Hi all, one of my smartsolars (connected to an ecoworthy 100ah lifpo4) is acting up. I originally thought it might be the battery collapsing but turns out the victron can enter float after 350-450wh which obviously means the battery is then “fully charged” to around 30% and is the cause for the voltage collapsing under use.
Ok so changing the voltage to enter float just makes the victron change the voltage to match so that’s no use. In the app it usually has 0.25v increase over battery terminal voltage. If i disconnect the pv then the victron can read the battery within 0.1v accuracy and will then go back into bulk to continue charging.
Ive changed absorption from 14.2v (smart lithium profile) to 14.6v and although the victron entered absorption today after 390wh (battery was resting at 12.84v overnight) it didn’t hang in float and stop charging (or at least drops to 6-26w as ive seen in the last few days).
Any solution to this? Going outside to the battery and turning pv off and on again several times a day isn’t ideal. Ive got 10 smartsolars and this one is the only issue.
I had the smartsolar and battery for 3 months and it used to charge 880-970wh fine in a single day and behave fine. In the last month though ive been having this issue.
Also if i use an inverter load (even 200w) then the energy will come from the battery as the victron smartsolar wont exit float. If i turn the inverter back off, dc/rc pv then it will go back to bulk and start taking pv to compensate for the inverter. In the logs it hangs at 13.48-13.5v float basically just a straight line when it has this issue and doesn’t exit it until i either dc pv or the smartsolar from the battery