# Solar inverters missing in venusOS

**URL:** <https://community.victronenergy.com/t/solar-inverters-missing-in-venusos/64228>\
**Category:** DIY\
**Tags:** 3-phase, vrm, energy\_meter, cerbo\_gx\
**Created:** [22 October 2026 08:22 UTC](https://community.victronenergy.com/t/solar-inverters-missing-in-venusos/64228 "2026-10-22T08:22:41Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![BAnders](https://avatars.discourse-cdn.com/v4/letter/b/dbc845/32.png) [@BAnders](https://community.victronenergy.com/u/BAnders)\
**Post date:** [22 October 2026 08:22 UTC](https://community.victronenergy.com/t/solar-inverters-missing-in-venusos/64228/1 "2026-10-22T08:22:41Z")

</div>

Somehow my Growatt PV inverters have gone missing after the grid connection was upgraded from a single phase to 3-phase connection. Both missing in VRM and in VenusOS. I’m actually a bit puzzled about this since two of the AC connected inverters are still on L1. Still charging the battery, and the production is still visible on a self made NodeRED dashboard.

Currently still only one Multiplus II on L1 (bidirectionally connected on AC-in) and the battery is charging, but not using all PV power.

I have one additional PV inverter moved over to L2, but everything is put on L1 by a script (reads data from the kWh meters). Worked flawlessly for over a year and a half so what am I missing here?

I have a VM-3P75CT setup as grid meter, but still only with one single CT clamp. I will change this later today so that all three are installed, but I am still missing some hardware to make this work. Will arrive this afternoon. Hence the lack of solar production in VRM etc

Edit: I wonder if the phase rotation (L1-L3-L2) could be the culprit. It might just be the lack of CT clamps on all phases but the Victron grid meter is still set to 1 phase only. Yeah puzzled. Something new to me.

Edit-2: It magically started to show up again. A day after I added the CT clamps. I surely did not solve this issue myself.

Did nothing on the software side of things, other than switching the meter setting from L1 only to 3-phase.