V3.90-beta7: 16-cell Pylontech-protocol battery stuck at ~56.1V / 96%, never reaches full
v3.90-beta7: 16-cell Pylontech-protocol battery stuck at ~56.1V / 96%, never reaches full
System: Cerbo GX (Venus OS Large), 1x MultiPlus-II 48/5000/70, SmartSolar 250/100, 150/100, 150/30, 500A SmartShunt. 6x Eco-worthy Cubix 100 (16S) in parallel, Pylontech protocol over CAN, BMS is the battery monitor. DVCC on, CVL limited to 57.6V, ESS Optimized without BatteryLife.
On v3.90-beta7 the system held charge voltage at about 56.1V (≈3.51V/cell, which matches the BMS-reported max cell voltage) for weeks. SOC stalled around 96%, and one pack sat at 91%. The BMS was requesting CVL 58.4V. Before the beta (prior to roughly 9/22) the bank regularly reached ~58V and 100%.
I downgraded to v3.81 Large and the bank went to 100% almost immediately: all 6 packs at 100%, CCL dropped to 0.
It looks like the new 16-cell overvoltage algorithm limits pack voltage to (max cell voltage × 16) and never lets the bank finish charging or balancing. Is there a way to tune or disable this for batteries whose BMS handles cell balancing?
Hi @robneff ,
If I understand correctly, you have a battery that isn’t actually a Pylontech battery, but is detected as one, which is now no longer fully charging?
There is a change in Venus 3.90 beta 7 specifically targeting 16-cell Pylontech batteries, to keep the highest cell at 3.52V.
This algorithm was already used on 15-cell batteries since Venus 3.60, and we expanded this to the 16-cell batteries as well. But because your battery is incorrectly detected as Pylontech, it uses a lower charge voltage than the 3.65V per cell the pack expects.
Usually the reason this happens, is because the battery sends the CAN frame with id 0x359, and they duplicate the letters PN (Pylontech) directly from the original protocol, which they really shouldn’t do. We then assume it is a Pylontech battery.
We will have to find a workaround to better detect batteries that send this data, but are not Pylontech.
Right now the only solution is to stay on an earlier beta until we can work something out.
I created an issue in our issue tracker to improve this.
The battery identifies as ECO-LFP4, but because we don’t recognise this string, it falls back to detecting it as Pylontech instead of Generic CAN-BMS. If we force Generic for all unknown manufacturer strings, it should resolve this issue.
Thanks for the quick and clear explanation, that matches what I’m seeing. My bank is 6x Eco-worthy Cubix 100 (16S LiFePO4) in parallel, not Pylontech.
One more detail that may help with the detection fix: in Eco-worthy’s app, the battery’s CAN protocol is already set to “Victron” (RS485 is set to Pylon). Even in that mode, Venus detects it as Pylontech, so it looks like Eco-worthy’s “Victron” CAN mode still sends “PN” in 0x359. Screenshot attached.
For now I’ve gone back to v3.81 stable, and the bank charges to 100% again with all six packs at 100%. Could you post here when a workaround is ready? I’m happy to test a beta with it.