# SOC 92% after many hours of motoring

**URL:** <https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535>\
**Category:** DIY\
**Tags:** marine, lithium\_battery, diy, cerbo-gx\
**Created:** [24 November 2026 20:57 UTC](https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535 "2026-11-24T20:57:19Z")\
**Posts on this page:** 12\
**Page:** 1

<div class="post-metadata">

**Author:** ![george123](https://avatars.discourse-cdn.com/v4/letter/g/aeb1de/32.png) [@george123](https://community.victronenergy.com/u/george123)\
**Post date:** [24 November 2026 20:57 UTC](https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535/1 "2026-11-24T20:57:19Z")

</div>

I am having an issue with the new installation.i have the zeus regulator with 275 amp alternator. LYNX BMS NG with 1200 amp hr of ng batteries. The zeus has firmware 1.28 Ekrano firmware 3.73. The system is wired for DVCC control. The system never gets above 92% SOC. The system goes from bulk to float so the SOC doe doesn’t increase. With the boat motoring with dc loads of 23 amps. the alternator supplements the boat load but never supplies current to increase the SOC. The absorption is set at 14.2v and float is 13.5v.

---

<div class="post-metadata">

**Author:** ![pwfarnell](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/pwfarnell/32/2341_2.png) [@pwfarnell](https://community.victronenergy.com/u/pwfarnell)\
**Post date:** [25 November 2026 10:13 UTC](https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535/2 "2026-11-25T10:13:14Z")

</div>

I can not answer detailed Zeus questions but have a similar set up with Wakespeed WS500.

The BMS is controlling with your set up, not the settings in the Zeus. The BMS requests either 14.0V or 13.5V, 14.0V is the absorption setting for the NG batteries, not 14.2V. There are 2 key settings in the BMS, repeated absorption interval, default 30 days and SOC Threshold, default 80%. A lot of people have raised the same point as you and what is happening is the BMS is remaining at 13.5V so it will not reach 100%. The way to check is to go into the Ekrano, battery device page and look under parameters at CVL, charge voltage limit, this will be staying at 13.5V. The BMS only requests an absorption charge if there has not been 1 for 30 days (repeat absorption interval) or the SOC has fallen below 80% (SOC Threshold). If your batteries are only cycling in the 80% to 100% range then you will only see absorption once a month on the default settings. If you want more frequent absorption charging then increase you SOC Threshold or reduce the repeat absorption interval. There is nothing wrong with the batteries not being charged to 100% daily, you need to get away from the led acid mind set.

---

<div class="post-metadata">

**Author:** ![Karl-Heinz](https://avatars.discourse-cdn.com/v4/letter/k/ad7895/32.png) [@Karl-Heinz](https://community.victronenergy.com/u/Karl-Heinz)\
**Post date:** [25 November 2026 12:19 UTC](https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535/3 "2026-11-25T12:19:59Z")

</div>

At a cell voltage of 3.37 V, a LiFePO4 battery is considered fully charged. 13.5 V is therefore correct.

---

<div class="post-metadata">

**Author:** ![george123](https://avatars.discourse-cdn.com/v4/letter/g/aeb1de/32.png) [@george123](https://community.victronenergy.com/u/george123)\
**Post date:** [25 November 2026 13:44 UTC](https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535/4 "2026-11-25T13:44:26Z")

</div>

I looked at the published spec in the manual and it shows 14.0 to 14.2 for absorption for the NG. The fully charged state for a lithium battery is 3.55 to 3.60 volts.  
Now i better understand the absorption issue. So lets say i am at 92% and i discharge to 68% when i start the engine my Zeus will go to full output and start charging the battery and when the battery gets to 14.0v it will hold for two hours(default) and drop to 13.5 v. The two hours may be long enough to get to 100% if it does not get to 100% i could increase to 2 hrs because my bank is a 1200ahr.

---

<div class="post-metadata">

**Author:** ![pwfarnell](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/pwfarnell/32/2341_2.png) [@pwfarnell](https://community.victronenergy.com/u/pwfarnell)\
**Post date:** [25 November 2026 17:28 UTC](https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535/5 "2026-11-25T17:28:32Z")

</div>

The manual is not fully up to date, it is being revised, the Lynx NG BMS is better than described, which still relates to the older pre NG BMS. The absorption time setting is not applicable to the NG BMS. The Lynx NG BMS will hold 14.0V until the tail current is below the tail current setting AND the cells are balanced AND the SOC has reset to 100%. If this occurs in 3 minutes then that is all the absorption you will get, if the cells need some balancing it may be longer. I have 600Ah and limit my 175A alternator to 100A. If I have daily absorption then I may see 5 minutes absorption. During charging with CVL at 14.0V, if the cells show an imbalance towards the end of charge the BMS reduces CVL to reduce charging current to keep within acceptable cell voltages.

---

<div class="post-metadata">

**Author:** ![george123](https://avatars.discourse-cdn.com/v4/letter/g/aeb1de/32.png) [@george123](https://community.victronenergy.com/u/george123)\
**Post date:** [25 November 2026 19:11 UTC](https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535/6 "2026-11-25T19:11:34Z")

</div>

Are you saying that all three conditions must be met before it drops to 13.5 volts? Something is triggering the zeus to drop to 13.5 before the soc reaches 100% . The system doesn’t get above 92%.  
The 30 day and the 70% may be preventing the SOC from going above 92%

---

<div class="post-metadata">

**Author:** ![pwfarnell](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/pwfarnell/32/2341_2.png) [@pwfarnell](https://community.victronenergy.com/u/pwfarnell)\
**Post date:** [25 November 2026 19:16 UTC](https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535/7 "2026-11-25T19:16:45Z")

</div>

Yes all 3 should be met as far as I understand it. Are you sure you are seeing CVL going up to 14.0V and the Zeus is going up to 14.0V only, not 14.2V. The other thought is that your Zeus may not be responding properly to DVCC and is doing it’s own thing. On the WS500 it says it is in slave mode. I can not help if the Zeus is not following DVCC properly.

---

<div class="post-metadata">

**Author:** ![george123](https://avatars.discourse-cdn.com/v4/letter/g/aeb1de/32.png) [@george123](https://community.victronenergy.com/u/george123)\
**Post date:** [25 November 2026 20:00 UTC](https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535/8 "2026-11-25T20:00:48Z")

</div>

The ekrano is showing slave mode and the.zeus app is showing DVCC. The voltage is set 14.2

---

<div class="post-metadata">

**Author:** ![pwfarnell](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/pwfarnell/32/2341_2.png) [@pwfarnell](https://community.victronenergy.com/u/pwfarnell)\
**Post date:** [25 November 2026 22:17 UTC](https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535/9 "2026-11-25T22:17:53Z")

</div>

But the Zeus voltage should be irrelevant if DVCC is working because the NG Lynx BMS works at 14.0V and this is not user variable. So you have to look at your CVL history from the BMS to confirm what this is doing. Hopefully you are logging history to VRM to check.

---

<div class="post-metadata">

**Author:** ![george123](https://avatars.discourse-cdn.com/v4/letter/g/aeb1de/32.png) [@george123](https://community.victronenergy.com/u/george123)\
**Post date:** [27 November 2026 18:28 UTC](https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535/10 "2026-11-27T18:28:22Z")

</div>

I thought the CVL in the parameter section was a limit that you set i.e. 14.0 volts. Where are you looking to set it go to 13.5 under DVCC control?  
Also where do you setup VRM logging$

---

<div class="post-metadata">

**Author:** ![pwfarnell](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/pwfarnell/32/2341_2.png) [@pwfarnell](https://community.victronenergy.com/u/pwfarnell)\
**Post date:** [27 November 2026 22:27 UTC](https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535/11 "2026-11-27T22:27:48Z")

</div>

The BMS sends CVL and CCL, charge voltage limit and charge current limit to the GX, which then controls all the chargers using these settings. You can manually add lower limits but never higher.

To see CVLand CCL go to the overview screen, click on the battery icon, ftom the list choose the BMS whatever you have named it, then scroll down the list to Parameters, this will give the info.

Regarding VRM, you have to set up a VRM account, have your GX connected to the internet, then register your GX serial number in VRM. I do not know the current way this is done in detail, but the GX manual should cover it. Also on the GX, go to settings, then VRM, this has a registration link, also settings for access level, time interval etc.

> **[VRM Portal - Victron Energy](https://vrm.victronenergy.com/)**
>
> VRM by Victron Energy gives realtime insights into your energy. Monitor complete energy systems, tanks and temperatures remotely.

> **[13. VRM Portal](https://www.victronenergy.com/media/pg/Cerbo_GX/en/vrm-portal.html)**

---

<div class="post-metadata">

**Author:** ![george123](https://avatars.discourse-cdn.com/v4/letter/g/aeb1de/32.png) [@george123](https://community.victronenergy.com/u/george123)\
**Post date:** [28 November 2026 13:24 UTC](https://community.victronenergy.com/t/soc-92-after-many-hours-of-motoring/65535/12 "2026-11-28T13:24:47Z")

</div>

Thanks iwill go and set this up. Thanks for your help.