What I’m seeing is massive, intermittent discharge towards the grid connection (one US2000C is being discharged at 55 A…)
My setup is as follows:
As soon as I switch to the internal meter, everything goes back to normal.
If I disconnect the public grid, it behaves normally too. It only discharges into the public grid in strong bursts (despite the grid setpoint being set to 150 W and grid feed-in to 500 W, but it seems to ignore those values completely).
It’s almost dark outside at the moment, with virtually no sunlight. It’s clearly charging the battery from the grid, but now it’s showing it the wrong way round.
Grid feed-in is also limited to 400W. It says “Grid feed in limit activ? → Yes”, but it doesn’t seem to care.
Has anyone got any other ideas?
If I turn the meter back round, it goes haywire again…
We see you “deliver” 1050W to the net, so the reversed meter works just fine but must be put around to its original place, sorry for that, but that was the test…
You use nothing at home.
Your solar produces 486W.
You battery charges with 486W as well?
I think your CT in the Multi gave up, you should see house consumption…
I would definitely do that with the current sensors. It doesn’t matter whether an external sensor is connected, since the internal sensor is bridged in the jack plug or, on newer models, at the terminal.
This is shown when the ESS Assistant is installed and the Multi is controlled by the GX. So that should be fine.
If you enter No for “Gridmeter required”, it should still fall back to the ET112 as long as one is available.
For an ESS with an ET112, set Gridmeter to “external” and “required” to yes; otherwise, for direct measurement, use Gridmetering internal Sensor.
I’m pretty sure people will be able to help you if you could show the behaviour in a video and post all the relevant settings (including the VE config) here.
Hi, I’d check the Current Sensor connections again more carefully. Dognose posted a link above — have you really worked through it thoroughly?
To me, it looks like you have exactly the problem with the intermittent connection in the sensor bridge, either in the jack plug or at the terminal.
The Multi wouldn’t regulate that quickly when operating in parallel with the grid. I wouldn’t assume it’s a configuration error.
One more thing: it looks like you’ve prioritised renewable energy under Advanced in the VE Config. That’s rather unusual in an ESS. Was that intentional? It shouldn’t be enabled.