# Victron Lynx BMS (non NG) in test loop mode with 3rd-party batteries ignores SoC reset settings

**URL:** <https://community.victronenergy.com/t/victron-lynx-bms-non-ng-in-test-loop-mode-with-3rd-party-batteries-ignores-soc-reset-settings/59002>\
**Category:** Modifications\
**Tags:** lynx\_bms, diy\
**Created:** [8 June 2026 07:26 UTC](https://community.victronenergy.com/t/victron-lynx-bms-non-ng-in-test-loop-mode-with-3rd-party-batteries-ignores-soc-reset-settings/59002 "2026-06-08T07:26:44Z")\
**Posts on this page:** 6\
**Page:** 1

<div class="post-metadata">

**Author:** ![Japie.G](https://avatars.discourse-cdn.com/v4/letter/j/7bcc69/32.png) [@Japie.G](https://community.victronenergy.com/u/Japie.G)\
**Post date:** [8 June 2026 07:26 UTC](https://community.victronenergy.com/t/victron-lynx-bms-non-ng-in-test-loop-mode-with-3rd-party-batteries-ignores-soc-reset-settings/59002/1 "2026-06-08T07:26:44Z")

</div>

I was helping a friend getting his victron system up and running. All is okay, but one thing triggers my attention.

The system uses a Lynx BMS (non NG version) on non victron batteries. Therefore the BMS port is bypassed with the victron cable. The device is only used as battery monitor and installed for its DC contactor. I see some issues with the battery monitor.

These are the settings:

 ![IMG_4608](https://europe1.discourse-cdn.com/victron/original/3X/c/d/cd21300db8459562166c771a7af19dd8d936d6b1.jpeg)

Total battery capacity is 628Ah

So it should reset SoC to 100% when voltage of **55,1** AND tail current is 1,5% (so 1,5% of 628A = 9,42a = **520w** ) is reached for **10 minutes**. Right? This is at least how my own smartshunt works.

In the system I am talking about I see this happening:

 ![Scherm­afbeelding 2026-06-04 om 17.18.15](https://europe1.discourse-cdn.com/victron/original/3X/d/2/d2870f023ff63c59a516142583b9e52cbc565cb5.png)

At 14:03 SoC resets to 100% (better said, it just climbed to 100%)

 ![Scherm­afbeelding 2026-06-04 om 17.18.35](https://europe1.discourse-cdn.com/victron/original/3X/c/2/c2ebc484ecc33cbc84d84886fd5f9ecf5aff31d4.png)

But at this specific time the reset limits/boundaries were absolutely not reached as you can see. It looks like the Lynx Smart BMS 500 is completely ignoring setting for the SoC reset.

Is this expected behavior for the Lynx SmartBMS (non NG)? Or am I missing something here?

System:

3x MPII 4k5  
2x JK-BMS v19  
lynx distributor  
lynx bms 500  
lynx class-t power in  
CerboGX running VenusOS Large 3.72

---

<div class="post-metadata">

**Author:** ![Japie.G](https://avatars.discourse-cdn.com/v4/letter/j/7bcc69/32.png) [@Japie.G](https://community.victronenergy.com/u/Japie.G)\
**Post date:** [10 June 2026 05:50 UTC](https://community.victronenergy.com/t/victron-lynx-bms-non-ng-in-test-loop-mode-with-3rd-party-batteries-ignores-soc-reset-settings/59002/2 "2026-06-10T05:50:29Z")

</div>

Nobody knows whether this is expected behavior?

---

<div class="post-metadata">

**Author:** ![Justin](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/justin/32/24_2.png) [@Justin](https://community.victronenergy.com/u/Justin)\
**Post date:** [10 June 2026 19:44 UTC](https://community.victronenergy.com/t/victron-lynx-bms-non-ng-in-test-loop-mode-with-3rd-party-batteries-ignores-soc-reset-settings/59002/3 "2026-06-10T19:44:04Z")

</div>

With respect, you’re using a product in a non-supported manner, using a function intended for use only as a testing method… as such, “expected” behavior doesn’t really exist.

I’ll move this topic over to the Modifications Space for other experimental/non-supported use-case users to weigh in, possible someone in there will have suggestions!

---

<div class="post-metadata">

**Author:** ![Japie.G](https://avatars.discourse-cdn.com/v4/letter/j/7bcc69/32.png) [@Japie.G](https://community.victronenergy.com/u/Japie.G)\
**Post date:** [12 June 2026 10:35 UTC](https://community.victronenergy.com/t/victron-lynx-bms-non-ng-in-test-loop-mode-with-3rd-party-batteries-ignores-soc-reset-settings/59002/4 "2026-06-12T10:35:04Z")

</div>

So you are telling me the battery monitor function (with is just a shunt in my opinion) is depending on the availability of a victron brand battery? Bypassing the BMS with the victron cable is a supported method right?

---

<div class="post-metadata">

**Author:** ![chrigu](https://avatars.discourse-cdn.com/v4/letter/c/ba9def/32.png) [@chrigu](https://community.victronenergy.com/u/chrigu)\
**Post date:** [12 June 2026 11:15 UTC](https://community.victronenergy.com/t/victron-lynx-bms-non-ng-in-test-loop-mode-with-3rd-party-batteries-ignores-soc-reset-settings/59002/5 "2026-06-12T11:15:53Z")

</div>

The lynx BMS is part of the victron smart lithium ecosystem. Theres no mention of third party battery support anywhere.

> [@Japie.G](#):
>
> the victron cable

Which cable exactly?

---

<div class="post-metadata">

**Author:** ![M\_Lange](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/m_lange/32/16_2.png) [@M\_Lange](https://community.victronenergy.com/u/M_Lange)\
**Post date:** [12 June 2026 11:59 UTC](https://community.victronenergy.com/t/victron-lynx-bms-non-ng-in-test-loop-mode-with-3rd-party-batteries-ignores-soc-reset-settings/59002/6 "2026-06-12T11:59:01Z")

</div>

Has the BMS/Shunt be synchronized to 100% correctly? That means charging until the charging current is 0A?

The SOC always goes up if there is a current going into the battery and that way it can reach “100%” before the settings for the synchronization are reached.

> [@Japie.G](#):
>
> Bypassing the BMS with the victron cable is a supported method right?

It’s supported for testing not for permanent use with non-Victron batteries.