Is the ESS oscillation caused by the ET112?

Hi everyone,

I’m having an oscillation issue with the ET112. It’s connected directly to the MP II GX via USB.
The network status shows no errors:

It appears in the device list:

What I’m seeing is massive, intermittent discharge towards the grid connection (one US2000C is being discharged at 55 A…)

My setup is as follows:

As soon as I switch to the internal meter, everything goes back to normal.

If I disconnect the public grid, it behaves normally too. It only discharges into the public grid in strong bursts (despite the grid setpoint being set to 150 W and grid feed-in to 500 W, but it seems to ignore those values completely).

Good afternoon,

Maybe you placed the meter or CTs opposite…can that be?..as then you get those bursts (called runouts).

Regards, Jeroen.

Hi everyone,

I’ve now got around to reversing the meter connection, and it looks like this:

It’s almost dark outside at the moment, with virtually no sunlight. It’s clearly charging the battery from the grid, but now it’s showing it the wrong way round.

Grid feed-in is also limited to 400W. It says “Grid feed in limit activ? → Yes”, but it doesn’t seem to care.

Has anyone got any other ideas?
If I turn the meter back round, it goes haywire again…

Here are a few more pictures of the settings:

How old is your MP?

There was a certain build time that had issues with the AC-Current Port causing “false” signals (Even when no AC Current Sensor is connected)

This could mostly be solved with plugin in “something” a few times and remove it again:

2021_12_mpii_esii_quaii_current_sense_socket_issue___rev4_161783.pdf (491.0 KB)

The document also contains a list of eventually affected units to check against.

Good evening,

We see you “deliver” 1050W to the net, so the reversed meter works just fine but must be put around to its original place, sorry for that, but that was the test…

You use nothing at home.

Your solar produces 486W.

You battery charges with 486W as well?

I think your CT in the Multi gave up, you should see house consumption…

Regards, Jeroen.

All good, no need to apologise — I’m happy to get tips on testing.

I’m not using the Current Sense; my setup runs as a plug-in system.

And what I’ve noticed is that I’m no longer getting any run-outs. Let’s see what it looks like when we get a bit of sun today.

Thanks to you too!

My serial number doesn’t seem to be affected

MP2 3000/35-32

HQ2330xxxxx

And mine doesn’t have the audio jack, but the 3-pin one

Yes, the run-outs have also happened with the counter reversed.

I’m open to any other ideas!

Thanks, everyone!

I would definitely do that with the current sensors. It doesn’t matter whether an external sensor is connected, since the internal sensor is bridged in the jack plug or, on newer models, at the terminal.

Clean, tighten, wiggle.

Hi, thanks!

The plug actually wasn’t plugged in. I’ve plugged it in now, but the timeouts still occur when switching to the “correct” Grid Meter (external Meter).

I’m surprised that the Home Screen shows “external Control”, even though it’s actually setting the parameters itself (Grid Metering → Inverter).

Being able to build any system you like is probably exactly the problem in my case: there are too many options :sweat_smile:

This is shown when the ESS Assistant is installed and the Multi is controlled by the GX. So that should be fine.

If you enter No for “Gridmeter required”, it should still fall back to the ET112 as long as one is available.

For an ESS with an ET112, set Gridmeter to “external” and “required” to yes; otherwise, for direct measurement, use Gridmetering internal Sensor.

I’m pretty sure people will be able to help you if you could show the behaviour in a video and post all the relevant settings (including the VE config) here.

Victron 04082026.vsc (6.4 KB)

Hi, and many thanks for getting back to me!

Attached are the VSC file and the two videos. Do you need anything else (along with the screenshots of the settings)?

I have a US2000C as a battery, and it’s sometimes loaded at 55 A, which is a bit worrying.

Best regards,

Immo

Hi, I’d check the Current Sensor connections again more carefully. Dognose posted a link above — have you really worked through it thoroughly?

To me, it looks like you have exactly the problem with the intermittent connection in the sensor bridge, either in the jack plug or at the terminal.

The Multi wouldn’t regulate that quickly when operating in parallel with the grid. I wouldn’t assume it’s a configuration error.

One more thing: it looks like you’ve prioritised renewable energy under Advanced in the VE Config. That’s rather unusual in an ESS. Was that intentional? It shouldn’t be enabled.

Hi, and thanks so much again!!

My MultiPlus doesn’t have a jack plug, but the newer 3-pin one (the yellow-marked version).

And it fits snugly, too.

But following your advice, I tried the whole thing again!

AAAAAAND…

Now everything’s working just how I imagined!

Thanks to you and all the other supporters here in the chat/forum!