I’d like to report a possible issue related to the grid input power limit in recent versions of Venus OS.
My installation has a Cerbo GX, three MultiPlus-II 5000 units connected in single-phase parallel, and an ESS system.
In VEConfigure, I have set an input current limit of 63 A, and the Dynamic Current Limiter option is disabled.
Since September 2026, I’ve noticed that the system does not import more than approximately 10 kW from the grid, even when there is enough demand to exceed that power level.
Tests carried out:
With Venus OS 3.80, the grid input power appeared to be limited to approximately 10 kW.
I installed Venus OS 3.79 and the problem disappeared. Grid input power once again exceeded 10 kW, reaching 15kw, which is the contracted capacity.
I subsequently updated to Venus OS 3.81, and exactly the same limitation returned.
These tests suggest a possible regression introduced after Venus OS 3.79, related to the management of the input current limit, the ESS, or VE.Bus systems with multiple units connected in parallel.
Has anyone else experienced this behaviour with Venus OS 3.80 or 3.81?
I’d be grateful if the Victron development team could investigate this issue.
Yes, I have the same problem, 2x MPII 5k in parallel, 100 A single-phase grid supply.
When the EV is charging, the MultiPlus battery charging current is reduced significantly. In one test the battery charge current fell to approximately 63 A (from 140A).
The behaviour appears to keep total grid import at approximately 10 kW, even though the MPIIs are in a grid parallel configuration.
When the EV stops charging, the MultiPlus battery charging immediately increases back to its normal full rate (140A).
I then rolled the GX device back from Venus OS 3.80 to the previous firmware (3.79), and the 10kW limit is removed.
Checks performed:
ESS Peak Shaving is disabled.
DVCC is not imposing a charge-current limit through the UI.
Full Installer access is enabled.
No intentional ~10 kW grid-import limit has been configured.