Hi,

installed two new VM-3P75CT.

The one configured as 3p net meter shows details for L1 only.

When configuring using VictronConnect (vrm, the Cerbo, devices) the dropdown combo boxes for role and phases are empty.  
I selected “net meter” and “3 phase”.  
There is no save button.

The meter keeps showing details for L1 only.

Also a factory reset holding “reset” button 3 + 10 seconds did not change the behavior.

VictronConnect is current version on iOS.

For the VM-3P75CT pls find screen shots attached. Any Idea?

[https://vrm.victronenergy.com/installation/382372/dashboard](https://vrm.victronenergy.com/installation/382372/dashboard)

BR  
Bjoern

 ![IMG_9543](https://europe1.discourse-cdn.com/victron/original/2X/9/9b825fd1652694aa119a62c872e588ea0b8f9e94.png)  
 ![IMG_9542](https://europe1.discourse-cdn.com/victron/original/2X/6/6f373e9534d87be2882bbda0965ce7a726a7fe34.png)

---

<div class="post-metadata">

**Author:** ![Luc](https://avatars.discourse-cdn.com/v4/letter/l/9dc877/32.png) [@Luc](https://community.victronenergy.com/u/Luc)\
**Post date:** [4 November 2024 08:31 UTC](https://community.victronenergy.com/t/solved-vm-3p75ct-cannot-change-settings/10089/2 "2024-11-04T08:31:09Z")

</div>

Hi @BjoernK, I can see all three phases on VRM. Can you confirm that you still have this issue?

If you are on the VictronConnect v6.10 beta, there might be some incompatibility with firmware v1.06. But since you mentioned you are on the latest version I don’t believe this to be the cause.

---

<div class="post-metadata">

**Author:** ![BjoernK](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/bjoernk/32/89_2.png) [@BjoernK](https://community.victronenergy.com/u/BjoernK)\
**Post date:** [4 November 2024 12:44 UTC](https://community.victronenergy.com/t/solved-vm-3p75ct-cannot-change-settings/10089/3 "2024-11-04T12:44:40Z")

</div>

@Luc  
Tranks for taking care.  
Confirm. Now it’s showing three phases and also the drop-down combo boxes in VictronConnect are filled.

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [19 March 2026 14:06 UTC](https://community.victronenergy.com/t/solved-vm-3p75ct-cannot-change-settings/10089/4 "2026-03-19T14:06:17Z")

</div>

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.