Thanks Buzzy. I currently have 23 hours of battery life per day without solar. Small 1 bed modular home. Currently using a petrol generator to top off lack of sunshine. In 3-3:30 hours the battery will charge from 0 to 100%. In sunshine or using generator, A second similiar battery costs 2700 euro from a company in Tipperary. But I believe you can now pick up 24v batteries with 400oh which would be roughly 10kv. Cheaper option than parallel charging two identical expensive batteries.
Estimating your consumption is roughly 200Wh, agree more battery capacity would help, but then your tropical Irish location means more sunshine power may be needed especially on cloudy days to keep things charged up.
I’m not going to suggest switching to 48V, as that is going to add a lot of cost in replacement equipment.
Maybe switch battery vendors and sell off the old battery to help pay for the upgrade?
Coming late to this, but since all five questions are still open, here is how I would work through it.
On the 400Ah question first, because it decides the rest: your MultiPlus 24/5000 can pull well over 200A at full load and charge at 120A, so any single 24V box needs a BMS honestly rated around 250A continuous, plus cabling and fusing sized for it. A lot of the cheaper 24V 400Ah units are built around 100-200A BMS boards — fine for lighter loads, marginal under a 5000VA inverter at 24V. Two identical 210Ah units in parallel split that current, which is the quiet advantage of the parallel route, but only if they are the same model and firmware, similar age, on equal-length cables, and individually fused.
On integration: at 24V, very few third-party batteries actually talk to the CCGX over CAN with proper DVCC control. Most run voltage-based, which works, but you lose accurate SOC and charge coordination. If managed comms matter to you, that is the filter to apply before price — and honestly it is where the Li-Gen earns part of its premium.
The energy math is the part I would check before spending anything. At roughly 5 kWh a day, 10 kWh buys you about two days of autonomy, but 1.86 kWp in an Irish winter will not refill a bank that size — expect the generator to carry more of the load, and a full recharge of a 400Ah bank takes roughly twice your current generator run. Doubling the array to around 3.7 kW helps in summer, but at 24V that is roughly 150A of charge current, so plan on a second MPPT and check string Voc against the 150V limit on cold mornings.
If it were my system, I would price both routes per usable kWh (including selling the Li-Gen if you replace it), and only take the generic 400Ah route if the BMS rating and low-temperature charge protection are documented rather than just claimed. Full disclosure: I write about home renewable energy (it is in my profile) and keep a running breakdown of home battery storage costs — mostly US pricing, but the cost-per-kWh way of comparing translates anywhere.