I look after a site which has 3 Victron Quattro 48/15000/200-100/100 230V in 3 phase config
It is an off grid installation
I randomly get an error on all 3 at exactly same time:-
Temperature L1’ on ‘VE.Bus System [276]
Temperature L2’ on ‘VE.Bus System [276]
Temperature L3’ on ‘VE.Bus System [276]
Then instantly get:-
Temperature L1’ cleared on ‘VE.Bus System [276]
Temperature L2’ cleared on ‘VE.Bus System [276]
Temperature L3’ cleared on 'VE.Bus System [276]
The error times and cleared time are identical
Any one else had this issue or anyone have any ideas how to resolve ?
Did you check to see if they are hot? It is a temperature warning after all.
It is possible it is hovering on the threshold. There could be heat accumulation around the units.
What is your installation like space wise and air flow? What kind of loads are the units running?
Usually air conditioning cooling the room is the answer.
No not excessively Hot (No more than normal)
Room Temperature 28C
Full Fan forced Air Circulation.
Seems strange all 3 inverters go to Over Temp and then all 3 clear instantly ? (Within 2 seconds)
Hi Kevin, what is the load like at that moment and what is the load?
Good evening,
Do the fans run at that point?
Place tell tails to see the air flow, and are your filters clean?
The fans start at 40 degrees, measure the output air to see if it is really that temperature.
Is silent fans switched on (no fans)?
Regards, Jeroen.
Fans run based on load, not purely temperature.