Two Multi RS units in the system, one of them switched off at the switch.
Since beta-6, the so-called Multi RS system has been shown as OFF, even though one of the two is active as an inverter. The two Quattros in the so-called Quattro system are actually OFF.
Can you provide more detail about your system? Why are quattros and the RS solar systems being mixed?
Worldwide-capable yacht for 50Hz or 60Hz:
Ekrano GX
2x 48/10,000 Quattros in parallel (for high-power loads or charging),
2x Multi RS 48/6,000 (for galley, small loads or charging; no MPPT use due to minimum voltage),
4x MPPT Smart 150/35,
2x Orion Smart 48/24-16,
2x 3kW Safiery Scotty (for 2x Alternator 28V/105A),
72 kWh 51.2V LFP (House),
6kWh 25.6V LFP (Navigation),
2x Onan MDKBR 17.5kW generators (230V 76Ah)
2x VM-3P75CT (1x Shore power & 1x Generator power)
Lynx Shunt & Distribution, Ve.Can, NMEA200, SignalK for control.
The overall system should have nothing to do with the incorrect display of the Multi RS status, as this was still being displayed correctly in beta5.
By the way, we have been waiting in vain for 2 years to be able to operate the two Multi RS units in parallel on AC Out…
I am not convinced that is a supported configuration so experience will vary.
The GX manages one system, it is capable of seeing another vebus system but for monitoring only, and using a mk3 adapter - they can’t share a common vebus.
In this case you are mixing CAN-based RS systems and vebus, that is not documented anywhere , which tends to put it into “here be dragons” territory.
There are existing limitations preventing common use of batteries, not clear from your description. If it isn’t clear if the configuration is fully supported, then that is not something that members are likely to help escalate. I will see if I can get clarity on the mixing of them on a common GX.
In the meanwhile, did it work on 3.79?
Thank you very much, Nick, for your support!
As I wrote earlier, the display was fine up to and including beta5.
When updating to beta6, one Multi RS restarted, and the display has been wrong ever since.
I have now restarted both Multi RS units and the EkranoGX. Lo and behold, it’s displaying correctly again — despite the lurking dragons Matthijs knows about.
Ah ok. There was a similar post for 3.80 where a secondary system on a gx had a bad status. It only resolved after a full reset, something clearly gets stuck and can’t recover cleanly. That provides useful context. Thanks.
I have posted on the internal group asking for guidance.
At least you’re sorted for now.