hi,
I’ve give a try with v3.50 18 and the issue is still here.
with an AC-coupling system:
-multiplus II 10000
-21 x microinverter in AC-OUT critical load
-1 MPPT with 2 x 2 PV
ESS mode 6
only the MPPT is feeding the battery. Multiplus is not
DVCC not used here
ESS is configured to use LifePo4 batt with a two-signal BMS mode
batterie are LTO
with official release it has worked since many month (day zero)
issue started with the beta 3.50 15 (estimated)
don’t know what you are doing in the beta but do not merge that to the GA version as you will induce a regression which will make several hybrid Victron installation out of service
Whatever has gone wrong, ESS believes a manual (user set) limit has been configured to block charge.
If your DVCC is forced off (which is why I asked), that is strange.