SmartSolar 250/100 - what SPD?

I see people are installing SPDs after the PV switches, but I cannot find any SPD that matches the voltage protection level of Victron’s MPPTs.

All are above 500 VDC.

Does this mean surge protection is not necessary in this case?

SPDs on the panels before the charger? Most SPDs I have seen are 500v but I also see smaller SPDs. I use the smaller type after the chargers which would protect the system but not the charger itself.

The inverter’s charger comes after the MPPT and draws current from either the battery / or the grid, and for that there are AC SPDs in the main panel.

But what protects the MPPT, from say a lightning surge? All DC SPDs I’ve seen are above 500 V..

That’d be one for strings up to 150 V.

I might be off piste here but as I understand it, it is almost impossible to protect a 250/100 beyond the Victron strict advice to make sure your string’s VOC remains below 250VDC in the case of a 250/100, because of the way SPDs work.

On the one hand, you have to make sure that your SPD doesn’t mistake normal operating voltage for a permanent lightning strike, for example. The voltage you quoted is most likely that (SPD’s UC rating, e.g 500v). On the other hand, this can only clip power (after a few moments by which time your charger is fried anyway) to 1.5-2.0 KV (SPD’s UP rating) which is too high for your charger. I think the smallest device you can find will be about 300v UC.

If you find an SPD with low enough UP rating, it will have very low UC rating, hence mistaking normal voltage for a surge.

It is still safer to use a PV SPD as a mitigating device, not a protective device. The SPD will not save your charger but it may help reduce the power, delay the impact and thereby help save your house.

I also think the SPD should mainly protect the rest of the house. In the event of a direct strike, there’s really nothing that can protect the MPPT, but the voltage can be limited to protect downstream equipment.

Correct cable routing can make a significant difference.

Route the cables to minimise the area of large induction loops (string within the module array), use metal profiles, twist the conductor pairs, etc.

Install a surge protection device in the generator junction box; for cable runs over 10 m, install another one close to the controller.

The voltage rating on a surge arrester refers to its maximum continuous operating voltage, not its protection level. The latter is always several kV.

The continuous operating voltage is more of a quality indicator. If you wanted to protect the MPPT, you’d need to add a fine-protection device (Type 3, close to the equipment) downstream of the Type 1/2 device.

I know, the brochures say “protection for your equipment” — but, as always, that’s at best only half the story.

In the best-case scenario, Type 1/2 devices only prevent the equipment from catching fire or exploding.

I would use the Midnite SPD-300 DC version.

What is you’re theoretical highest pv voltage?
Even a 500v SPD will offer protection.