Venus OS beta v3.50 18: ESS bug: Multiplus not charging battery still here

hi,
I’ve give a try with v3.50 18 and the issue is still here.
with an AC-coupling system:
-multiplus II 10000
-21 x microinverter in AC-OUT critical load
-1 MPPT with 2 x 2 PV

ESS mode 6

only the MPPT is feeding the battery. Multiplus is not

with the official GA release, the issue disappear.
this issue appeared some weeks ago on the Beta train

with v3.41

ESS #6 is a user configuring the CCL in DVCC to 0.
Have you checked this setting?
Which battery is this?

DVCC not used here
ESS is configured to use LifePo4 batt with a two-signal BMS mode
batterie are LTO

with official release it has worked since many month (day zero)
issue started with the beta 3.50 15 (estimated)

don’t know what you are doing in the beta but do not merge that to the GA version as you will induce a regression which will make several hybrid Victron installation out of service

Whatever has gone wrong, ESS believes a manual (user set) limit has been configured to block charge.
If your DVCC is forced off (which is why I asked), that is strange.

1 Like

Hey both, this was a bug, fixed per v3.50~20.

(Pls do confirm! @jps34 )

Hi both
I do confirm the issue is now fixed with v3.50 20

2 Likes