Victron system in a class B motorhome

,

I know this is a very basic question but I am getting two completely different answers. Our Ford transit has a complete victron system including victron batteries (2x300amh)..The van is outside and we are located in the upper midwest where in can get below 0 degrees for several days (weeks). The van is used occasionally during the cold months but can sit for several weeks without being used. Was told by our installer that we should keep the batteries plugged in to shoreline when not in use even if its for several months. Reading other forums they say don’t keep them plugged in but unhook them completely from all equipment. Last winter kept them plugged in but had several times when the BMS worked and didnt allow charging etc due to the cold. Is this hard on the system?

I’d trust your installer on this one — the BMS blocking charge in the cold is exactly what it’s supposed to do, so the system protected itself. Keeping it on shore power is fine as long as low-temperature charging is prevented, which it sounds like it was.

I have a boat on the UK inland waterways with a full Victron system including the NG lithium batteries and Lynx BMS. I keep it on shorepower over the winter and occasionally see low temp stopping charging, no concerns at all doing this. The solar mostly keeps it topped up, the shorepower is a back up for periods of prolonged low light using the “prefer renewables” option on the Multiplus, often listed as “wind and sun priority”.

I do the same with my RV in Ohio. Last winter, we had some days when the batteries prevented charging, but with shore power connected it was never an issue. Recently, however, I added battery heaters to my Victron NG because I want to do some winter camping this year and I want to make sure I can fully charge the batteries anytime w/o worrying about the outside temperatures.

One more point, as the response is a pretty resounding, yes leave the shore connection connected.

Rather than relying solely on the BMS to prevent cold charging, Victron chargers have a “low temperature cut-off” in the battery settings, so you can prevent the chargers themselves from trying to charge and add a belt to your braces. :+1:

N.B. your chargers will all need to be networked i.e. VE Direct via a Cerbo or the like or “Smart Networked” over Bluetooth to do this as they’ll need to receive battery temperature data.

Ed, I would be interested in knowing what you used for heating the NG, I have thought about it controlled via a Cerbo relay, but so far it has not caused an issue so I have not bothered.

An additional point to keep in mind is, since ive ran into this issue myself, if the VE.Bus BMS deactivates charge due to low temperatures, your system can run into a deep discharge or load cutoff as well.

I did not notice that the BMS deactivated charge due to low temperatures, and over several days the load kept discharging the battery while any charge was blocked, since ive used the vehicle and the Victron system. Until it also ran into a load disconnect. Thats when i noticed the issue. Due to the peristant low temperature, i was not able to restart the system anymore by supplying shore power, since both charge and discharge were blocked at the same time. I had to heat up the battery compartment to get out of that deadlock (Yes you can bridge the ATC signal as well, but charging gets blocked for chemical reasons on low temps, and i didnt want to stress the discharged cells even more).

Additionally, whenever charge is blocked, the charge sources also stop supplying/compensating DC loads. In theory they should be able to compensate for DC loads while holding the battery charge current a zero, since thats what matters. But i understand that in practice this is hard to achieve in a real system, so the safer path is to completely block the sources. Which in turn increases the load on the batteries.

Me personally, if i know im not going to use a system for a prolonged time, upwards of a month or two, i (dis)charge the batteries to about 50% SOC and then physically disconnect a pole, eihter by a switch, or removing a terminal or fuse. Its also a question of wasting energy. Leaving a Multiplus connected to the grid while the rest is idle will easily use 0.5kWh daily in just standby losses (depending on the model and whatever else is in standby as well). Does not sound like much, but over half a year thats 90kWh already, while the only benefit of that is that you dont need to switch the system off when you dont need it.

We make our own heating pads and use relay #2 on the Cerbo to control a SSR or Smart Battery Protect to switch the current. I have three 24V 300Ah NG batteries in my RV. We used four small silicone heating pads per battery sandwiched between two sheets of thin steel and with some corrugated aluminized material adhered to the top for even better heat spreading. Low and slow heating is best, just like BBQ :slight_smile:

Thanks, a good job that, well thought out.

Thank you. We’ve been making and selling them on an ad-hoc basis for several years and they work well.