# Victron Multiplus II AC input current limit is not equal to grid limit

**URL:** <https://community.victronenergy.com/t/victron-multiplus-ii-ac-input-current-limit-is-not-equal-to-grid-limit/24990>\
**Category:** Q&A and troubleshooting\
**Tags:** multiplus-ii, parallel, expert, ess\
**Created:** [12 March 2025 09:37 UTC](https://community.victronenergy.com/t/victron-multiplus-ii-ac-input-current-limit-is-not-equal-to-grid-limit/24990 "2025-03-12T09:37:31Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![vaursechs](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/vaursechs/32/20929_2.png) [@vaursechs](https://community.victronenergy.com/u/vaursechs)\
**Post date:** [12 March 2025 09:37 UTC](https://community.victronenergy.com/t/victron-multiplus-ii-ac-input-current-limit-is-not-equal-to-grid-limit/24990/1 "2025-03-12T09:37:31Z")

</div>

Hi All,

I have a system build for a friend who uses two Multiplus 48/5000 in Parallel on a single phase grid. All loads are on AC-Out. SolarEdge PV system is on AC-In. Victron vm-3p75ct grid meter is connected directly to L1 after the grid meter.

The problem I have is that when I set the Grid Current limit to 25A, the Multiplusses only use a maximum of 25A on the input of the multiplus itself. While when the SolarEdge system is producing power on the AC-in side, the grid meter shows less than 25A.

For example: Solar AC feed in is 10A and grid current limit is 25A, the total amount of current that should be available to the Multiplusses should be 35A. How do I set this up?

 ![1](https://europe1.discourse-cdn.com/victron/original/3X/7/b/7b4f0d15d3a9fd88ff26a677a9b821102a21b22b.jpeg)  
 ![2](https://europe1.discourse-cdn.com/victron/original/3X/3/a/3aa015a73880894c5a5b6a92c29b42be05742139.jpeg)  
 ![3](https://europe1.discourse-cdn.com/victron/original/3X/a/3/a3138844b67f80077363154b6569c2fd0137ec6e.jpeg)  
 ![4](https://europe1.discourse-cdn.com/victron/original/3X/a/1/a15cd2fe9e7a0f95e4085c217a8a4140997a68e3.jpeg)

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [12 March 2025 09:48 UTC](https://community.victronenergy.com/t/victron-multiplus-ii-ac-input-current-limit-is-not-equal-to-grid-limit/24990/2 "2025-03-12T09:48:09Z")

</div>

The limit doesn’t differentiate between sources. It sets the point at which power assist kicks in, as per the manual.  
You could create a nodered flow to temporarily increase the limit by what the PV inverter is producing.

---

<div class="post-metadata">

**Author:** ![vaursechs](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/vaursechs/32/20929_2.png) [@vaursechs](https://community.victronenergy.com/u/vaursechs)\
**Post date:** [12 March 2025 09:55 UTC](https://community.victronenergy.com/t/victron-multiplus-ii-ac-input-current-limit-is-not-equal-to-grid-limit/24990/3 "2025-03-12T09:55:26Z")

</div>

I hope that this is going to be updated on a future firmware update. Personally I have the Multi RS 6000 in my system, and in that system I can set the grid input current and multi rs input current separately:

 ![5](https://europe1.discourse-cdn.com/victron/original/3X/0/0/00a0be003da44f7c0cee2d47605ae4694fa47492.png)

In my opinion, the Multiplusses should ignore the built-in current sensor when an external grid meter is installed.

---

<div class="post-metadata">

**Author:** ![Joerik](https://avatars.discourse-cdn.com/v4/letter/j/3d9bf3/32.png) [@Joerik](https://community.victronenergy.com/u/Joerik)\
**Post date:** [9 April 2025 00:00 UTC](https://community.victronenergy.com/t/victron-multiplus-ii-ac-input-current-limit-is-not-equal-to-grid-limit/24990/4 "2025-04-09T00:00:43Z")

</div>

I think I have your question “in reverse”. understanding your post I think my idea might actually work as I want it to work. Could you take a look please?

Thanks!

edit: the link: [Limit Multiplus current and AC-in connected solar (combined) for external breaker box](https://community.victronenergy.com/t/limit-multiplus-current-and-ac-in-connected-solar-combined-for-external-breaker-box/28258)

---

<div class="post-metadata">

**Author:** ![JeroenSt](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/jeroenst/32/12543_2.png) [@JeroenSt](https://community.victronenergy.com/u/JeroenSt)\
**Post date:** [4 May 2026 20:30 UTC](https://community.victronenergy.com/t/victron-multiplus-ii-ac-input-current-limit-is-not-equal-to-grid-limit/24990/5 "2026-05-04T20:30:29Z")

</div>

The internal current sensor can’t be ignored, sometimes the Victron is limited by the cable and the fuse to the main distribution box while the main fuse is bigger.

I have a friend who has 20A fuse for the Multiplus 5000gx because of wiring that was not replaceable and they have a 40A main fuse. The main is measured with an VM-3P75CT.

So in VE.Configure the limit is set to 18 amps. And I think there is no limit applied on the main since I saw a draw of 25A while the Multiplus was charging with 18A.

So there has to be a setting for the Victron and for the mains.