# Soc wont reset have added pic of settings and diagram of system i have 2 array system

**URL:** <https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592>\
**Category:** DIY\
**Tags:** victron\_community, mppt\_controllers, diy\
**Created:** [7 September 2026 19:24 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592 "2026-09-07T19:24:03Z")\
**Posts on this page:** 13\
**Page:** 1

<div class="post-metadata">

**Author:** ![joe4](https://avatars.discourse-cdn.com/v4/letter/j/c37758/32.png) [@joe4](https://community.victronenergy.com/u/joe4)\
**Post date:** [7 September 2026 19:24 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592/1 "2026-09-07T19:24:03Z")

</div>

![controller 1](https://europe1.discourse-cdn.com/victron/original/3X/a/6/a697692bdb76ea463c803755a67631cdbfcfdbcf.jpeg)

 ![smart shunt](https://europe1.discourse-cdn.com/victron/original/3X/4/a/4affefb5dd241b5f60fa1305d17a6c3eb5048df2.jpeg)

 ![controller 2](https://europe1.discourse-cdn.com/victron/original/3X/e/b/eb1a003bccfea0bc1d51506bfa6566c32d37991d.jpeg)

 ![diagram of solar panel](https://europe1.discourse-cdn.com/victron/original/3X/b/b/bb0fa9a556a97a73ef2710f8008dbe380b7be0f5.jpeg)batteries are on this side 3- 24v batteries

My SOC wont reset to 100% on its own when fully charged. The SOC wont show a increase in charge % when more power is coming in than going out.

---

<div class="post-metadata">

**Author:** ![MikeD](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/miked/32/1522_2.png) [@MikeD](https://community.victronenergy.com/u/MikeD)\
**Post date:** [7 September 2026 21:17 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592/2 "2026-09-07T21:17:58Z")

</div>

Both the inverter and the MPPT should be connected to the load side of the shunt.

Without this, the charge is not registered, and the tail current won’t drop to below the limit.

---

<div class="post-metadata">

**Author:** ![joe4](https://avatars.discourse-cdn.com/v4/letter/j/c37758/32.png) [@joe4](https://community.victronenergy.com/u/joe4)\
**Post date:** [7 September 2026 21:22 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592/3 "2026-09-07T21:22:38Z")

</div>

so are you saying i need to add a jumper wire from my neg buss to the load side?

---

<div class="post-metadata">

**Author:** ![joe4](https://avatars.discourse-cdn.com/v4/letter/j/c37758/32.png) [@joe4](https://community.victronenergy.com/u/joe4)\
**Post date:** [7 September 2026 21:33 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592/4 "2026-09-07T21:33:42Z")

</div>

sorry that’s not what i meant . i meant to remove the neg from the controller that’s on the neg buss bar and put it on the neg load side

---

<div class="post-metadata">

**Author:** ![MikeD](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/miked/32/1522_2.png) [@MikeD](https://community.victronenergy.com/u/MikeD)\
**Post date:** [7 September 2026 21:34 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592/5 "2026-09-07T21:34:49Z")

</div>

No, The negative bus connects to all of the battery -ve terminals and the battery terminal of the shunt. NO OTHER wire connects to this node. Both the Inverter negative and the MPPT battery negative connect to the LOAD side of the shunt, as does any other load / charger on the system.

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/b/e/be2d0544947ae43298199d70bff22d268986ba3b.png)

---

<div class="post-metadata">

**Author:** ![pwfarnell](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/pwfarnell/32/2341_2.png) [@pwfarnell](https://community.victronenergy.com/u/pwfarnell)\
**Post date:** [8 September 2026 14:13 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592/6 "2026-09-08T14:13:43Z")

</div>

@joe4 See the linked FAQ, especially the diagram.

> [@Shunt / battery monitor not reading the correct SOC/ Amps, missing solar, decreasing daily or other misreading problems](https://community.victronenergy.com/t/shunt-battery-monitor-not-reading-the-correct-soc-amps-missing-solar-decreasing-daily-or-other-misreading-problems/87):
>
> This topic covers the SOC / Amps reported by BMV battery monitors, SmartShunts, Lynx BMSs and Lynx Shunts and will just be called shunt below. It is also assumed that the shunt is monitoring the domestic / house / cabin battery bank and not engine start / bow thruster / winch / caravan mover battery banks. The problems may be one or more of the following The SOC decreases daily despite the solar charger or other charger(s) working. The SOC increasing when discharging and falling when charging…

---

<div class="post-metadata">

**Author:** ![joe4](https://avatars.discourse-cdn.com/v4/letter/j/c37758/32.png) [@joe4](https://community.victronenergy.com/u/joe4)\
**Post date:** [8 September 2026 17:48 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592/7 "2026-09-08T17:48:00Z")

</div>

Mike THANK YOU was able to get to it this morning and it WORKS PERFECT

---

<div class="post-metadata">

**Author:** ![vaursechs](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/vaursechs/32/20929_2.png) [@vaursechs](https://community.victronenergy.com/u/vaursechs)\
**Post date:** [8 September 2026 18:22 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592/8 "2026-09-08T18:22:59Z")

</div>

Your charged voltage at 28,6V is WAY too high! Should be set at 27,6V (3,45V per cell)  
Charge voltages are also too high in my opinion. Absorption voltage should be 28V max, float should be around 26,8V.  
You are stressing your cells too much with these high voltages, and you’re not gaining any extra capacity.

---

<div class="post-metadata">

**Author:** ![Justin](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/justin/32/24_2.png) [@Justin](https://community.victronenergy.com/u/Justin)\
**Post date:** [8 September 2026 18:24 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592/9 "2026-09-08T18:24:39Z")

</div>

The “charged voltage” should be roughly 0.2v below the charging voltage, and the charging voltage is set to 28.8, so the charged voltage is appropriate.

---

<div class="post-metadata">

**Author:** ![vaursechs](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/vaursechs/32/20929_2.png) [@vaursechs](https://community.victronenergy.com/u/vaursechs)\
**Post date:** [8 September 2026 18:25 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592/10 "2026-09-08T18:25:20Z")

</div>

Charging voltage is also too high for an 8 cells LFP battery. There is no benefit charging a LFP cell over 3.45V even though they can be charged to 3.65V. There is no extra capacity difference between 3.45 and 3.65.

---

<div class="post-metadata">

**Author:** ![Justin](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/justin/32/24_2.png) [@Justin](https://community.victronenergy.com/u/Justin)\
**Post date:** [8 September 2026 18:28 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592/11 "2026-09-08T18:28:02Z")

</div>

OP doesn’t say what batteries he’s using; profiles are set to Pb.

---

<div class="post-metadata">

**Author:** ![vaursechs](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/vaursechs/32/20929_2.png) [@vaursechs](https://community.victronenergy.com/u/vaursechs)\
**Post date:** [8 September 2026 18:30 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592/12 "2026-09-08T18:30:21Z")

</div>

Fair point, forgot that people still use anything other than LFP these days 😅

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [22 September 2026 18:30 UTC](https://community.victronenergy.com/t/soc-wont-reset-have-added-pic-of-settings-and-diagram-of-system-i-have-2-array-system/62592/13 "2026-09-22T18:30:32Z")

</div>

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.