Hi for quite some time now I regularly get low battery ALERTS notifications from VRM while my battery is completely fine with pleny of chenergie. The CLEAR message always follows a few seconds after that.
The system is setup with a min charge setting of 11%.
See below email I received while the battery is at around 51%.
From: VRM Notifier bounces@victronenergy.com
Subject: ALERT - ‘Hweg’: ‘Low battery’ on ‘VE.Bus System [276]’
Date: Wed, 4 Nov 2026 18:48:49 +0100 (CET)
To: marcel@emol.nl
This can happen if the connection to the battery BMS is unstable.
It can also happen when the GX device is overloaded and cannot allow communication between the BMS and the MultiPlus via DVCC. That’s probably what’s happening here, if the clear is immediately afterwards.
I have seen this on installations with a Color Control, which has limited processing power
So first of all, I was mislead by the alarm in thinking it was about SOC values, while it indstead is about battery voltage. Maybe the alarmmessages could be a bit more informative.
This is a 16S system (3x16 EVE MB31)
20 minutes ago I changed the cut off voltages (lowering all off then by 0.5V). Currently thaey are set to:
You are running them at the bottom end of their cell range with close to 100A load. Lifpo4 are known to have issues there. And more so if the battery bank is ageing or weak.
Massive drop under load could be high resistance in the battery, or DC to the inverter. I see a 0.3v drop between the battery and inverter). So if that is a DIY battery check it is still ok in construction. Or just give it a good charge to full.
Then you can have soc drift as well to add to the confusion.
So 47v at 50% does seem a bit low to be honest as I scanned first I thought you had 15s batteries untill I read deeper.
In the first voltage picture you can also see the voltage from the battery (yixiang).
The BMS is JKBMS.
After charging the battery to 100% the voltages are in line with expectations again. The whole soc range from 10 to 90% shows around 53V now!
So again, it just was a massive SOC drift case.
Thanks all for your comments and suggestions that pointed me in the correct direction.
And yes, if Victron staff reads this, please update the alarm message contents to be more informative. I see the console shows ‘low battery voltage’, but the email message just shows ‘low battery’. Also adding the measured value to message (also in the console) would be helpfull as well!