I am reporting a suspected New UI issue on a Cerbo GX in an RV with two Quattro 24/5000/120-2x100 120V inverter/chargers.
Firmware: Venus OS v3.71; build date/time 20260315163256.
Operating conditions: Connected to a 30 A shore supply; generator stopped. The New UI identifies the active source as Shore and shows Active AC Input = AC input 1.
Observed behavior / reproduction:
- In New UI, the shore current limit showed 34.0 A and was grayed out. Tapping it displayed: “This current limit is fixed in the system configuration. It cannot be adjusted.”
- The same restriction appeared in both the Quattro device page and the Controls pane.
- Switching to Classic UI allowed the Input current limit editor to open and the value to be changed to 30.0 A.
- Switching back to New UI made the shore limit non-adjustable again, with the same fixed-configuration message.
I had been able to adjust the limit the previous day. No VEConfigure changes were made during this comparison; only the user interface was switched. The generator limit also appears grayed out at 50.0 A, but I am not requesting a change to that limit.
Expected: Both interfaces should agree about whether the active shore input limit can be adjusted.
Workaround: Use Classic UI to access the input-current-limit editor. I have not independently verified the effective current-limit enforcement, so this report concerns the reproducible interface discrepancy rather than claiming a confirmed control failure.
Is this a known issue in v3.71, and is there an official firmware version that fixes it? Please advise which additional diagnostics would help. I have photos of the firmware page and both interfaces.