Hi everyone,
I have a question about how a Victron ESS curtails output when the DC-coupled PV system is significantly oversized.
I’m planning to build my first Victron ESS in the near future, and this question has been going round in my head. I haven’t been able to resolve it so far.
For example, consider the following setup:
-
48 V ESS
-
Cerbo GX
-
Several SmartSolar MPPTs
-
LiFePO₄ battery
-
Later, 3× MultiPlus-II 48/6500
-
Around 30 kWp of DC-coupled PV in the longer term
-
Distributed across three different orientations, so the full rated PV output is only available simultaneously very rarely
Of course, I realise that having to curtail PV output is not particularly sensible economically or in terms of energy yield. For now, I’m purely interested in the technical theory and how the system behaves in this borderline case.
In my mind, the scenario would look something like this:
Due to the three orientations, the nearly 30 kWp PV system would produce significantly less than its rated output for most of the time. The 3× 6.5 kW units could handle a large proportion of this on the AC side. However, if, for example, 20–25 kW of DC PV were available for a few hours, the battery were full and the Multis could only deliver part of it to the house or grid, perhaps the final 20% of the PV output would have to be curtailed — in other words, the peaks would be smoothed out.
The actual question is: Is this possible at all, and if so, how does the curtailment happen technically?
Is there active power control whereby the Cerbo/MultiPlus units provide the SmartSolar MPPTs with a specific power setpoint or limit?
My current understanding is roughly as follows:
-
The battery reaches the configured CVL, e.g. 55.2 V.
-
With DC surplus feed-in enabled, the DC voltage is allowed to rise slightly above the CVL.
-
The MultiPlus units try to draw the additional DC power on the AC side and feed it into the house or grid.
-
Once the Multis reach their maximum DC→AC output, they can no longer draw any more power from the DC bus.
-
The DC voltage continues to rise towards the permitted limit.
-
The SmartSolar MPPTs then leave the MPP and reduce their PV output.
Is that correct?
Or is there also some kind of direct, coordinated power limitation between the GX, MultiPlus and SmartSolar MPPTs?
In short: Can 3× MultiPlus-II 48/6500 technically be operated without problems with nearly 30 kWp of DC PV if, due to the different orientations, for example 80% of the generation falls within the available AC power and you consciously accept that the remaining peaks will be curtailed when the battery is full?
Thanks everyone!