Hi all!
I have Victron SmartSolar 100/30 and Smart Battery Senser installed. I also added VE.Direct connection to the SmartSolar to connect to my own systems.
However, I found that the temperature data from Smart Battery Senser isn't available. Is there a way to get it available to VE.Direct? I think it would be smart addition to the system that the SmartSolar would send that data if it's available.
Thank you!
1 Answer
TL;DR:
Device: Solar Charger; Triggered by: Automatic monitoring; Description: Error code: #1 - Battery temperature too high
Error received and MPPT shut down when battery temp hits 50°C as reported by SBS. Where is that setting? I can't find it in MPPT, CCGX or SBS.
System consisting of:
----------------------
Background:
A remote installation suffered from battery neglect. 4S 2P 12V for 48V system voltage: one string of 4S 12V was experiencing very high temperatures under moderate charging with substantial electrolyte loss. SBS is on one battery in this string, but BMV was shared temp sense on the healthy string, so temp comp and alarms were based on the healthy string. During troubleshooting and testing, ailing string was observed to be... 64°C. Confirmed with IR thermometer.
Bank replacement is planned, but "limped" minimal use is needed for a few more weeks. Current and absorption voltage reduced to better manage temperature. Extended absorption phase to compensate for lower absorption voltage.
Sample simultaneous readings:
0 Answers
Hallo, what kind of generic temperature sensor I need to use with smartshuunt, instead of the victron temperature sensor? I just know that is a in-built chip temperature sensor and not a resistance sensor.
Can someone post a example link please?
Thank you.
0 Answers
Marine setup. 4x Renogy 12v/200amp (100amp Max continuous charge) LiFePO4 batteries w/internal BMS & Bluetooth. Sources of Charge: (a) 2x Volvo Diesel engines with standard Alternators (guess 65amp each) - internal regulators configured for typical LED 12v charge profiles, (b) Multiplus II 12/3000/120 (30 amp Shore Power), and (c) Victron Blue Solar MPPT 100/30. Question #1. Recommendations for methods to manage/control Charge Profile for current produced by engine Alternators to manage Lithium batteries instead of LED batteries. I suspect this would be via the use of Orion DC-DC 30amp Charge Controllers - would you recommend (A) one for each engine or 2x stacked per engine, and (B) would these be then common connected to a bus bar or directly to battery bank or via a Victron Lynx product (I want to be able to manage and see in real time the performance of DC chargers and control situations where Solar and Shore power and Engine Power is all coming in at once via the Victron Connect App. Question #2 How do I configure the 4x Battery Bank to be able to see each individual batteries performance via the Victron Connect App? I currently have a Victron Venus GX & one Victron BMV700 with temp sensor and smart shunt - should I buy additional smart shunts + battery protectors, or, Lynx Smart Shunt, or will any of the Victron external BMS systems work?
0 Answers
I would very much like to make sure that Smart battery sense can share the temperature with the smartshuunt to compensate for capacity, and not just with smartsolar.
Because my smartshuunt has no temperature sensor because I need the engine battery voltage reading. Is it possible to do this? If this is not possible, it would be very convenient for victronenergy to implement this possibility via firmware in the future.
1 Answer
Hello
I have a smart batteryprotect 12/24V 65A. I try to resetten the pincode, but it does not work. I use the 3 dots and enter the PUK-code. The answer is: function not available.
How do I resetten this device?
Thnxs Harm Abel
1 Answer
Hello, I have a smartsolar 100/30 on the VE network. SMART with smartshuunt and smart battery sense.
Now, smartschunt don't have the temperature sensor because I need the engine start battery voltage function.
The smartsolar receive from smartshuunt current and battery voltage. And receive from battery sense only the temperature.
But I would like the smartsolar to receive only the current from the smartshuunt. And that it receives temperature and voltage from the smart battery sense. It's possible?
0 Answers
Odd issue that randomly pops up between a SmartShunt without an auxiliary temperature sensor, a Smart Battery Sense, and a pair of MPPT 100/30 controllers.
The SmartShunt will occasionally take over temperature monitoring duties and it sticks at a temperature of 30 F. This causes issues with over voltage on my battery bank.
All devices are on the same V.E. Smart Network
I am unsure what is causing the demotion of the Smart Battery Sense temperature sharing. The SmartShunt does not have the external temperature probe installed physically, and it is not enabled in the firmware either.
5 Answers
Good day,
I have been using Smart battery sense a little over a month together with a MPPT 100/20, Smartshunt 500 and Cerbo GX. Smart Battery sense is located on top of my 100Ah Lifepo4 battery and transmits the battery temperature to the MPPT unit which is 2 meters away from the battery compartment.
Everything was working in harmony until yesterday. The weather was perfect and sunny but the MPPT wasn't charging my battery. After spending some time, I realized that the SBS was reporting a temperature of -18*C. Of course, MPPT was not sending any amperes to the battery in order to protect it. However, -18*C couldn't be true as I had access to another temp device in the trailer which was reporting +23*C. I was checking this remotely via VRM.
Today, when I came close to my trailer, I noticed that the SBS was reporting the temperature correctly, +12*C. However, when I enable the Bluetooth on the MPPT, the temp value received by the MPPT is still showing -18*C. Maybe, SBS needs an reset or a power recirculation but I wanted to share this here to ask if any of you had a similar experience.
I will appreciate your kind assistance
Best regards
Sedat Bilgebay
6 Answers
Hallo Community,
Ich würde gerne mal ein Verkabelungsdiagram abfragen für folgende Problemstellung:
I habe 2 GEL 200AH Verbraucherbatterie in Reihe (12V) mit einem Smartshunt 500A und bin gerade am planen für eine Solaranlage am Boot. Hierzu wurde ein 150/35 MPPT Victron angeschafft nun die Frage: Der Smartshunt hat ja schon ein Kabel an den Plus Pol meiner Batterie für Temperatur, nun will ich den Victron Smart Temperatur Sensor nachrüsten. Muss ich für beide Batterien einen Temperatur Sensor kaufen und mit dem MPPT Regler verbinden? Oder langt nur ein Sensor? Wie ist denn der Schaltplan hierzu? Ich kann leider nichts hierzu finden....
Danke für Euere Unterstützung.
VB Beluga...
Schema:
[image]
2 Answers
datasheet-mppt-250-60-up-to-250-100.pdfI'm configuring the Smart Battery Sense and Smartsolar 250/85. I have created the network on the Smart Battery Sense but I can't select any options in the Smartsolar 250/85 to connect to a VE network.. The data sheet says it can... See attached
Please assist.
3 Answers
Hi, I'm going to add the Smart Battery Sense to our Bluesolar 100/50 mppt controller to improve charging on our battery bank. The system is 24v and we have 4 x 6v FLAs in series. Which battery should the SBS be connected to (and presumably to both terminals on the same battery)?
4 Answers
I noticed the smart network menu is not available in my smartsolar MPPTs. Never needed it until a technician installed a Smart Sense on a site but forgot to set the smart network up... a site in a island :(
We have a GX device just for monitoring purposes and change MPPT charge profile if needed. Can we set the VE.Smart Network with the Smart Sense, remotely?
1 Answer
Is the BMV-712 able to provide voltage and temperature meassurements to the Victron MPPT Solar Charger or I also need a Smart Battery Sense?
Will the Cerbo GX connect with the Smart Battery Sense too?
3 Answers
Hi,
My setup is Smart Battery Sense with bluetooth connection to MPPT 75/10, which has a VE.Direct USB cable to Raspberry Pi.
The MPPT can see the data from the smart battery sense, and in VRM I can see the MPPT. But I cant see the data from the Smart Battery Sense. Is this normal? I expected that the MPPT would pass on ALL data to the VRM portal.
Thanks,
Cameron
3 Answers