I need to check the Ze with the ESS I have. It is a typical ESS with Multiplus 2 10kVA on the incomer, supplied by batteries.
Does anyone have the correct testing proceedure for Ze and R1+R2. I think that the best way to do it will be to fully isolate the Multiplus 2 from circuit and test as normal without Multiplus 2 in circuit. The reason is that even with low ohm testing can cause problems with the ground relay.
For testing the fault current this can be done with the Multiplus 2 isolated from the incomer, expecting a slightly higher resistance and lower fault current than the PME grid, due to smaller transformer size.
Are there any critical don’t does, that will damage the invertor?
Thanks