Spikes in A when consumption from the Public Grid is present

Hello Everyone,

Nice to be here. I haven’t been on forums since the 2010s, it’s a nice feeling and from what i have read so far, a nice community too.

I would like to introduce you a situation which I encounter since my PV system was installed (more than 1 month ago).

First, my system main components:

  • one MultiPlus-II 48/10000/140-100 inverter;
  • 3x LiFePo4 Battery 51,2 V/100Ah NG;
  • 3 SmartSolar MPPT 250/100 -TR Ve Can
  • 26x Canadian Solar 460 W

My connection to the Grid is ensured through a 150 m long underground cable (10mm2 AL) ( I mentioned this part because i think it is relevant).

The situation is the following, when the system consumes from the Public Grid, I have really high spikes of A (for example, when I extract 400-500 W from the Grid, the V is 220-230 stable, but the current goes nuts, sometimes hitting 30-40 A (or even higher). Even in the situations when the system was at rest (the panels are not producing, the battery is not charging/discharging) the minimum current from the grid as like 2 A for everything under 150 W. So if i had a consumption of 50 W from the grid, i would still have minimum 2 A (which is huge for this power, when V is constant 210-230).

From what I have been able to observe (through multiple trial and errors with changes in the system parameters) I have managed to narrow the presence of this problem to the following situation:

  • it appears that the spikes are present when the battery charges from the Grid.

At this moment, i switched the system physically to the “Grid” (which i thought that it meant that my home will draw energy directly from the public grid, but it is not the case) from “Victron system”. This way i thought that i will bypass Victron configuration (i wanted to see if that this is the problem), but the electricity still passes through the inverter. However, this was not entirely in vain because now the house is entirely charging from the public network at a stable rate (V stable and A stable) WHILE battery is discharging. This is an important part because from what i have been able to see is that when the battery starts to charge (even a few W, most probably to “balance” the cells, individually) the A goes nuts, if my home consumes 800-1000 W and a few W goes to the battery, the entire consumption is plagued with 20-30 A for 1000 W drawns from the grid (again, with V stable at 210-230).

This being said, i don’t know if i identified correctly the problem (i still investigate this with my installer) but i tend to think that i found the situation when these spikes appear. Now, i don’t know why and more important, i don’t know what i could do. Any opinions, suggestions would be well received.

PS: I don’t know why my post was moved in “DIY”. I started it in the “Q&A and Troubleshooting” section.

Disabled ESS LOM if you are able to test and see.

Also did the cable get meggered?

What is the voltage doing when the spikes occur

Hello Radu, Keep working with your installer.

More details will be needed about your setup for any of us fellow Victron users to lend a hand. Examples:

  • Schematic wiring diagram and photos of the equipment
  • Spreadsheet or other system calculations. Checking the math would be good!
  • Complete list of equipment? e.g. is there is an AC current meter; Lynx busbar and BMS setup; a Shunt measuring battery voltage and current; Ekrano or Cerbo GX controlling everything. Any extra AC PV inverters.
  • What country? Are you running ESS or DESS energy storage system, what’s the idea e.g. to save peak costs, sell back extra solar, run everything off grid if the grid fails?
  • What are the AC loads on the MP II? eg single phase 230V feeds what things in the house?
  • How are you getting the current and wattage measurements? eg with actual test equipment or from an Ekrano GX?
  • Have you tested the system in sections? e.g. with PV disconnected from th MPPTs, so they aren’t contributing to what is going on.
  • Is the system setup in VRM? If so, some graphs would help us understand

Concerns:

300Ah (15kWh) might not be quite enough battery for a MPII 48/10000. Either your battery is possibly a bit undersized (minimum is 250Ah, 1000Ah is the upper end) or inverter is oversized. So at nearly full load, it will be running low in just over an hour. :face_with_spiral_eyes: And then it will want to be topped up, running the charger a lot.

Solar panel arrangement - how are the panels arranged? 26 panels on 3 MPPT 250/100 could be excess voltage on cold days, depending on how things are arranged. If it was just 24 panels, 8 in series on each MPPT, open circuit voltage exceeds 315V, and the absolute maximum is 250V for the MPPT. So hopefully they are arranged differently.

Good luck and welcome to the Forum!

Welcome. There are some great folks here with plenty of knowledge. Also lots of information for you to discover as well.

Hello LX,

Thank you for the proposal. I will talk with the installer. As of yet, i have access only to the VRM platform. From what i understood, this option is in VE Configure (which I cant access right now).

Regarding the megger, no, i did not, however, it would be a little strange that if it is a problem on the insulation, this would appear only when the battery charges. However (2), i am not an expert, therefore i cant exclude any possibilities, i will put on the list for checks.

The voltage is stable when the spikes occurs. I use the system’s meter, a Carlo Gavazzi Et340 (if i am not mistaken).

Hello Buzzy,

There is some information that you request, i will try to gather all the pieces that you requested and reply on each of your point. Much of this data is not in my hands (but the installer’s). I will try to see what i can do.

For an additional context, i have almost the same configuration (only that the system is on trifazic) a few streets away and there the system runs perfectly (i have even less storage there, only 10 kWh, ofcourse, there are smaller inverters, i believe 3 x 5 kW)

Thank you for the welcoming Nick.
Definitely, there is a lot of information here and thats perfect because i want to add:

  • a bidirectional charger (EV);
  • a heat pump;
  • and a little bit further in the future, to optimize the production/consumption based on dynamical tariffs. (my head is already spinning only thinking about this). But first, to straight the problems a bit.