# Where are the inverter DC fuses supposed to sit — Lynx Power In or Distributor?

**URL:** <https://community.victronenergy.com/t/where-are-the-inverter-dc-fuses-supposed-to-sit-lynx-power-in-or-distributor/64697>\
**Category:** DIY\
**Tags:** beginner, multiplus-ii\
**Created:** [3 November 2026 12:11 UTC](https://community.victronenergy.com/t/where-are-the-inverter-dc-fuses-supposed-to-sit-lynx-power-in-or-distributor/64697 "2026-11-03T12:11:55Z")\
**Posts on this page:** 11\
**Page:** 1

<div class="post-metadata">

**Author:** ![Muguyaro](https://avatars.discourse-cdn.com/v4/letter/m/b782af/32.png) [@Muguyaro](https://community.victronenergy.com/u/Muguyaro)\
**Post date:** [3 November 2026 12:11 UTC](https://community.victronenergy.com/t/where-are-the-inverter-dc-fuses-supposed-to-sit-lynx-power-in-or-distributor/64697/1 "2026-11-03T12:11:55Z")

</div>

I’m reviewing a three-phase quote with:

- 3× MultiPlus-II 48/10000/140
- 8× BYD LV5.0+ (51.2 V, ~41 kWh)
- 4× SmartSolar MPPT 250/100-Tr VE.Can

The quoted DC stack is 2× Lynx Power In with no Lynx Distributor.

My understanding from Victron documentation is that:

- Lynx Power In provides busbar connections for paralleling batteries
- Lynx Distributor holds MEGA fuses for inverter/charger and MPPT connections

If only Lynx Power In is used, where are the inverter DC fuses intended to mount? And how many fuse positions are typically needed for this equipment combination?

Also — does the MultiPlus-II 48/10000/140 require a battery DC disconnect/isolator as part of the installation? The manual mentions one should be included, but I want to confirm where it fits in the architecture.

Thanks.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [3 November 2026 12:19 UTC](https://community.victronenergy.com/t/where-are-the-inverter-dc-fuses-supposed-to-sit-lynx-power-in-or-distributor/64697/2 "2026-11-03T12:19:25Z")

</div>

Most of the questions you are asking are a design one. And are you to you as the installer  
You can house them in the lynx or have them external.

The fusing for the inverters are between the inverter battery terminals and the bus bar. If you use the distributor then they are right there before the bus bar.

As an fYi if you Google it you will find a modification for the lynx power in that people do so you can add mega fusing fusing

Spend a little more time looking at the schematics and the manuals the pictures in them are worth 1000 words and definitely make it clearer than AI.

---

<div class="post-metadata">

**Author:** ![Muguyaro](https://avatars.discourse-cdn.com/v4/letter/m/b782af/32.png) [@Muguyaro](https://community.victronenergy.com/u/Muguyaro)\
**Post date:** [3 November 2026 12:42 UTC](https://community.victronenergy.com/t/where-are-the-inverter-dc-fuses-supposed-to-sit-lynx-power-in-or-distributor/64697/3 "2026-11-03T12:42:50Z")

</div>

Thanks for the response. Just to clarify — are you saying the standard Victron reference design uses Lynx **Distributor** units (with integrated MEGA fuses), or Lynx **Power In** units with aftermarket modification for fusing?

> [@Muguyaro](#):
>
> Thanks for the response. Just to clarify — are you saying the standard Victron reference design uses Lynx **Distributor** units (with integrated MEGA fuses), or Lynx **Power In** units with aftermarket modification for fusing?

---

<div class="post-metadata">

**Author:** ![Muguyaro](https://avatars.discourse-cdn.com/v4/letter/m/b782af/32.png) [@Muguyaro](https://community.victronenergy.com/u/Muguyaro)\
**Post date:** [3 November 2026 14:14 UTC](https://community.victronenergy.com/t/where-are-the-inverter-dc-fuses-supposed-to-sit-lynx-power-in-or-distributor/64697/4 "2026-11-03T14:14:25Z")

</div>

Thanks for the response. Just to clarify — are you saying the standard Victron reference design uses Lynx **Distributor** units (with integrated MEGA fuses), or Lynx **Power In** units with aftermarket modification for fusing?

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [3 November 2026 15:15 UTC](https://community.victronenergy.com/t/where-are-the-inverter-dc-fuses-supposed-to-sit-lynx-power-in-or-distributor/64697/5 "2026-11-03T15:15:04Z")

</div>

The power in is for the batteries, often you can place the lynx shunt and loads and chargers on the other side using the distributor for solar and inverter connections. It is shown like that in the manual. That is how the system is designed by Victron to be used.

However that being said. You can modify it to suit your design if you don’t want to use the whole system.

---

<div class="post-metadata">

**Author:** ![Muguyaro](https://avatars.discourse-cdn.com/v4/letter/m/b782af/32.png) [@Muguyaro](https://community.victronenergy.com/u/Muguyaro)\
**Post date:** [3 November 2026 16:51 UTC](https://community.victronenergy.com/t/where-are-the-inverter-dc-fuses-supposed-to-sit-lynx-power-in-or-distributor/64697/6 "2026-11-03T16:51:59Z")

</div>

Thanks for the clear answer. I’m trying to compile commissioning documentation, so I’d like to reference the official Victron manual if possible. Where in the documentation does this layout appear — is it the MultiPlus-II manual, the Lynx Distributor manual, or one of the reference design drawings like BJE-354A?

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [3 November 2026 19:00 UTC](https://community.victronenergy.com/t/where-are-the-inverter-dc-fuses-supposed-to-sit-lynx-power-in-or-distributor/64697/7 "2026-11-03T19:00:27Z")

</div>

> **[5.1. Lynx distribution system parts - 5. System Design](https://www.victronenergy.com/media/pg/Lynx_Distributor/en/system-design.html#UUID-241a483f-f9c9-5ff3-f4e2-b64906d6226d)**
>
> A Lynx distribution system usually consists of a single Lynx Smart BMS or Lynx Shunt VE.Can module together with a Lynx Class-T Power, Lynx Power In or Lynx Distributor.

Each product page has what you need on it.

> **[Lynx Power In | Victron Energy](https://www.victronenergy.com/dc-distribution-systems/lynx-power-in)**
>
> Connect batteries to the Lynx DC distribution system with the Lynx Power In, a modular DC busbar. Find a dealer nearby.

> **[MultiPlus-II | Victron Energy](https://www.victronenergy.com/inverters-chargers/multiplus-ii)**
>
> The MultiPlus-II is ideally suited for professional marine, yachting, vehicle and land based off-grid applications. Learn more now.

Click on downloads it will jump the page to the section needed

---

<div class="post-metadata">

**Author:** ![Muguyaro](https://avatars.discourse-cdn.com/v4/letter/m/b782af/32.png) [@Muguyaro](https://community.victronenergy.com/u/Muguyaro)\
**Post date:** [4 November 2026 15:05 UTC](https://community.victronenergy.com/t/where-are-the-inverter-dc-fuses-supposed-to-sit-lynx-power-in-or-distributor/64697/8 "2026-11-04T15:05:46Z")

</div>

Thanks LX, that’s clear, and it matches what I’d understood: Power In on the battery side, Distributor for the inverter/charger and MPPT connections.

I’ve since found the arrangement illustrated in the Lynx Shunt VE.Can (M10) manual, §5.2.2 — Power In with paralleled batteries, the Shunt carrying the main fuse, and the Distributor with the fused inverter/charger connections. That example is drawn with lead-acid batteries. Does the same layout carry across to a LiFePO4 bank, or does chemistry change the recommendation?

Two things I’d still like to pin down for the commissioning file:

1. **Fuse positions.** With three inverters and four MPPTs I make it ten fused DC connections — six for the inverters, four for the MPPTs. Is three Distributors the expected minimum, or are MPPT outputs commonly grouped onto fewer positions?
2. **Battery-side fusing.** For a 48 V LiFePO4 bank of roughly 800 Ah, is MEGA fusing in a Distributor adequate for the prospective fault current, or is HRC/Class-T fusing needed on the battery side? Victron’s published three-phase drawings appear to use NH3 HRC 25 kA fuses at the battery racks, with MEGA only downstream.

Separately — the isolator question didn’t get picked up. The MultiPlus-II 230 V manual’s installation warning says every installation must include a means to disconnect the AC and DC circuits, and that where fuses are used a separate disconnect is required between the source and the fuses. Where does that sit relative to the Lynx stack?

Thanks again — appreciate the help.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [4 November 2026 16:18 UTC](https://community.victronenergy.com/t/where-are-the-inverter-dc-fuses-supposed-to-sit-lynx-power-in-or-distributor/64697/9 "2026-11-04T16:18:23Z")

</div>

> [@Muguyaro](#):
>
> Does the same layout carry across to a LiFePO4 bank, or does chemistry change the recommendation

Yes. Ideally they need fuses with higher arc quenching.

> [@Muguyaro](#):
>
> manual’s installation warning says every installation must include a means to disconnect the AC and DC circuits

The separate disconnect is usually local regulations related. But I can say from maintenance and repair as well as system safety you should have it all.  
Position is between each branch of an electrical circuit.  
Where you physically place it could be affected by your physical installation

---

<div class="post-metadata">

**Author:** ![Al-2.0](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/al-2.0/32/338_2.png) [@Al-2.0](https://community.victronenergy.com/u/Al-2.0)\
**Post date:** [4 November 2026 16:25 UTC](https://community.victronenergy.com/t/where-are-the-inverter-dc-fuses-supposed-to-sit-lynx-power-in-or-distributor/64697/10 "2026-11-04T16:25:03Z")

</div>

Do not use MegaFuse for a 48V/51.2V LFP battery bank, they cannot stop the fault AIC rating. Use the BYD cabinet with breakers, Victron Class T PowerIn or external Class T Fuses / NH series Fused Disconnects.

---

<div class="post-metadata">

**Author:** ![frank](https://avatars.discourse-cdn.com/v4/letter/f/3d9bf3/32.png) [@frank](https://community.victronenergy.com/u/frank)\
**Post date:** [11 November 2026 16:03 UTC](https://community.victronenergy.com/t/where-are-the-inverter-dc-fuses-supposed-to-sit-lynx-power-in-or-distributor/64697/11 "2026-11-11T16:03:18Z")

</div>

NH disconnectors are certainly very safe, because the DC fuses used there have the necessary breaking capacity. Adler fuses in the Lynx distributor would also be significantly better than mega fuses, but there is no switch for maintenance. Adler fuses are available from 150–300 A. Best regards, Frank