even though i got strong wind and 60vdc at the pv input side. And the voltage on battery bank is more than 5v lower (51,2v - 57,6 is cycle use)

I was thinking that voltage from generator is to close to the battery voltage, I was thinking about putting a voltage stepup module infront despite the loss..

Any thoughts from you guys?

[image]

myren asked
Tom h edited ·

1 Answer

Victron wind turbine regulator?

Anybody at Victron thought about releasing a small wind turbine regulator?


There are a lot of small <500W wind turbines out there with rubbish regulators including premium manufacturers like Rutland. Maybe one of your MPPT models could be easily redesigned for the purpose?



sv-gabrielle asked
maremotomoto answered ·

1 Answer

How to connect 2 Wind turbines dc motor 85w to 1 MPPT?

Hi Everyone,

I have 2 wind turbines to connect to my Victron mppt 100/20 controller.

My motors are dc 85w. So connection is just 2 wires.

Works well with one wind turbine. Straight forward connection with negative and positive.

My question is; can someone please tell me how to connect the 2 wind turbines in parallel to the controller?

please give detailed description of wiring and what is needed. If I need to use small diodes on the positive? Etc..

Please help!

Thx.

ago72 asked
ago72 commented ·

1 Answer

Combining Solar, wind into 48v off grid system.

I have been searching through the articles to see how best to combine solar and wind with lithium batteries.
I am providing power for a remote radio/ comm tower. The setup I have 2400 watts of solar, going into a smart solar 150/100 mppt. this charges 324 ah 48v lithium battery bank. This feeds into 3kva multiplus. I have a constant load of +- 300 watts going out the ac side. I have a BMV700 and everything is interconnected using Venus GX to make monitoring and remote configuring easier.
This all works well on 90% of the days when there is good sun, the only time I have issues is on prolonged overcast days. What i am looking at is a way of maximising the battery life by decreasing the DOD as much as possible.
The idea I have had is to install a 600 watt wind turbine and controller. I don't like the controllers as they do not seem to work well with lithium, and have rudimentary controls or setting points and from what I have read you cannot really put them through an mppt as it tracks to slow for the fluctuations of a wind turbine system.
I thought the best way to get around this is to take the controller that comes with the wind turbine and push this up to 64v and then string a number of supercapcitors with their balance boards together to make up 64vdc. then run this into an mppt on the input side. I can then monitor flow of power, and the GX / multiplus can control the system to maximise the power usage. has anyone tried this or had any luck with something similar.

dgnevans asked
dgnevans commented ·

3 Answers

AC connect 3kW wind turbine Victron Quattro System

I have a Off-Grid Quattro 10kVA with AC Connected 3kW Fronius Primo solar inverter and 4kW of solar panels. Frequency shift is used to manage battery overcharge. System works great in summer but we are expanding for winter with additional solar, and a wind turbine. We will AC connect an additional 4kW Fronius and solar array. For wind, we are installing a 3kW 60V AC turbine that will rectify to 48V DC and this feeds to a grid tie wind controller/ inverter (China Supply) that will synch to the AC Bus. The controller will dump power to dump resistors to protect the turbine from over speed/ voltage/ frequency.


However, i am concerned the Wind controller inverter will not spill turbine power (trigger dump resistors) when the AC Bus frequency is shifted by the Victron Quattro (High batrery voltage). Logic tells my the inverter would disconnect on high AC Bus frequency and send all power to dump resistors, though I cant be sure and manufacturer info is sketchy.

My question is whether it would be possible as a back-up to use one of the quattros Programmable relays to trigger when the AC Bus frequency is shifted to say 53hz. In this way I could trigger dump resistors to spill wind turbine power when it is not needed for House Load or battery charging.

gallows asked
gallows edited ·

0 Answers

BMS-712 secondary bat midpoint monitor

My campertruck has 2 different battery systems.
Household battery is a bank of 3x110aH parallel 12v Accu’s
Starter battery is 24v trucksystem, so 2 in serie

Can I use the second aux-input on the BMS-712 as a midpoint monitor for the 24v starter Accu’s, while using the rest of the system for the 12v system monitoring?



words asked

0 Answers

Wind turbine inverter as AC In to the Multiplus?

Hi Guys, I'm planning my off-grid system and I need some help with the design.

My initial plan is to use Mulitplus II GX/MultiGrid with DC coupled PV connected to the BYD battery pack. The issue at this stage is the optimal connection of the wind turbine (3 phase generator).

Inverter recommended for this turbine can operate in both on-grid and off-grid installations. In on-grid mode it would be connected to AC out of the Mulitplus. If I'm not wrong surplus energy can be used to charge the battery but without any control of the Victron or BYD BMU.

Off-grid model can be connected to the batteries and work without the grid but the communication with BMU/BMS isn't supported.


Do you think that it's possible to use output of the wind inverter as an input to the Multiplus (or as genset for MultiGrid)?

This is a schematic for the off-grid, 'connection point to the electricity grid' will be the Multi.

[image]

Both Multi and PS100 will be connected to the same battery pack, but charging/discharging will be disabled in PS100. This should allow Multi to use power generated from wind to charge the batteries in line with BMU communication. If I'm not wrong it will also resolve the problem with overcharging the batteries.


What's your thoughts about this approach?

dyju711 asked
dyju711 commented ·

1 Answer

Can I add a wind turbine to my EasySolar

We have an EasySolar with a PV array and generator to keep the bank of 48V batteries charged. This is all working well, but would like to consider the addition of a vertical wind turbine to help in the winter, Important here in Orkney where the winter nights are long! Have been looking at TRiStar controllers, dump loads, etc but getting confused about how this might all work together without the PV controller and wind turbine "fighting" each other to charge (and not overcharge) the battery bank. Anyone done this type of thing before? We also have a BMV712 monitoring the current/voltage.

anguswbrown asked
Grant Cleveland commented ·

2 Answers

Where do I connect my AC hydro generator power in to my Easy Solar 48v, and what voltage range does it accept?

We've been enjoying using our Easy Solar 48v/3000, charging BYD lithium batteries for the summer with solar panels, waiting for my hydro system to be up and running for the winter. Can someone please point me in the right direction for plugging in the AC power from the hydro turbine - I'll need to set up a dump load or two to my hot water cylinder and heater, but what voltage range, AC/DC format, and frequency can the Victron unit accept? And where do I connect this?

Thanks.

Rick asked
Grant Cleveland commented ·

1 Answer

Is there a charge controller that can handle both a hydro input and a solar input?

I want to use two power sources to charge a battery, which will in turn power a motor. I need to know how to design the circuit required so I can charge the battery from two sources

ewanb asked
Bruce A. answered ·

3 Answers

MPPT Charging for Hydro. Victron 150v Blue solar not finding correct Maximum power point

Hi all. i have been running my off grid cabin on hydro for over a year now. i have been useing a tristar mppt controller and fixing the correct voltage in order to load the turbine correctly. this voltage is around 50v under load. That is the ideal speed to load the turbine to in order to catch the most energy from the water. that 50v equates to the turbine moving at half the speed of the water leaving the nozzle, this is the optimum relationship between nozzle volicity and rpm.


Now i have had lots of problems with morningstar and decided to try a victron blue solar controler. I planned on useing the mppt controler to find the best voltage instead of me needing to fix the voltage to 50v. I have plugged it in and at first i found that is would be all over the place and not find a voltage and stick to it. It would sometimes get close to the right voltage but then do another sweep and loose it again. I put this down to the fact that it is acting differently from solar and could do with some large capacitors to smooth it out. I have done this now and tested it and it isnt all over the place anymore but it thinks the maximum power point is at 30v and it simply isnt. The maths says it is at 50v. i have been using it for a year at 50v and that has giving me the most power. (I have done endless testing) But for some reason the blue solar controler seems to think the maximum power point is at 30v My question is why? and has anyone got an ideas? It will sometimes do a sweep and the voltage goes up and as it does the wattage produced goes up to. but then it just goes back to the 30v again. at 30v i am loosing alot of my efficiency because that relationship between nozzle velocity and rpm is off.


Thanks for any help.


kris

Kris Harbour Natural Building asked
markus commented ·

2 Answers

Strong A&V Fluctuation of MPPT for Hydro

The "4min" pictures show the effect. In this case we came from Float. The battery is full, no current is flowing. Everything is fine. Then at the load output of the MPPT a light bulb is switched on - about 2 A the bulb wants to pull at 12.75 V = 25.5 W. Makes sense. But the load from the generator starts to swing now from zero to 150 W.4min Solar (W) and Load (A) 20190730-093526.jpeg

The charge controller seemingly can't cope with controlling that, because when it tries to take the voltage back up, it brakes the water wheel, voltage drops and current goes down simultaneously.4min Solar (V) and Batt (V) 20190730-093613.jpeg 4min Solar (A) and Batt (A) 20190730-093635.jpeg

The pictures "42min" show the course over a longer period. Sometimes it goes smoothly for a few minutes, but then everything oscillates again. 42min Solar (W) and Load (A) 20190730-112209.jpeg42min Solar (V) and Batt (V) 20190730-112228.jpeg42min Solar (A) and Batt (A) 20190730-112249.jpeg

The currents jump up to 10A and down to 0A. You can also hear it in the running noise of the system, how the generator grabs and brakes and then lets go again. Definitely not good electrically for the battery and mechanically?

Is there a trick for hydropower units? From my point of view, the charge controller is too fast? If it were a PID controller, you could tune it. But I didn't find any parameters that could be tuned.

We are at a water wheel with a weight of approximately 1 ton (3.5 m diameter, 1.5 m wide); with the water flow and fall height, theoretical power 100 W, rotating at ~ 10 rpm IMG_3530.jpg-> 3 stage gear system to increase rpm IMG_20180323_181324.jpg-> 3-phase AC generator (ZXA 50500) -> bridge rectifier -> BlueSolar MPPT 75/10 -> 100 Ah 12 V battery

kali-the-miller asked
tilo answered ·

3 Answers

brake for hydropower

markus,

the heater has a very non linear curve, such that It draws quite some current when cold. best solution would be to use a triac driven on input voltage > tbd and use thta the connect to the heater on the AC side of the generator. unless the generator is a 3 phase type, but switching dc powers creates always turn-off surges and sparks. best would be a PWMpower fet control with the heater as a load, so there is no hysteresis and oscillation. allways add surge protectors, snubbers etc.

good luck !

basreflex asked
markus commented ·

4 Answers

MPPT 100/50 with Permanent Magnet Generator as input.

Greetings everyone, I am new to forum and would like to say hello.

I have a question regarding input on the MPPT 100/50.

Is it possible to use the DC output of a permanent magnet generator 60v-72v with maximum 70 amps to the input of 1 or 2 paralleled mppt 100/50 charge controllers?



hydrotruth asked
hydrotruth commented ·

2 Answers

Using Victron MPPT for wind turbine

My 24v 1040ah system is running with 2.6kw of solar controlled by two MPPTs in parallel, a 3kw multiplus, a Venus GX, and a BMV-712.


I am wanting to add a wind turbine to the system, and as I have a spare blue solar MPPT I was wondering if anyone has any experience with this? If I get a 48vdc turbine I think the MPPT would do the job. I was thinking if I use one of the relays in either the Venus or the BMV to switch a larger power relay to divert the turbine output from the solar controller to some dump load resistors when SOC reaches 100%, this would stop the turbine from free spinning? And also if I put the resistors in the right location I can use them for heating if required.


This would a be preferable setup for two reasons, one because I already have a spare co troller, and two because it would make tracking power generation a lot easier as I could use the Venus for it.


Would love to know everyone’s thoughts.

brokenlegg asked
sean answered ·

2 Answers

Not-victron wind charge controller + DC load monitoring

For off-grid system (multiplus + MPPT + wind turbine charge controller) with AC load and continuous DC load 24V need to monitor additional DC generation from wind and DC load consumption. Is it possible?

Without wind turbine I just have to switch on "has DC loads" (or something like this) in CCGX. But with additional non-victron charger information will be not full and not correct. May be I can use additional BMV for that purpose, am I?


andrewb asked
houser answered ·

2 Answers

Wind Charger - Unstable MPPT

I have 2 x 150/35 and 2 x 100/20 MPPT's controlling 20 x 100 w solar panels. I also have 2 x D400 wind chargers with their own controllers. All connected directly to a 24 v 1200 ah battery bank

Every time there is a gust of wind, the output from the MPPT's is reduced for a few seconds - I presume because the MPPT's sense a slightly higher voltage and need to adjust to that new parameter? Is there a setting on the MPPT's that can be changed to overcome this fluctuation?

I also have 2 x 24/5000/120 Multiplus. When running my Genset and the Multi's are charging, the MPPT's supply zero power. The same thing happens when my main engine is running and the alternators are supplying power. It would be preferable if the MPPT's continued to operate normally and the charger/alternator power was reduced. Is there a solution to this?

I have an MK3 interface to change the parameters.

Thanks


meshugga asked
troy answered ·

3 Answers

Hydro Generator Brake - how?

Hi,

I know this question has nothing to do with Victron equipment in first place, but I think there are good electronics engineers around in this board, maybe someone can help me.

I have had a hydro power installation with a Victron MPPT Charge controller.

See: https://www.victronenergy.com/blog/2017/12/18/diy-ingenuity-hydro-power-in-the-austrian-alps/
Unfortunately, a heavy storm and the affiliated flood flushed it all away.

I'm just about to rebuild everything bigger and better now. You can read about it in a near future blog from John Rushworth, when it is finished.

The problem I am heading now is, that the open circuit voltage of my generator after rectification is above the maximum MPPT input Voltage of my charger.

My charger accepts a maximum of 250V and the Voc of the generator is 300V.

My conclusion is to find a solution to electrically brake the generator so the Voc stay safe below 250V

I have to put a 1Ampere load to the generator to brake it down to safely below 240V


I have 3 approaches to solve this, but I do not know which way to go.


1.) connect a power resistor in parallel to the generator to brake it

This would be the easiest way to solve this, but I will lose usable energy through the resistor.

I do not like this solution


2.) build a voltage stabilisation circuit with a transistor and a Z-diode that short circuits the generator at e.g. 230V and over to brake but does not apply below 230V.

This is the most complicated solution, but a good one I think.

The problem here is, that I would need some help to calculate the components of the circuit.

I am just not good enough to do this completely on my own.


3.) build a serial diode brake.

The approach here is, that a silicon diode is not conductive in transmission direction below 0.7V

You can get 5A silicon rectifier diodes very cheap.

So when I solder 300 of them in serial and connect them in parallel to the rectified generator output, that should to the trick.

The diode characteristics would then be my generator "brake characteristics"

This is a bit of a dump solution but I do like it. The cost of 300 diodes would be around 30€.


The idea behind posting this here is, that maybe someone has a better idea.

I would tend to go and solder some diodes. :o)


Thanks,

Markus

markus asked
markus edited ·

9 Answers