Victron Multiplus 24/3000/70 and Waveform

I have a V3000 MP 1 and a surfeit of solar energy during the day. So I thought I could use a power reducer to reduce the input power of a 3kW immersion heater in my hot water tank, so I can heat with around 750W from solar.

I bought one of these - Cruise control 230 V, cruise control 230 V, motor 10 A 4000 W | voltage regulator SCR, dimmer, European plug, cruise control, motor use, with protection : Amazon.fr: Industrial & Scientific

The ingredients of the controller are a BTA 41 1000B 40A standard TRIAC and a couple of MPR 275 X2 smoothing capacitors. The BTA changes the phase to achieve the voltage adjustment.

It works - at an output of AC 70v, the DC draw is around 30A at 28v which is perfect.

But there is a light buzz from the Victron as well as the normal cooling fan. I am wondering if this buzz is detrimental in the long term. I assume it is feedback/the harmonics on the AC system making the transformer buzz??

I have attached three oscilloscope traces - the normal output from the V3000,

one of the AC system with the controller in operation

and the other immediately on the output of the controller.

There are more harmonics than usual on both traces.

The alternative device to use is an UNITED AUTOMATION BVR-25 POWER REGULATOR, 25A - BVR-25 Datasheet | United automation The BVR doesn’t change phase but is more ££££.

But now having found this topic - Optimal dumpload regulation from a point of view of a Multiplus

a Crydom PMP2425W would probably do the trick, but I would like to know more about the control method??

rather than trying to “dim” an immersion heater, with consequential degradation of waveforms, why not:-

  1. Turn it on for 10 mins, then off for 20? (could cause lack of system capacity…)

  2. Run it through a step down transformer, stepping down to 120V will give 1/4 power, say ~500W. This will maintain the resistive load.

Thanks. Immersion is 3kW, inverter only 3000VA.

Transformer more interesting.

A BVR-25, which maintains the waveform is probably better. Or a custom immersion with dual elements.

Alternative would be to use a dedicated inverter or Variable Speed Drive to power the heater. Dedicated inverter can be 120V, and you can trim the ac voltage a bit to get the desired load.

Thanks. It occurred to me that a VFD might be the solution without introducing harmonics that affects other electrical items.

I’ve successfully used a 1ph to 3ph 1.5kW VFD to drive my anchor winch motor.

I’ve found this 1ph to 1ph VFD - Wattive Frequency Inverter for VFD Motor, Frequency Converter 2.2kW Single Phase Input 220V Output Single Phase 220V CNC Frequency Converter with 2m Extension Cable : Amazon.fr: Industrial & Scientific

I guess reducing the output frequency reduces the power??

With a heater it’s more important to control the voltage than the frequency. For a motor, the voltage may also be reduced with frequency, but this relationship will depend on the motor requirement. You would have to look at the data sheet.