# Why scheduled charging is not starting

**URL:** <https://community.victronenergy.com/t/why-scheduled-charging-is-not-starting/63884>\
**Category:** Deutschsprachiger Bereich\
**Tags:** cerbo-gx\
**Created:** [12 October 2026 19:40 UTC](https://community.victronenergy.com/t/why-scheduled-charging-is-not-starting/63884 "2026-10-12T19:40:32Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![Stevan\_Sewell](https://avatars.discourse-cdn.com/v4/letter/s/f05b48/32.png) [@Stevan\_Sewell](https://community.victronenergy.com/u/Stevan_Sewell)\
**Post date:** [12 October 2026 19:40 UTC](https://community.victronenergy.com/t/why-scheduled-charging-is-not-starting/63884/1 "2026-10-12T19:40:32Z")

</div>

I have MultiPlus-II 48/30000-35/32, Cerbo GX, Pylontech batteries, I am switching to a lower night time tariff, so have been trying to set the ‘Scheduled Charging’ so far without any success. I am in ‘Optomized Mode’ SoC is below the target set etc.

---

<div class="post-metadata">

**Author:** ![HolgerBle](https://avatars.discourse-cdn.com/v4/letter/h/ebca7d/32.png) [@HolgerBle](https://community.victronenergy.com/u/HolgerBle)\
**Post date:** [13 October 2026 07:50 UTC](https://community.victronenergy.com/t/why-scheduled-charging-is-not-starting/63884/2 "2026-10-13T07:50:45Z")

</div>

You should go with “optimised without BatteryLife”…

and is it even worth it? You can only charge at about 1.7 kW from the grid… and around 25% of the power is lost going in and out of the battery..

---

<div class="post-metadata">

**Author:** ![Stevan\_Sewell](https://avatars.discourse-cdn.com/v4/letter/s/f05b48/32.png) [@Stevan\_Sewell](https://community.victronenergy.com/u/Stevan_Sewell)\
**Post date:** [13 October 2026 08:19 UTC](https://community.victronenergy.com/t/why-scheduled-charging-is-not-starting/63884/3 "2026-10-13T08:19:29Z")

</div>

Thank you Holger for your reply I will monitor the economy of charging in the cheaper off peak tariffs bearing in mind that 25% of power is lost going in and out. The Scheduled charging is now working the problem was obvious but unexpected. I hadn’t realised that the there is a difference of 1hour between the Cerbo GX clock and that displayed on the VRM? As I was using the VRM to set Schedules I was always one hour too late!

SS