Zs and R1+R2 testing Multiplus 2 ESS

I need to check the Ze with the ESS I have. It is a typical ESS with Multiplus 2 10kVA on the incomer, supplied by batteries.

Does anyone have the correct testing proceedure for Ze and R1+R2. I think that the best way to do it will be to fully isolate the Multiplus 2 from circuit and test as normal without Multiplus 2 in circuit. The reason is that even with low ohm testing can cause problems with the ground relay.

For testing the fault current this can be done with the Multiplus 2 isolated from the incomer, expecting a slightly higher resistance and lower fault current than the PME grid, due to smaller transformer size.

Are there any critical don’t does, that will damage the invertor?

Thanks

After much searching I have found an EICR testing document (may save others time in future).

Anyone with other knowledge or experience, I would greatly appreciate any info you can share.

victron_multiplus_ii_10kva_eicr_testing_guide.pdf (5.2 KB)

Are you able to share the source of your test guide?

Energiean.co.uk

Like everything I will be thoroughly checking through the procedure until I am happy, before using it.