Venus OS 3.80 / 3.81: Incorrect AC Loads calculation with gen on AC-in

Off-Grid System Setup

  • MultiPlus-II 48/5000
  • Cerbo GX with Venus OS V3.79/V3.81
  • AC-coupled PV inverter on AC-Out
  • MPPT PV Chargers
  • Gen connected to AC-In
  • Gen is started/stopped by the MultiPlus Generator Relay Assistant
  • System worked correctly on Venus OS 3.79 and below

Issue 1: AC Loads shown incorrectly in VRM

After upgrading to Venus OS 3.80 / 3.81, the VRM power flow appears to overstate the AC Loads whenever the gen is supplying power into AC-In.

Venus OS 3.79 (correct)

Multi:

  • AC In = 2106 W
  • AC Out = 2536 W

VRM:

  • PV Inverter = 518 W
  • AC Loads = 3045 W (correct)

Calculation:

2536 W (AC Out)

  • 518 W (PV Inverter)
    = 3054 W

which matches the displayed AC Loads of 3045 W.

Venus OS 3.80/3.81

Multi (correct):

  • AC In = 1993 W
  • AC Out = 2149 W

VRM (incorrect):

  • PV Inverter = 702 W
  • AC Loads = 4376 W (incorrect)

Expected calculation:

2149 W (AC Out)

  • 702 W (PV Inverter)
    ≈ 2850 W

but VRM displays:

4376 W

which is significantly higher than the actual load.

The issue only occurs while the generator input is active and the MultiPlus is in “Assisting” mode.

The Multi’s internal measurements remain self-consistent (AC In, AC Out and DC current all balance correctly). The discrepancy only appears in the VRM/GX calculation of AC Loads after upgrading to Venus OS 3.80/3.81.

Issue 2: Generator tile shows “Stopped”

This has been present since at least Venus OS 3.79.

When the gen is actively supplying approximately 2 kW into AC-In:

  • Generator tile shows ~2000 W power
  • Generator state still displays “Stopped”

The relay of the MultiPlus controlling the gen is definitely active and AC-In is receiving power.

Question

Has anything changed in Venus OS 3.80+ regarding:

  • AC Loads calculation in the VRM or Remote Console power flow,
  • handling of AC-In sources,
  • Generator Assistant state reporting,
  • or the way “Critical Loads” are calculated while the MultiPlus is in Assist mode?

The 3.79 vs 3.81 screenshots seem to indicate a change in the load calculation, while the system configuration remained unchanged.

Thanks, guys!

Hi Andy, thanks for reporting. I forwarded it to a colleague to have a look.

Hi @OGGA ,

I took a look at your site and I notice you also have a second inverter connected to the GX, that appears to be running from the same battery bank. This might be the reason for the change.

In Venus 3.80, instead of showing just the consumption from your “main” inverter, we sum the output of all connected inverters. So the extra 1kW you are seeing there, is the load on the other inverter. At least, that would be my guess. If I am wrong, you are welcome to tell me and I will take another look.

So yes, the way we calculate that did change.

Regarding issue 2, I think there is some confusion as well. That state indicates the state of the generator start/stop component that is built into the GX device, which starts/stops a generator using the relay in the GX, or a dedicated genset controller. You are using the relay in the Multiplus, which is a completely different implementation, and is not displayed on the GX device.

As an aside, how are you enjoying your Ora? I have mixed feelings about mine, mostly around the infotainment, but it’s a good car :slight_smile:

Hi Izak,

thanks a lot for your fast reply and the information you’ve sent.

That all makes a lot more sense now. I wasn’t quite sure what changed in 3.80 but clearly the numbers didn’t line up anymore.
Also, the GX generator component and the resulting state showing in the generator tile also makes sense now. The Multiplus Generator Assistant and the full GX controlled generator start/stop service with warm-up sequence, tank level monitoring and minimum required runtime are two different systems, but only the GX controller shows its state in the VRM. Thanks for the explanation.

Yes, correct, I also have a Phoenix 48/3000 connected to the same battery. With previous firmware up until 3.79, the output of an additional Phoenix was completely ignored. It showed up as a device, was monitored for warnings and alarms, but did not play a role in the overall energy system.

Venus 3.80 introduced support for displaying Phoenix inverter power in VRM, which is a great improvement. I was waiting for this for many years.

However, the new AC Loads calculation now includes ALL GX-connected inverter outputs.

For some systems, especially where a secondary inverter is used as an additional power source or booster inverter like in my setup, this causes the displayed AC Loads to differ significantly from the actual load connected to AC-Out because the power is measured twice.

Would it be possible to make the aggregation optional, or allow specific inverter services to be excluded from the AC Loads calculation? Like an “Exclude this inverter from AC Loads aggregation” checkbox? This monitors all Victron inverters through the GX (alarms,…) and also allows for installations where the inverter output is already upstream of another measured inverter or device.

Not sure if Victron would consider such an option and system-modelling choice but it would give users the most flexibility without requiring Victron to understand every possible system topology out there. The user could simply decide if an inclusion of a Victron inverter makes sense for their specific installation.

I’m more than happy to test any possible Alpha or Beta version and support Victron in the development of such a feature for future updates.

Thank you very much again for your assistance with this.

The Ora is a great car. My wife mainly uses Android Auto with the system, but yeah, the infotainment could be improved a lot with some updates. Especially when you’re used to the Tesla software, it feels a bit outdated​:grinning_face_with_smiling_eyes: I also installed a WICAN OBDII adapter in the Ora which allows to read the vehicles parameters into Home Assistant. We now have a fully automated system for the vehicle and can control SOC level charging, timer settings and desired departure time through the Victron EVCS.

Can you explain what you mean by this?

How it is supposed to work: If one inverter has a 4kW load and the second inverter has a 1kW load, it should show a total of 1+4=5kW of output load.

What your description sounds like: You are seeing more than the expected 5kW of load.

Do I understand this correctly? Or is it merely that you prefer some loads not to be displayed?

Hi Izak,

Andy’s case is different from mine, but the underlying problem is familiar: the equipment works as intended, while the energy flows and statistics do not always reflect what is actually happening.

I currently have three systems where one inverter/charger is used to charge the battery from the grid and another supplies the loads. Their configurations differ slightly. In one of them, a MultiPlus-II charges from a single-phase grid connection, while three Quattros supply three-phase loads. These are two independent VE.Bus systems sharing a DC bus.

On Venus OS 3.79, the power drawn from the grid by the MultiPlus-II was added to the displayed load. When that energy passed through the DC bus to the Quattros and on to the loads, the statistics showed the grid charging the battery while the battery supplied the loads at the same time. The AC input roles were also assigned incorrectly.

I made a package of four patches for this configuration and tested it in my workshop. In the operating conditions I tested, the energy flows and statistics were displayed correctly on Venus OS 3.79. The system is now awaiting installation on site. After that, I plan to update Venus OS to the latest stable release, test everything again, and adapt the package if needed. I have not tested it on 3.80 or 3.81 yet.

This is not a fix for Andy’s case, but another example of how similar accounting problems can appear differently depending on the configuration. I’ve published the package on GitHub, along with a description of the system, the fixes, and their limitations. Perhaps this experience will be useful as Venus OS develops:

Dual VE.Bus Support for Victron Venus OS

Hi Izak,

in my case, the Phoenix inverter feeds the Multiplus and acts as a booster. If the power output of the Multiplus exceeds 3.5kW for 10s, its internal relay closes and activates the Phoenix inverter to supply additional 2kW of power to the Multiplus AC-in (the Ac input current limit controls the output of the Phoenix inverter). When power output goes under 2kW for 60s, the Multiplus turns off the Phoenix inverter again. For this, I use the Multiplus generator start/stop assistant which monitors the load.

Because the Multiplus already shows the correct output power (including the any gen or Phoenix power through its AC-in), I don’t want to include the power output of the Phoenix in the Critical Load calculation again. This was working in V3.79 where the Phoenix output was simply ignored and the Critical load calculation was correct.
With v3.79 the total load consumption shows 2536W, which already includes 2106W from the gen/Phoenix + 430W from the Multiplus in Power-Assist mode. The actual power output of the Phoenix was ignored in the calculation with this or previous firmware versions.

Now, with v3.80+, the GX uses the Multiplus output power (which already includes the Phoenix output) and adds the power output of the Phoenix once again. Therefore, it shows an exaggerated power output of 4642W of which 2536W are coming from the Multiplus and Phoenix + 2106W from the Phoenix inverter again.

If the inclusion of Victron inverters to the load calculation would be optional, I could simply switch this off for my Phoenix inverter and the calculation would be correct again.
Alternatively, I can also unplug the Phoenix inverter from VE.direct to overcome the issue, but this is of course not ideal as I lose all monitoring capability of the Phoenix and make this great Victron device basically to a dumb non-Victron inverter.

Thank you again.

Yes, that would be the obvious solution. I think users might have other reasons to also exclude it too. I made an issue in the issue tracker for adding some sort of option to make it optional.

As usual, the hardest part of the project will be to think of a proper name or label for the feature. The mechanics isn’t all that hard :slight_smile:

Thanks for reporting!

I think a per-device option may be more flexible than a global System Setup option.

Example: one Phoenix inverter used as a booster on AC-In could be excluded, while a second Phoenix inverter supplying an independent load circuit could still be included.

Something like this maybe?