I’m trying to get some information about the daily production of controllers, but unfortunately I’m only able to do it for the first MPPT controller.
If i read registers 784,785,786,787 there are values, but only from first regulator.
I need to read the same informations from other regulators.
There are avialble registers 3708…3727 but i can read only zero, no correct values.
Next possibility are registers 3148…3167 but there i don’t have any answer.
Please, if exists any possibly how to read these informations via TCP Modbus, give me feedback. Thanks.
If you go to Settings → Services → Modbus TCP → Available services, what do you see there?
Do you see all controllers?
If yes, you may need to change the device ID with the ones there for reading individually.
I can see ID Units:
com.victronenergy.battery - ID225
com.victronenergy.solarcharger - ID1
com.victronenergy.temperature - ID26
com.victronenergy.temperature - ID25
com.victronenergy.temperature - ID24
com.victronenergy.solarcharger - ID100
com.victronenergy.vebus - ID227
com.victronenergy.hub4 - ID100
com.victronenergy.system - ID100
registers 3708…3727 are in com.victronenergy.solarcharger ID1 or ID100.
I tried all of IDs from CERBO ID list (1,100,225,227…)
I can read this registers via TCP Modbus (ID=1 or 100), but values in these registers are zero.