I currently have a x15 Quattro48/10000 set up in a 3-phase configuration (5 units each phase). The system is off-grid and boosted by a 175 kW generator each evening for a few hours. Recently one Quattro on Phase 3 has been overloading during generator operation.
I have been able to temporarily remedy the problem by lowering the input current limit to 95A down from 110A. However, that 110A is what it has run at for the past 5 months without issue.
Previously the system has overloaded at generator startup/when the Victrons first accept the power, however these recent overloads have occurred hours into generator operation.
What could have the caused this Quattro to suddenly not be able to handle the incoming current?
Thank you
0 Answers
I am currently expanding my RE system with a third multi II inverter to 3 phase from the current 2 phase in parallel. (mulltiplus II 5000/48/70-50) I have purchased some Airpax 150A DC breakers and just wondered if I need to link them all together so if one trips, they all trip. I don't have any 3 phase motors running just 3 separate circuits on the AC side to spread the loads which get quite high when we run air con,etc..
Any help much appreciated
2 Answers
according the manual "VE.bus firmware version explained", it should be no problem, to match
https://www.victronenergy.nl/upload/documents/manual-VE.Bus-firmware-versions-explained-EN.pdf
2x MultiPlus-II: (software 2629481)
1x MultiGrid-II: (software 2625481)
together to a three phase system.
I use the latest VE-configuration tools, but it is not possible to do this.
An error messages in VE-Bus Quick configure tells:
Only Multis of same kind and with same firmware version are allowed!
Procedure will be restarted
Switch all devices off and press OK
What is the probleme?
Best regards
Roland
0 Answers
I've done a 3x Multiplus II 5000 set up in a 3 phase configuration and noticed that when the system is set to TOTAL OF ALL PHASES in Multiphase Regulation it will balance the phases to near 0w as far possible by feeding into the grid on L1 the same as it would pull on L2 and L3. But this is not ideal if the grid meter is prepaid as the meter would charge you units for what u are pushing back. If I set it to INDIVIDUAL PHASE it only seems to feed PV into L1 and L2 and L3 dont get any PV benefit. The system consists of: 3x Multiplus II 5000, 2x Smartsolar 150/85, 14kwh Li-ion, and 8.9kwp Solar PV. What am I doing wrong or might it be better to set the 3 inverters up as a parallel system on L1 and put all my heavy loads on L1 if the system is not capable of supplying all 3 phases individually?
[image]
3 Answers
Hello,
I am installing a 3-phase system to a property, where the existing loads are single phase. The only reason its being wired as 3-phase is to future proof for a high speed charger, and because an existing 3 phase supply is already in place from the grid.
I have read in detail the documentation provided by Victron on 3 Phase ESS, with the respective examples, but its not clear enough in my view, sorry Victron.
Does anyone know of any other material where the examples are better set out with text ?
I want to ensure even though most of the loads are on L1, the 3 phase AC inverter, and the 3 x Multi's on the DC side, will not waste the excess energy.
Thank you
0 Answers
Hi,
I am trying to set up 3 phase/2 parallel system based on 6 MP-II.
How to set the master and slave in each phase?
[image]
1 Answer
i installed 3x MP2 3000VA /48V. Updated Firmware to 2629474. made ve quick config, setted all settings. made the ess assistant in each MP. Now i try everything but the whole system acts like phase compensation is disabled although it is enabled. each inverter does only deliver so much power as required on the specific phase according to the grid meter. No idea why the compensation setting in the venus gx is not working. Please help!!
AC L1,L2,L3 is connected to MPNr.1-ACIN, MPNr2-ACIN, MPNr3-ACIN. The system is useless. If the electric car is plugged in on one phase with 7kW it only delivers max. 2.4kW from one inverter, if no other loads are switched on. If someone cooks on L2, i only get 2.4kW from the inverter on Nr.2.
I read all installation manuals, the training video on the Victron professional side, there is no hint what is wrong, looks like a software bug on the Venus gx!
[image]
[image]
7 Answers
This issue as been discussed before, but still it is a problem - and a very serious problem
I have a grid-tie 3-phase multiplus 3000/48-32 setup with ESS
In VenusOS I have set grid point to 500W (cut everything above 500W) and I have set "Multiphase regulation" to "Total of all phases"
I now expect the battery system to keep a maximum of 500W imported power.
This is not happening.
When I turn the own on, the total on that phase exceeds the power the victron can give at the moment.
The inverter on L2 is doing what it can, but it cannot compensate for the full load, and 500W is beeing bought from the grid.
The other two inverters are not helping L2 to zero the feed in. They are just zeroring their own phase.
AC-loads
L1 627 W
L2 3179 W
L3 130 W
Grid
L1 164 W
L2 683 W
L3 105 W
Solar about 40 W per phase
Total from grid: 952 W
Expected is 500W
Expected:
When L2 has reached its maximum, L1 or L3 should produce mote power, and even sell power to keep the grid point at 500W
There is no differance in behaviour between "Total of all phases" and "Individual phases" The result is exactly the same. There is no change what so ever.
Expected behaviour is: If grid point is set to 500W, This should be obeyed at all times, even if two phases are selling and one is buying, as long at the total is equal to the grid-set point.
This is a MAJOR bug. This makes the ESS useless out of a zero-feed-in scenario.
Most electricity companies where I live have "Total of all phases" as their means of billing.
Expected:
"Total of all phases" = make total to grid-point even if it makes other phases sell or use more power that the individual phase requires
Attached pictures show the system with a "grid set point of 500W and "total of all phases""
Yet it is still importing 452W more that expected, even thought L1 and L3 are hardly doing anything (especially L3)
[image]
[image]
5 Answers
Dear Guy Steart at Victron Expert Community,
I can show you 15 very unsatisfied customers within this forum who all have the same problem.
They are very disappointed about the fact that their investment in 3 phase system is not able to make phase compensation and so their investment is not satisfying their needs.
Loading electric vehicles will not be supported by Victron. Is this your strategy and can you tell us that you dont want to support solutions with ESS+EV's or is it just an unwanted failure and this important change request did never pop up at your programming experts and product managers?
Please look at the threads that are unanswered:
4 Answers
[image]
Hello!i am planning a solarsystem whit 3x VE MultiPlus-II 48/3000/35-32 ( se more in picture) for a 3-phase system.
I have made a simple wiring diagram over how i´m planning to set it up, am i thinking right?
- I want a 3-phase, for example the heating system needs 3-phase to work.
- UPS-funktion of the whole household
- i want to use as much solar energy i can for myself, more optimised for winter then summer.
- not designing the system to be optimised to sell as much power i can. not selling at ALL right now.
- want to use ESS, have lead-acid batties right now, planning to upgrade to lithium a.s.a.p.
- yes a electrician will connect it all.
I was just hoping a "victron-guru" could take a look and see if i´m totaly off or just maybe close to actually thinking right :-)
// Jocke
4 Answers
For an 3 fase offgrid system with 3 Quattros - will be feeding 2 motors that are controlled by two WEG frequency drives (CFW500)
Is there any risk of that the frequency drives create a bad harmonic that can effect the Quattro inverter.
If yes, how can this be avoided?
Thank you in advance for your thoughts/solutions.
0 Answers
Schermafbeelding 2021-01-30 om 12.42.38.png
3 Answers
I have 3x multiplus 24/3000 connected in a master/slave config with VE-bus. Making 3-phase 400V. Out of 1 phase or 24V battery. Worked fine for years. Now I get error codes when switching from mains to battery: E4, E3, E1. Quite random. And obviously system fails
One (I think slave) unit makes a lot of rattling noise. Or sometimes a somewhat slower tick, tick tick (half a second interval)
Cleaning UTP connections or even replacing them helped me in the past, but not this time.
Is this a dead machine or is this fixable?
And if not fixable, can I replace 1 machine? Are 12-15 years old..
1 Answer
Hi,
I like to build a 3 phase system with 3 Multiplus 2 an Pylontech batteries
My idea for the generator is:
* use a 4th Multiplus 2 with the 1 phase generator for charging. Does this work? Do I have more power on this phase?
* or can I use a cheap charger without CAN to charge the Pylontech with the generator?
And I have another question:
* is there a cheap way for more amps for the transfer switch (anti islanding)?
Thanks, Markus
2 Answers
3 Answers
Wood-Mizer makes an MP260 planer/moulder that requires 230V 3-phase power -- it typically draws between 20 and 32Amps.
I understand I can configure a 3-phase system with three parallel inverter/chargers, but which?
I have a MultiPlus 24/3000/70-50 120V VE.Bus. Can that be used to produce a 230V system or do I need to get three 220-240V units?
I'm off-grid, solar and generator, so a Multiplus should be sufficient?
Thank you for your help!
Cheers,
Kailash
2 Answers
I have a 30kW Hybrid unit including DC generator, 48V Li batteries, 3 x 10kVA Quattros in 3phase. The inverters are in inverter mode only and do not charge the batteries, the generator charges the batteries, controlled by a PLC. The inverter configured to cut off at low voltage setpoint.
I'd like to combine two of these units to serve a max of 60 kVA load , 3 phase.
Can I AC couple these systems ? Connecting inverter 1 of each unit to phase 1, etc. so I'd have 2 inverters on each phase, 20 kVA per phase?
Is this possible ? How would it be configured software ?
I realise normally two DC batteries can not be used if not on same DC bus, but does it matter if the inverter never charges the batteries ?
2 Answers
For last couple of months my system ( 3 x 5 KVA Quattors in 3 phase with BYD 10 KWH) randomly resets ( all the quartos go offline and come back on)
#10 Alarm system time sync error, #1 device switched off commonly seen.
Initially, I Suspected network cabling so replaced with CAT 7 high-quality cables and cleaned the network sockets with contact cleaning fluid
Also, checked if all DC connections are tight ( they are )
There seems to be no pattern to these switch offs ( observed at 2 am in the night and also during afternoon or evenings ) -
The system works fine for a couple of weeks and in one day I could face one or more restarts with associated error logs
All firmwares are the latest except Quatro which are on V430 ( latest is 464 i believe)
Quetsions
1- Is there a detailed log somewhere indicating which unit is causing the shutdown
2. Should I upgrade quattro firmsware to rule out any other issues
3. Is this the issue of any external EMF affecting the network cabling ( they run parallel to the power cables - not in my opinion as CAT 7 are each pair individually shielded )
https://www.pcgamer.com/what-are-the-differences-between-cat5-cat6-and-cat7-ethernet-cables/
https://en.wikipedia.org/wiki/ISO/IEC_11801#CAT7
Class F channel and Category 7 cable are backward compatible with Class D/Category 5e and Class E/Category 6. Class F features even stricter specifications for crosstalk and system noise than Class E. To achieve this, shielding was added for individual wire pairs and the cable as a whole. Unshielded cables rely on the quality of the twists to protect from EMI. This involves a tight twist and carefully controlled design. Cables with individual shielding per pair such as category 7 rely mostly on the shield and therefore have pairs with longer twists.
[image]
[image]
4 Answers
Hi,
I do have a Fronius Symo 8.2 with my PV grid tied. Also grid parallel there is a 3 Phase Multiplus II setup with 900Ah 48V Lithium and a Cerbo plus Smart Meter.
I did the system setup with MKII Interface. Remote Control shows everything properly and everything runs fine.
When I use the Victron Connect App I see the Cerbo but when I click on device list, no multiplus is shown. Therefore I cannot adapt any parameter oder do a firmware update.
Is this due to the fact that I run it in 3 Phase ESS mode....?
Any ideas?
thx
charly
2 Answers
Dear Victron,
in May i have seen your blog entry presenting an future Victron Wallbox, i was super happy as i would assume that it would make my life way easier in regard to dynamic/smart EV charging as part of an offgrid 3 phase island system.
As the car is now available i have to decide whether i wait for the finished Victron product (which hopefully offers dynamic/smart charging) or go with an DIY solution including extensive programming (what I wane avoid).
Maybe I am lucky and you are already in a state to spread some more infos to the community!?
Regards
Janek
5 Answers
Hi! o/
I presently have 2 x 48V 3000 VA Multiplus VICTRON PMP483021010 in parallel connected to a LiPo Freedom Won 20/14 LifeP04 KWh battery working great in an offgrid config (+ victron solar gear charging + genset).
Soon I will need to add two three phase devices as load 400 V AC (+-15%) / 3 ~ max actual 32,6A. In addition I need to accommodate the current maximums allowed by my current setup (<=6000W peak, ~4400W sustained on single phase max ambient temp 40C in summer). The three phase loads will never be used at the same time as the max output of a single phase. This is for a small workshop, it's either or, never both. The three phase loads are large compressor + plasma CNC.
Below are the options I think I have. They are in order of preference by cost:
Are any of these options non viable? Are there better options? Ideally option 2 would be 3 phase solution with a single phase using the Multiplus 48/5000/70 + the other 2 phases using my existing Multiplus 48/3000/50s - but I am told should never happen and Bad Things(tm) will happen - and so is excluded for that reason.
Thanks!
Nanzikambe
1 Answer
Dear Victron Fellows,
I have the following use case for two almost identical installations:
On the already existing 3-Phase ESS installation using MultiPlus II Devices, the battery should be charged in case of a grid failure and in time of insufficient PV power.
The installation already has the following devices:
A single phase 5kVA 230V Diesel inverter is available. It should be used to provide the power for the charger.
Is it possible to charge the battery using an additional MultiPlus II connected to the CCGX?
Can the Multi be connected to the CCGX and does it receive the relevant battery information BYD BMS information (DVCC)?
According to the following question it should be possible. And that is what I would expect and I think is the reason of DVCC.
Asking my dealer to verify the answer he told me that it is not be possible to connect the additional Multi to the existing CCGX, because the additional multi would need its own controller and needs to operate independent from the ESS system.
He suggested to connect the Multi by the relays (LINK). This would not be an preferred option for me because I would expect the charging process to be more optimal if it is controlled by the batteries BMS.
If the additional Multi can not be connected to the CCGX, would it be possible to add another Venus device and connect the CAN Bus to this device for retrieving the BMS information?
Best regards,
Martin
3 Answers
Hello,
I understand from the manuals that Multiplus 3-phase networks must be Wye/Star, not delta. However, I should be able to run 3-phase delta loads from the legs of the star, since the line-line voltage would still be 400V. Such a concept is drawn below.
[image]
My question is, what to do with the neutrals? They much be connected for the Multis to reference each other, and they are grounded by the ground relay. As drawn, there is nowhere to place an RCD or ground fault interrupter.
What is the best way to power a 400V_LL, three-wire, three-phase load.
1 Answer
Hi All,
today I had a short circuit in the Critical Loads section on my ESS. All circuit breakers in between grid and the short circuit switched off. Whereas I was expecting that only the circuit breaker of the circuit itself should be switched off.
now I’m searching for some design rules to better design selectivity in case of ESS.
The connection to the grid is made by 25A fuses (3 phase). So to maintain selectivity I have a 3P-16A circuit breaker between the switch board and the Multi’s. I estimated that adding an ESS creates its own energy system but now I realize that under normal circumstances the relais between grid input and Critical Load output is closed. Following the NEN1010 selectivity rules I then have to use 10A circuit breakers to individual circuits. But that means I have to swap my complete household switch board because it now contains 16A circuit breakers which is quite normal in Holland. And it also leaves me in a non preferred situation since 10A is far to low for some off the systems I’m using (dishwasher, etc.).
I have systems on the non-critical side of ESS like EV, heat pump and so on. They have there own 16A circuit breakers.
Perhaps someone can help me with some suggestions to create a save and reliable system? Or is what I described the way to go (using selectivity and see the multi as a intermediate device).
kind regards,
Harold
1 Answer
Is it possible to setuo a 3-phase ESS without a MK3-USB cable?
If yes how? Remote VeConfigure does not have this..
1 Answer
Is a 3 phase system with 3 phase AC input and single phase AC Input possible?
I have a 3 phase system with 3 Multiplus II and i want add additionally a single Phase Mulitplus to load the Battery.
The Battery is a BYD LVL 15.4 kw with BYD BMS
1 Answer
Hello,
I have 3-phase system build on EasySolar-II GX (phase L1), 2x Multiplus-II (phase L2 and L3)
There is no ESS assistant loaded only Two-signai BMS.
First time this system reported overload on phase L3 twice.
It happened when there was grid loss for less than a minute.
System is under development and there is practically no load (50-60W)
Why this overload happen?
[image]
[image]
3 Answers
I have 3 Quattro 48/15000 configured in a 3-phase system.
When ACin is connected, the system doesn't switch and stays in inverter mode. Through VEConfig 3 / CCGX, here are the parameters read.
[image]
[image]
[image]
[image]
Why is Current = 0 A?
In stand-alone mode, each unit switches properly.
ACin parameters
Frequency = 50 Hz
Voltage = 230 V
[image]
3 Answers
I've got 3 x 10 kVA Quattros set up for a 3 phase AC load.
The primary generating source is a 48 V DC Hybrid Generator and lithium battery system connected to the Quattros at 48V DC.
There is a intermittent AC mains resource that I'd like to utilise to charge to batteries or feed the load when available, the AC connection is in single phase. At the moment, the AC-in connection is wired up at 3 phase with 1 phase connected to each of the Quattro AC-in-1 connections.
Can I connect a single phase AC-in even though AC out in 3 phase ?
Should it just be connected to 1 phase only ? i.e. 1 quattro AC-in connection or should I parallel the AC-in across 3 Quattros ?
1 Answer
Hi all,
it seems to me the feature "Switch as Group", in the VE.Bus Configurator, is a bit under-documented .
So, please verify, in a three phase system with Quattros in all phases (at input 1), when "Switch as Group" is not checked, does it affect all the Quattros ? ..... meaning that any of the three, and any number of them, can operate as inverter or charger independently?
In that case, one or two units, could operate with the ""Power Assist" feature, while the remaining one (s) can operate as charger.
Thanks.
0 Answers